Question: Got a beefy portable gen the forestation wants hocked up when they have an emergency so it's going to be Twist lock- set up I guess?..... I don't have specs about the unit yet looking at it Saturday but want to know how you would hock this up?????? Is it as simple as Installing a 3 position knife switch and the building feeder in middle and service on top and Temp set up below??? I have seen that but always looked weird.Never done one this size..... Service for building is 3/0 208

Okay, let's break down how to hook up a portable generator to a 208V service for emergency backup, focusing on safety and code compliance. Given your 3/0 208V service, here's a safer and more robust approach than just a 3-position knife switch

Why the 3-Position Knife Switch is Problematic (Especially for This Size)
Safety Concerns

Knife switches are inherently less safe for high-current applications. Arcing can occur during switching, and they are not typically enclosed, leading to potential accidental contact. A knife switch is not designed to be used as a transfer switch.


Durability

Knife switches are not designed for frequent switching or the stresses of potentially high fault currents.

Code Violations

Using a knife switch for this is likely a violation of the national electric code(NEC)

The Correct Approach: A Proper Transfer Switch


The
only safe and code-compliant way to connect a generator to your service is with a listed and labeled transfer switch. This switch ensures that the generator and utility power can never be connected at the same time, preventing backfeeding onto the utility grid. Backfeeding is EXTREMELY DANGEROUS, potentially lethal to utility workers, and can damage equipment.

Steps for a Safe and Compliant Installation1. Determine Generator Capacity

This is crucial. You need to know the generator's output voltage, amperage (both running and surge), and phase configuration. Is it 120/240V single-phase, 120/208V three-phase, or something else? This dictates the type and size of transfer switch and wiring. Get the nameplate information from the generator before you buy anything.2.

Select the Right Transfer Switch



Automatic vs. Manual

Automatic transfer switches (ATS) detect a power outage and automatically start the generator and switch the load. Manual transfer switches require you to manually start the generator and flip the switch. For emergency situations, an ATS is often preferred. However, they are more expensive.

Ampacity Rating

The transfer switch
must have an ampacity rating equal to or greater than the service size (in your case, likely at least 100 amps for a 3/0 service, potentially more depending on your main breaker size).

Voltage and Phase

The transfer switch must match the voltage and phase configuration of your service and the generator. Since your service is 208V, you'll need a 208V-rated transfer switch. If the generator is single-phase 240V it will not work.

Listed and Labeled

Ensure the transfer switch is listed by a recognized testing laboratory (UL, ETL, etc.). This ensures it meets safety standards.


Enclosure Type

Choose an enclosure type suitable for the location (NEMA 1 for indoors, NEMA 3R for outdoors, etc.).

Consider Load Shedding

If the generator's capacity is less than the full service load, consider a transfer switch with load shedding capabilities. This allows you to prioritize essential circuits during an outage.3.

Wiring (General Guidance - Consult an Electrician!)
Generator Inlet

Install a weatherproof power inlet box (with the appropriate twist-lock connector) on the exterior of the building, close to the transfer switch location. The inlet's amperage and voltage rating must match the generator.

Wiring Size

The wiring from the generator inlet to the transfer switch, and from the transfer switch to the service panel,
must be sized appropriately for the generator's output and the transfer switch rating. Consult the NEC for proper conductor sizing based on ampacity, temperature rating, and derating factors. 3/0 is likely too large for the wire between the inlet and transfer switch.

Grounding

Proper grounding is critical. The generator, transfer switch, and service panel must all be properly grounded and bonded according to the NEC. Never rely on the neutral conductor for grounding.

Conduit

Use appropriate conduit (EMT, PVC, etc.) to protect the wiring.4.

Interlock Kit (for Panel Mount Transfer)

An interlock kit is a mechanical device that only allows one breaker, either the main utility breaker or the generator breaker, to be in the "on" position at any given time.

Professional Installation and Inspection

This is
not a DIY project for anyone without extensive electrical experience. Hire a licensed electrician to perform the installation. They will ensure everything is wired correctly, grounded properly, and meets all applicable codes. After installation, have the work inspected by the local electrical inspector.

Example Scenario (Assuming 208V Three-Phase)


Let's say you find the generator is 120/208V three-phase, 60 amps per phase.1. Transfer Switch

You would need a 208V three-phase transfer switch rated for at least 60 amps (but ideally higher, like 100 amps, to allow for future expansion).2.

Generator Inlet

You'd need a 60-amp (or higher) 208V three-phase twist-lock inlet.3.

Wiring

The wiring from the generator inlet to the transfer switch, and from the transfer switch to the load panel, would need to be sized to handle at least 60 amps continuously, taking into account the wiring's temperature rating and any derating factors.

Important Considerations



Local Codes

Local electrical codes may have specific requirements for generator installations. Always check with your local building department.

Permits

You will almost certainly need an electrical permit for this type of installation.


Generator Placement

Never run a generator indoors or in an enclosed space. Generators produce carbon monoxide, which is deadly. Place the generator outdoors, in a well-ventilated area, away from windows and doors.

In summary, using a proper transfer switch is non-negotiable. It's the only safe and code-compliant way to connect a generator to your electrical system. Get the generator specs, consult with a licensed electrician, and obtain the necessary permits.
Flag for review