Topic: Derating question

User: Alwayslearningelec, Location: NJ

Asked on: Tuesday, September 2, 2025 at 2:18 pm EDT
Answered on: Wednesday, September 3, 2025 at 1:39 pm EDT

Question: Have several 3P 30A motor circuits. They have 3 #10 hots, 1 #10N and 1 #10G.If I were to combine two of these circuits in one pipe I would be limited to 70% of the ampacity listed in the 90 degree column?So using THHN @ 90 degrees #8 is good for 55A. I would have to take 70% of that which is about 38A. So I could use #8's? Thanks

You're on the right track with the derating for conductors in conduit, but there are a few key points to clarify and some corrections needed to your assumptions

Understanding Derating for Current-Carrying Conductors
NEC 310.15(C)(1) [Formerly 310.15(B)(3)(a)] - Adjustment Factors

This is the section in the NEC that governs the adjustment factors for having more than three current-carrying conductors in a raceway or cable. The principle is that more conductors generating heat in close proximity raise the overall temperature, requiring a reduction in the allowable ampacity of each conductor.


Current-Carrying Conductors (CCC)

The neutral conductor in your situation only counts as a current carrying conductor if it carries significant unbalanced current (i.e., non-linear loads). Since you're dealing with motor circuits, unless you have a lot of single-phase loads branching off these circuits, the neutral is unlikely to be considered a CCC. The ground is never considered a current carrying conductor.

Application to Your Scenario
You have three current-carrying conductors per 3-phase motor circuit (the three hots). If you combine two 3-phase motor circuits in the same conduit, you'll have a total of six current-carrying conductors. Referring to NEC Table 310.15(C)(1), for 4-6 current-carrying conductors, the adjustment factor is 80%, not 70%.

Corrected Calculations and Conductor Sizing1. Initial Ampacity

Your motors are 30A each.2.

Adjustment for Number of Conductors

With six current-carrying conductors, you need to apply an 80% derating factor.3.

Required Ampacity After Derating

To determine the required conductor ampacity before derating, divide the motor's current by the derating factor: 30A / 0.80 = 37.5A4.

Temperature Rating

You mentioned using the 90°C column for THHN. While you can use the 90°C ampacity for derating and adjustments, you must terminate the conductors at equipment rated for the temperature you are using (Typically, terminations are rated for 75C). If the terminations are only rated for 75C, then that is the column you need to use.5.

Selecting the Correct Wire Size (Assuming 75°C Terminations)

#8 THHN at 75°C is rated for 50A, which is greater than the 37.5A after derating.

#8 THHN is acceptable.
Important Considerations



Motor Full-Load Amps (FLA)

Make sure you're using the motor's actual FLA from its nameplate, not just a generic value.

Overcurrent Protection

You'll need to size the motor's overcurrent protection (circuit breakers or fuses) according to NEC Article 430 (Motors). This often requires sizing the overcurrent protection higher than the conductor ampacity to allow for motor starting currents.


Conduit Fill

Ensure that the conduit fill is within the limits specified in NEC Chapter 9, Table 1. With six #8 conductors and two #10 conductors, you'll need at least a 1" conduit (check the actual conduit fill calculations based on the conductor insulation type and conduit type).

Voltage Drop

Consider voltage drop, especially on long runs. Larger conductors may be required to keep voltage drop within acceptable limits.


Local Codes

Always check for any local amendments or variations to the NEC that may apply in your jurisdiction.

In Summary:
You are correct that you need to derate the conductor ampacity due to the number of conductors in the conduit. The correct derating factor for six current-carrying conductors is 80%, not 70%. You need to make sure the terminals are rated for the temperature column you are using. Assuming 75°C Terminations, #8 THHN is acceptable.I strongly recommend consulting with a qualified electrician or electrical engineer to ensure your design meets all applicable codes and safety requirements. Flag for review