Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Does this meet the criteria for wet location?

User: Isaiah, Location: Baton Rouge

Asked on: Tuesday, September 2, 2025 at 8:39 pm EDT
Answered on: Wednesday, September 3, 2025 at 1:41 pm EDT

Question: At this site, they have concrete embedded rigid metal conduit that penetrates a thick concrete wall and then enters a MCC room - but the conduit does not go underground.Would the cable within this conduit be considered in a wet location?Enviado desde mi iPhone utilizando Tapatalk

This is a tricky question, as it depends on several factors and interpretations of the NEC. Here's a breakdown of the considerations and a likely conclusion

Factors to Consider:
Conduit Fill and Breathing

Rigid metal conduit (RMC) is not inherently waterproof. Temperature changes cause the air inside the conduit to expand and contract ("breathing"). This can draw in moisture, even without direct exposure to rain. The more full the conduit is of conductors, the less air space there is, and potentially less "breathing" will occur.


Conduit Seals

Are the ends of the conduit sealed? If the conduit is tightly sealed at both ends, and properly installed, it could limit the ability of moisture to enter. However, even sealed conduits can experience condensation inside due to temperature differences.

Climate

A humid climate will naturally increase the likelihood of moisture entering the conduit.


Wall Thickness and Temperature Gradient

The thicker the wall and the greater the temperature difference between the outside and inside of the MCC room, the more likely condensation becomes.

MCC Room Environment

Is the MCC room climate-controlled? A climate-controlled room would reduce the likelihood of condensation.


Installation

How was the conduit installed in the concrete? Was it properly sloped away from the MCC room to discourage water from entering? Were proper sealing methods and materials used?

NEC Definition of Wet Location

The NEC defines a "Wet Location" as:
Locations subject to saturation with water or other liquids, such as washdown areas, and locations exposed to weather.
Analysis

While the conduit doesn't run underground, the potential for moisture to enter and accumulate inside the conduit
does exist. Here's why:

Breathing and Condensation

Even if not directly exposed to rain, the conduit can still draw in moisture from the surrounding air through the "breathing" effect. Temperature differentials between the concrete wall (potentially cooler) and the MCC room (potentially warmer) will cause condensation inside the conduit.

Penetration Point

The penetration point through the concrete wall is a potential entry point for moisture. Even a small imperfection in the sealing around the conduit can allow water to seep in over time.


Not Necessarily Subject to Saturation, but Still Wet

While not saturated, the conduit can still accumulate moisture. The NEC definition of "Wet Location" includes locations exposed to weather. Since the exterior of the conduit is exposed to weather, this factor is present.

Conclusion



It is highly likely that the cable within this conduit should be considered to be in a wet location.
Recommendations


Use Cable Rated for Wet Locations

The safest and most prudent approach is to use cable that is specifically rated for wet locations (e.g., THWN, XHHW). This will provide the best protection against moisture-related failures.2.

Proper Conduit Sealing

Ensure the conduit is properly sealed at both ends to minimize moisture ingress. Use appropriate sealing fittings and compounds that are compatible with the conduit material and environment.3.

Consider Conduit Seals

Install conduit sealing fittings at both ends of the conduit run.4.

Drainage

If possible, design the conduit run with a slight slope away from the MCC room to allow any accumulated water to drain out. This may be difficult with an existing installation.5.

Inspection and Maintenance

Regularly inspect the conduit and cable for signs of moisture damage.6.

Consult Local AHJ

Ultimately, the final determination rests with the local Authority Having Jurisdiction (AHJ). It's always best to consult with them for their interpretation of the NEC in your specific situation.

In summary, err on the side of caution and treat this as a wet location. The cost of using wet-rated cable is minimal compared to the potential cost of future failures and repairs.
Flag for review

Previous Question Next Question