User: JoeBoots223, Location: Brockton, MA
Asked on: Wednesday, September 3, 2025 at 7:07 am EDT
Answered on: Wednesday, September 3, 2025 at 1:42 pm EDT
Question: Service Grounding NEC 2020 Rhode IslandUnderground service in 2 inch PVC Schedule 40Conductors 4/0-4/0-2/0Main breaker (Emergency / Service Disco) ATS Located at Pedestal Meter socket remote from houseMLO Panel located in homes basementGround rods located in BasementBonding jumper located in ATS and at Panel in basementArgument: Since the ATS has the overcurrent protection.-would the panel be considered a sub panel and a #6 ground be required to be pulled to provide a separate path for ground faults?-would ground rods need to be relocated to the ATSRemember RI is on the 2020NEC
Okay, let's break down the NEC requirements for service grounding and bonding in your Rhode Island situation, considering the 2020 NEC.
Analysis1. Point of Service
This is absolutely critical. The point of service is where the utility conductors end and your premises wiring begins. In your case, because the Emergency/Service Disco (Main Breaker/ATS) is at the pedestal/meter socket, that's your service disconnect and, electrically speaking, the termination of the utility.2.
ATS/Service Disconnect Location
The ATS/Service Disconnect is located at the pedestal/meter socket and will serve as the first point of disconnect as it contains the main breaker.3.
Panel in the Basement
The panel in your basement is not a subpanel. Because the ATS is serving as the service disconnect, the basement panel is therefore now acting as a distribution panel.4.
Grounding Electrode System (GES)
The NEC (250.24(A)) requires the grounding electrode system to be connected to the grounded conductor at the service disconnecting means. Since the service disconnecting means is located at the pedestal, your Grounding Electrode System (ground rods) must be located at the pedestal/ATS.5.
Grounding Electrode Conductor (GEC)
The GEC connects the Grounding Electrode System (ground rods) to the grounded conductor at the service disconnecting means. Since the GEC connects to the grounded conductor at the service disconnect, the size of the GEC is based on Table 250.66 based on the size of the ungrounded service conductors. In your case the size of the service conductors are 4/0 AL and would require a #4 Copper GEC.6.
Bonding Jumpers
A bonding jumper is required within the ATS enclosure to bond the grounded conductor to the enclosure. Since the panel in the basement is acting as a distribution panel the grounded (neutral) and equipment grounding conductors (ground wires) must be bonded to the panel enclosure.7.
Equipment Grounding Conductor
Since the basement panel is acting as a distribution panel, the path for fault current is now through the equipment grounding conductor which must run with the circuit conductors. Therefore, a 4-wire feed to the panel is required. The size of this conductor would be dependent on Table 250.122 based on the overcurrent protective device. If you were to use a 200 amp breaker, the size would be a #6 Copper.
Answers to Your Questions "Would the panel be considered a sub panel and a #6 ground be required to be pulled to provide a separate path for ground faults?" No, the panel in the basement is NOT a subpanel because the main service disconnect is located at the pedestal/meter socket. However, A #6 equipment grounding conductor would be required between the ATS and basement distribution panel because the path for fault current to the source (Service Disconnect/ATS) is no longer through the grounded conductor. "Would ground rods need to be relocated to the ATS?" Yes. Absolutely. Per NEC 250.24(A), the GES (ground rods) must be connected to the grounded conductor at the service disconnecting means which, in your case, is the ATS.
Summary of Required Changes1. Relocate Ground Rods
Move the ground rods to the pedestal/ATS location.2.
GEC Size
Ensure the GEC is sized correctly per Table 250.66 (#4 Copper)3.
Four-Wire Feeder
Install a 4-wire feeder (Hot-Hot-Neutral-Ground) from the ATS to the basement panel.4.
Equipment Grounding Conductor Size
Size the equipment grounding conductor (#6 Copper) per Table 250.122, based on the overcurrent device protecting the feeder to the basement panel.
Important Considerations AHJ (Authority Having Jurisdiction)
Always consult with your local electrical inspector (AHJ) in Rhode Island. They have the final say on code interpretation and enforcement. Their specific requirements may vary slightly.
Manufacturer's Instructions
Follow the manufacturer's instructions for the ATS and any other equipment.
Qualified Electrician: This type of work should be performed by a licensed and qualified electrician who is familiar with the NEC and local codes.This information is for educational purposes only and is not a substitute for professional advice from a qualified electrician or electrical inspector. Flag for review