User: busman, Location: Northern Virginia
Asked on: Tuesday, September 2, 2025 at 3:23 pm EDT
Answered on: Wednesday, September 3, 2025 at 1:40 pm EDT
Question: All,I don't use a Megger all that often. I have an A/C unit that is tripping a CB. To determine whether it is the OFM or the Compressor (single phase residential unit), I disconnected the compressor and the unit started and ran the fan only. Thinking it was a shorted compressor winding, I disconnected all three leads. Connected one side of the Megger to ground and then tested all three three coil wires at 100 VDC - got short to ground on all three. I know I would get that on a shorted coil, but just for grins, I did the OFM motor which I'm sure runs and got the same readings. Am I missing something. If needed, I can go back and double check the findings.As always, thanks for any insight.Mark
Okay, Mark, let's break this down. You're seeing a short to ground on both the compressor windings AND the OFM motor windings with your Megger, and that's suspicious. Here's a breakdown of what could be happening and how to further investigate
Understanding Megger Readings
What a Megger does
A Megger (insulation resistance tester) applies a DC voltage and measures the current flow. A healthy motor winding should have very high resistance to ground (ideally infinity). A good rule of thumb, especially for low voltage AC motors, is you should see at least 1 megohm to ground.
Short to Ground
A short to ground means a low resistance path exists between the winding and the motor's frame (which is connected to ground). This is dangerous and will cause a circuit breaker to trip.
Normal Readings vs. Faults
With all motor leads disconnected, a healthy winding should show very high resistance to ground (Megohms). A low reading (approaching zero) indicates a problem.
Possible Issues and Troubleshooting Steps
Megger Issues
Battery
Low Megger battery voltage can give false readings. Ensure your Megger has fresh batteries. Sometimes a Megger might appear to work but gives inaccurate readings with low batteries.
Leads
Check your Megger leads for continuity and insulation damage. A short in the leads themselves would mimic a short to ground. Swap leads and retest.
Megger Function
Verify your Megger is functioning correctly. Test across a known high-value resistor (e.g., 1 Megohm or higher) to confirm it reads appropriately. If you have access to another Megger, compare readings.2.
Wiring Issues
Misidentification
Are you absolutely positive that ALL compressor wires are disconnected from everything? Make absolutely sure the wires you're testing are only connected to the compressor windings. It's surprisingly easy to overlook a connection.
Contamination
Oil, moisture, or dirt can create a conductive path. If the compressor terminals are oily or wet, clean them thoroughly with a non-residue electrical contact cleaner and try again. Make sure the area is dry before retesting.3.
OFM Testing
Same problem as the Compressor? It is certainly odd that the OFM motor would fail exactly the same way at the same time. Make extra sure it is fully disconnected as well.4. Compressor Specifics
High Voltage Test
Your testing with 100 VDC is a good start. You can also perform this test at 500 VDC. This will help you isolate a failing coil that may be more resistant at lower voltages.
Capacitor
Remove the capacitor if it is still connected. A bad capacitor could be contributing, though it's unlikely to cause a direct short to ground.
Overload Protection
If the compressor has an internal overload, make sure it has cooled down completely. An overheated overload could give a false reading, although that's less likely.*
Winding-to-Winding Test
While you're checking for shorts to ground, also check the resistance between the compressor windings themselves. They should have a relatively low resistance (a few ohms, depending on the compressor). Infinite resistance (open circuit) between windings would also indicate a problem.
Troubleshooting Steps - In Order
Verify Megger Function
As described above, test with a known resistor. Check/replace Megger batteries. Examine leads.2.
Double-Check Disconnections
Be absolutely certain ALL wires to the compressor and OFM motor are fully disconnected and isolated. Trace them back to their source.3.
Clean Terminals
Clean the compressor and OFM terminals thoroughly with electrical contact cleaner.4.
Retest at Higher Voltage
If the problem persists, test again at 500 VDC, if your Megger allows.5.
Winding-to-Winding Test
Check resistance between the compressor windings.
If you still get shorts to ground after all of this, it's highly likely both the compressor AND the OFM motor have failed. While statistically unlikely, it's possible, especially if they're of similar age and have been subjected to the same operating conditions (voltage spikes, overheating, etc.). In this scenario, the next step is to replace both motors.
Important Safety Note: When working with electrical equipment, always de-energize the circuit, lock out/tag out the disconnect, and verify the circuit is de-energized with a reliable meter before touching any wires. Flag for review