Question: My customer wants to install a 22kw Honeywell under a deck, if I’m going off the installers manual we should be good (18” clearance from existing walls, 5’ ,clearance vertically, 10’ from openings and windows etc). I can’t seem to find anything in the code book challenging this either. I’m asking because rarely do I install these anywhere but the side of the house or next to free standing meters. This red circle is basically where we would want to put it. It’s technically in open air just with this vine fencing he’s built around it.
You're doing the right thing by double-checking! Installing a generator under a deck requires careful consideration of safety and code compliance. Here's a breakdown of the factors and how to approach this installation
Key Concerns and Considerations:
1. Manufacturer's Installation Manual is Primary
You're correct. The
most important document is the Honeywell installation manual for that specific 22kW generator model. It supersedes general code requirements to a large degree. Follow it strictly. If the manual says 18" from a wall, that's the rule, even if the code seems more lenient.2. Clearances
Horizontal
Ensure you meet the required clearances from the deck supports, the vine fencing, and any other obstructions. Double-check the manual's specifics on combustible and non-combustible materials.
Vertical
5' vertical clearance minimum is probably right based on what I typically see. This is critical for exhaust dispersion.
Windows/Doors/Openings
10' is a common requirement for nearby building openings to prevent exhaust from entering the building.
Service Access
Remember to maintain ample space for servicing the generator. Technicians need to be able to reach all components easily for maintenance, repairs, and adjustments.3.
Exhaust System
Exhaust Direction
The direction of the exhaust is CRITICAL under a deck. The exhaust must vent away from the house and away from the deck area. It should not be trapped or allowed to accumulate under the deck.
Exhaust Extension
You may need to extend the exhaust pipe vertically or horizontally to properly direct the exhaust. Consult the manual and possibly a qualified mechanical engineer or HVAC professional if the exhaust situation is challenging.
Exhaust Temperature
The exhaust pipe gets extremely hot. Ensure it is adequately insulated and shielded to prevent contact with combustible materials (decking, supports, etc.) and to protect anyone who might be near the generator.
CO Detection
Strongly recommend the customer install CO detectors inside the house, particularly near any doors or windows closest to the generator's location.4.
Combustion Air
Adequate Ventilation
Generators need a lot of air for combustion. The under-deck area needs to be open enough to provide sufficient airflow for the generator to operate efficiently and safely. Enclosed spaces can lead to overheating and incomplete combustion, increasing carbon monoxide production. The vine fence could restrict airflow.
Air Inlet Obstruction
Ensure that the vine fencing cannot be easily blocked by leaves, snow, or other debris, which would further restrict airflow.5.
Fuel Source (Natural Gas or Propane)
Gas Line Sizing
Ensure the existing gas line is adequately sized to handle the generator's fuel demand. Undersized gas lines can cause the generator to malfunction. A licensed plumber or gas fitter should verify this.
Gas Line Protection
Protect the gas line from physical damage, especially in an under-deck environment where it might be more vulnerable.
Leak Testing
After installation, a thorough leak test of the gas line is essential.6.
Electrical
Local Codes
All electrical work must comply with local electrical codes.
Transfer Switch
The transfer switch needs to be installed correctly and properly grounded.
Wiring
Use appropriate wiring methods and conduit for the environment (e.g., weatherproof conduit if exposed to moisture).7.
Noise
Sound Reflection
Under-deck installations can amplify generator noise. Consider how the deck structure might reflect sound towards the house or neighboring properties. Discuss noise mitigation options with the customer (e.g., sound blankets, barriers).8.
Inspection
Code Enforcement
Contact your local building and electrical inspectors before you start the installation. Discuss the proposed location and the specifics of the installation. They may have specific requirements or concerns. Get their approval before you proceed.
Code Considerations (General - check your local codes)
While the manufacturer's manual is paramount, here are some code sections that often apply to generator installations:
NEC (National Electrical Code)
Article 700 (Emergency Systems) or Article 701 (Legally Required Standby Systems) if the generator is connected to a transfer switch. Article 445 (Generators) is also relevant. Pay attention to grounding, overcurrent protection, and wiring methods.
NFPA 37 (Standard for the Installation and Use of Stationary Combustion Engines and Gas Turbines)
This standard addresses fuel systems, exhaust systems, and ventilation for stationary engines.
Local Building Codes
These codes may have specific requirements for generator installations, including permits, inspections, and setback distances.
Fuel Gas Codes (IFGC or similar)
Governs the installation of gas piping.
Recommended Actions
Thoroughly Review the Honeywell Manual
Read it cover-to-cover. Pay close attention to the sections on location, clearances, exhaust, and ventilation.2.
Contact Honeywell Technical Support
If you have any questions or uncertainties about the installation, contact Honeywell's technical support line. They can provide clarification and guidance specific to their product.3.
Consult with Local Inspectors
Talk to your local building and electrical inspectors before starting the work. They can provide valuable insights and ensure the installation complies with local regulations.4.
Document Everything
Keep a record of all communication with Honeywell, inspectors, and the customer. Take photos of the installation process.5.
Consider Alternatives
If the under-deck location presents too many challenges or uncertainties, explore alternative locations with the customer. It's better to find a safer and more code-compliant location than to force a risky installation.
In summary, installing a generator under a deck requires careful planning, strict adherence to the manufacturer's instructions, and compliance with all applicable codes. Don't hesitate to seek expert advice from Honeywell, local inspectors, and other qualified professionals. Safety is paramount! Flag for review