Topic: Recessed AC Combiner for (2) 25 kW Inverters

User: bellington, Location: Hahira, GA

Asked on: Tuesday, September 2, 2025 at 10:22 am EDT
Answered on: Wednesday, September 3, 2025 at 1:38 pm EDT

Question: Good morning.I have (2) Chint 25 kW 480 3-phase inverters to pack into a very small space. They will use the Chint FlexOM Gateway. To provide adequate space for air flow, I am considering using a standard 480-volt 100-amp recessed electrical panel with (2) 40-amps 3-pole breakers, and an 80-amp main for combining AC output. The 100-amp panel output would then connect to an 80-amp breaker in a 250-amp panel with a 100-amp main that also provides power for 3 water heaters. The 250-amp panel would connect to an 600-amp panel in another building. The 600-amp panel is connected through the switch gear to the battery, other solar, and/or generator. It is located in the Bahamas and falls under Canadian Code.Questions:1. Is there a better option for combining the (2) inverter outputs?2. Will a standard recessed panel work for a combiner?3. Will I still be required to have a separate disconnect if the 100-amp panel main breaker would serve the same purpose?4. If I wanted to remotely open the circuit with the BESS, how should I go about that?Thanks,Byron

Good morning Byron,Let's break down your questions regarding combining the Chint inverter outputs, keeping in mind the context of the Bahamas (Canadian Code influence) and aiming for a safe and efficient solution.

General Considerations



Canadian Electrical Code (CEC)

Since you're under Canadian Code influence, ensure all equipment and wiring comply with the CEC. Specifically, pay attention to Sections 12 (Wiring Methods), 14 (Protection and Control), 26 (Distribution Equipment), and 64 (Renewable Energy Systems). Local Bahamian amendments to the CEC might exist, so always check with the local AHJ (Authority Having Jurisdiction).


NEC Comparison

While I'm more familiar with the National Electrical Code (NEC) used in the US, many concepts overlap with the CEC. I will try to address code requirements using both where possible.

Safety First

This is critical. All work should be performed by qualified electricians familiar with renewable energy installations and the applicable codes.

Addressing Your Questions


Is there a better option for combining the (2) inverter outputs?
Your Proposed Solution

Using a 100-amp recessed panel is a solution, but not necessarily the best.

Alternatives



Pre-Manufactured Combiner Box

The cleanest and often safest option. These are specifically designed for combining multiple AC outputs. Look for one UL/CSA listed for your application, rated for the voltage and current, and with sufficient space for wiring. The Eaton Bussmann series and similar products from other manufacturers are good examples.

Enclosed Disconnects

Use two separate, fused disconnect switches (rated for your voltage and current) feeding into a larger fused disconnect switch. This offers a high level of safety and isolation for maintenance.


NEMA Enclosure with DIN Rail

This offers a slightly less expensive option to build a combiner yourself.

Why Pre-manufactured or Enclosed Disconnects are often "Better"



Safety

Specifically designed for combining power sources.

Compliance

Typically already UL/CSA listed for the intended purpose.


Ease of Installation

Clear wiring diagrams and optimized layouts.

Maintenance

Easier access and isolation.


Code Compliance

Likely meets all the requirements of the CEC/NEC for overcurrent protection, disconnecting means, and labeling.2.

Will a standard recessed panel work for a combiner?
Technically Possible, but Not Recommended

A standard panel
can be used if properly sized and installed to meet all code requirements.

Concerns



Listing

Is the panel specifically listed for use as a combiner box in this type of application? Many are not.


Overcrowding

Fitting all the wiring, breakers, and terminations in a recessed panel and maintaining adequate airflow for the inverters can be difficult. Overcrowding leads to overheating and potential fire hazards.

Neutral/Grounding

Proper neutral and grounding connections are essential. Follow CEC/NEC guidelines for grounding electrode conductors, equipment grounding conductors, and neutral-to-ground bonding.


Airflow

As you mentioned, maintaining airflow for the inverters inside a recessed panel would be difficult.

