Question: Multi family pool equipment. During a call to verify pool equipment is working. Its discoovered that the pool pumps are not bonded. The receptacles for motors arent gfci. The cords used at motors have no grounds. The pool pump room sits next door to boiler room. Would the pool pump motors need to be bonded with the circulation pumps inside boiler room? Would I also bond the pool pump motors to copper water pipe onsite? The ground rod has deteriorated from chlorine water from pool water system leaking. I wish i could post a picture. Ive never seen this before.The complex is old. Im sure multiple contractors and maintenance have been involved doing repairs. I told management to close pool until we or other electrical contractor doesn't these repairs as a suggestion.

Okay, this is a serious situation. You've correctly identified multiple critical safety issues. Let's break down the problems and the best course of action.

Here's a summary of the key issues you found



No Bonding of Pool Pumps

This is a major electrical safety hazard. Bonding is essential to equalize electrical potential and prevent dangerous voltage differences that could lead to electric shock.


Non-GFCI Receptacles

Receptacles within a certain distance of a pool (typically within 20 feet) must be GFCI protected. This is another crucial safety measure.

Ungrounded Cords

Using cords without a proper ground connection defeats the purpose of grounding the equipment and creates a shock hazard.


Proximity to Boiler Room

The close proximity of the pool pump room to the boiler room presents further concerns due to the potential for water leaks, condensation, and other environmental factors that can exacerbate electrical hazards.

Deteriorated Ground Rod

A damaged ground rod is a significant problem because it compromises the entire grounding system's ability to safely conduct fault currents.

Addressing the Issues


Immediate Action (As You've Done)



Pool Closure

You were absolutely right to recommend closing the pool immediately. This is a critical safety precaution to prevent potential electric shock incidents. Do not allow use of the pool until ALL electrical deficiencies have been corrected.2.

Comprehensive Electrical Evaluation by a Qualified Electrical Contractor (Essential)



Detailed Inspection

A licensed and experienced electrical contractor specializing in pool electrical systems MUST perform a thorough inspection to identify all code violations and safety hazards. This includes:
Inspecting all wiring, conduit, and connections. Testing the grounding system. Verifying proper GFCI protection. Assessing the condition of the electrical panel serving the pool equipment.

Code Compliance

All repairs must comply with the current National Electrical Code (NEC) and any applicable local codes. Pool electrical systems have specific requirements that must be followed precisely.3.

Specific Repairs and Corrective Actions



Bonding



Bond ALL metal parts

This includes the pool pump motors, metal housings, metal conduit, metal parts of the pool structure (if any), metal fencing within a certain distance of the pool, and any other metal objects that could become energized.

Solid Copper Conductor

Use a solid copper bonding conductor of the correct size, as specified by the NEC. This is usually #8 AWG or larger.


Bonding to Other Systems



Boiler Room Pumps

YES, the pool pump motors should be bonded to any metal parts of the boiler system. If the boiler room pumps are metal and connected to metal piping they must be bonded to the pool equipotential bonding grid. The NEC emphasizes creating a
common grounding and bonding system for all potentially conductive elements to minimize voltage differences.

Copper Water Pipe

YES, the pool pump motors should be bonded to the nearest available copper water pipe in accordance with NEC requirements. However, do not rely solely on the water pipe as your primary grounding electrode. It's supplemental.

Grounding Electrode System



Replace Ground Rod

The deteriorated ground rod MUST be replaced. Install a new ground rod (or multiple ground rods as required by code) that is driven deep enough to provide a reliable connection to earth.

Grounding Electrode Conductor (GEC)

Ensure the GEC connecting the ground rod to the electrical panel is of the correct size and properly connected.


GFCI Protection



Install GFCI Receptacles

Replace all non-GFCI receptacles within the required distance of the pool with GFCI-protected receptacles.


GFCI Breakers

Consider using GFCI circuit breakers in the electrical panel to provide additional protection for the pool circuits.

Cords and Wiring



Replace Ungrounded Cords

Replace all ungrounded cords with properly grounded cords designed for outdoor use and appropriate for the equipment they serve.

Proper Wiring

Ensure all wiring is installed in approved conduit (e.g., PVC or rigid metal conduit) and is suitable for wet locations.


Pool Pump Motor Wiring Connections



Proper Connections

Ensure all wiring connections to the pump motors are made inside a properly grounded junction box. Use watertight connectors.


Wiring Inside Conduit

All wiring from the electrical panel to the pool pump should be installed inside conduit, not just exposed.

Bonding Jumpers



Over Joints

When bonding metal pipes, use bonding jumpers to connect across joints to maintain electrical continuity.

Pool Safety Signage



Warning Signs

Install prominent warning signs about electrical hazards around the pool area.4.

Permitting and Inspection



Permit Required

In most jurisdictions, electrical work on a pool requires a permit from the local building department.


Inspection

After the repairs are completed, schedule an inspection by the building department to ensure the work complies with code and is safe.

Important Considerations



Electrical Contractor Qualifications

Hire an electrical contractor with specific experience in pool electrical systems. They should be familiar with the NEC Article 680 (Swimming Pools, Fountains, and Similar Installations).


Documentation

Keep detailed records of all inspections, repairs, and permits.*

Pool Equipment Maintenance

Establish a regular maintenance schedule for the pool equipment to prevent future electrical problems.