Recommendation

Unless you have
very strong reasons to use a standard panel and are extremely confident in your ability to meet all code requirements (and get it approved by the AHJ), it's best to use a pre-manufactured combiner box or an enclosure specifically designed for this purpose.3.

Will I still be required to have a separate disconnect if the 100-amp panel main breaker would serve the same purpose?
Likely Yes. Reasons



Accessibility

The disconnect must be readily accessible and located near the equipment it disconnects (the inverters). A recessed panel might not be considered readily accessible if it's behind furniture or otherwise obstructed. Check the CEC/NEC definition of "readily accessible."

Clear Identification

The disconnect
must be clearly labeled to indicate its purpose (e.g., "Inverter Disconnect").

Serviceability

It might be helpful to have a local disconnect located near the inverters to isolate them for service.

CEC/NEC Requirement

The CEC/NEC requires a disconnecting means for PV systems. While the 100A main breaker
could potentially function as a disconnect, you'll likely need an additional disconnect closer to the inverters, especially if the 100A panel is remote.

Recommendation

Install a separate, lockable disconnect switch (or circuit breaker in a suitable enclosure) near the inverters. This is the safest and most code-compliant approach.4.

If I wanted to remotely open the circuit with the BESS, how should I go about that?
Options



Remote-Controlled Breaker

Use a circuit breaker that can be remotely tripped via a signal. These are typically specialized breakers and require a control system. Companies like ABB, Schneider Electric, and Siemens manufacture these. They require a communication interface and control logic.

Contactor

A contactor is an electrically controlled switch. You can place a contactor in series with your inverter output and control it remotely. This requires a control system to send the open/close signal to the contactor's coil. Ensure the contactor is rated for the voltage and current of the circuit.


Smart Disconnect

Some pre-manufactured disconnects come with remote control capabilities. These are typically integrated with monitoring systems and allow for remote shutdown.

Control System

You'll need a control system (e.g., PLC, BMS, or dedicated monitoring/control system) to manage the remote operation. This system would receive the "open" signal (e.g., from the BESS or a monitoring system) and then activate the remote-controlled breaker or contactor.


Safety Interlocks

Extremely Important! Implement safety interlocks to prevent accidental or unauthorized remote operation. Consider factors like:

Confirmation

Require a confirmation step before remotely opening the circuit.


Communication Loss

Implement a "fail-safe" mechanism that automatically opens the circuit if communication with the control system is lost.

Emergency Override

Provide a manual override in case the remote control system fails.


Cybersecurity

Since this is a remotely controlled system, consider cybersecurity implications to prevent unauthorized access and control.

Recommendations for Your Situation


Consult with a Qualified Electrical Engineer/Contractor

This is essential. They can assess your specific site conditions, calculate the required conductor sizes and overcurrent protection, and ensure compliance with all applicable codes.2.

Use a Pre-Manufactured Combiner Box

This simplifies the installation, enhances safety, and ensures code compliance.3.

Install a Separate Disconnect Near the Inverters

This provides a local means of disconnecting the inverters for maintenance and emergencies.4.

Design a Robust Remote Control System (if required)

If remote operation is necessary, use a reliable control system with safety interlocks and cybersecurity measures.5.

Obtain AHJ Approval

Before starting any work, submit your plans to the local Authority Having Jurisdiction (AHJ) for review and approval.

Important Notes



Overcurrent Protection

Correctly sizing breakers and fuses is vital to prevent overloads and short circuits. Follow CEC/NEC rules for conductor ampacity, overcurrent protection sizing, and derating factors.


Grounding

Proper grounding is essential for safety and to prevent equipment damage. Follow CEC/NEC guidelines for grounding electrode conductors, equipment grounding conductors, and bonding.*

Labeling:
Clearly label all equipment, including disconnects, combiner boxes, and panels, with their function and voltage/current ratings.I hope this detailed response helps you design a safe and code-compliant system. Please remember to consult with qualified professionals to ensure the correct and safe implementation of your project. Good luck! Flag for review