Question: Say i have a service with a single 200A disconnect which is a typical 200A main breaker panelboard. Say i tap the service conductors in the panel, ahead of the main breaker and run them to another service . disconnect. Lets say the GES consists of 2 ground rods and the GEC lands in the original panel on the neutral bar. Can i use the "common location " provision in 250.64 and thus NOT run a GEC tap the the second disconnect? Would it make any difference if this for PV vs a regular 230.40 exception #2 install?
Okay, let's break down this scenario and address the grounding and bonding requirements according to the NEC (assuming you're referencing the National Electrical Code).
Understanding the Scenario
You're describing a scenario where you have:1. Original 200A Service
A standard 200A main breaker panelboard serving as the primary service.2.
Tapped Service
You're tapping the service conductors before the 200A main breaker in the original panel to feed a second service disconnect (we'll assume it's also a panelboard with a main breaker).3.
Grounding Electrode System (GES)
The GES consists of two ground rods, and the Grounding Electrode Conductor (GEC) connects to the neutral bus in the original 200A panel.
Analysis and Code Considerations 250.64(C) Common Location
This section of the NEC allows a single GEC to serve multiple service disconnects under specific conditions, primarily when the disconnects are in a "common location." The key is to ensure all requirements of 250.64(C) are met.
250.24(C) Main Bonding Jumper and System Bonding Jumper
This section provides that for separately derived systems, a system bonding jumper shall be installed at the source. 230.40 Exception No. 2 This section states that two to six service disconnects can be located in one location. 230.71(A) Maximum Number of Disconnects States that a service shall not have more than six disconnects in one location. PV Systems vs. Other Loads
The NEC has specific sections for PV systems (Article 690), and there are nuanced differences. The core grounding principles remain the same, but the application might differ slightly.
Answer to Your Questions1. Can you use the "common location" provision in 250.64(C) and thus NOT run a GEC to the second disconnect? Potentially, YES, IF you meet all the requirements of 250.64(C). Here's the breakdown: Common Location
The crucial part is determining if the two service disconnects are truly in a "common location." The NEC doesn't explicitly define this, but it generally implies they are in the same room, building, or immediate vicinity. A judgement call is necessary here.
GEC Sizing
The GEC must be sized according to 250.66 based on the largest service entrance conductor of all the services being supplied. If the tapped conductors feeding the second disconnect are smaller than the conductors feeding the original 200A panel, you base the GEC on the original 200A service conductors. If they are larger, you must use those larger conductors.
Connections
You'd likely land the GEC in the first service panel (the original 200A panel, as you described). Then, a properly sized bonding jumper (sized per 250.102(C)) must connect from the neutral bus of the first panel to the equipment grounding bus (usually the same bus) of the second panel. This bonding jumper effectively extends the grounding electrode system to the second disconnect.
Solidly Connected
The GEC must be without splice or joints, unless spliced by irreversible means.2.
Would it make any difference if this is for PV vs. a regular 230.40 exception #2 install? Yes, potentially. Here's why: PV System Grounding
PV systems have additional grounding requirements in Article 690. Specifically, 690.47(C) often requires a separate equipment grounding conductor (EGC) to be run with the PV source circuit conductors.
Interconnection
The location of the PV interconnection can also affect the grounding scheme. If the PV system is backfeeding the service through the second disconnect, then additional considerations apply for overcurrent protection and disconnection means. Consult the NEC (Article 690) and local AHJ (Authority Having Jurisdiction) for specific requirements.
Rapid Shutdown Requirements
PV systems are often subject to rapid shutdown requirements, which may impact grounding considerations.
Important Considerations and Recommendations AHJ Approval
The interpretation of "common location" is up to the AHJ. Always discuss your proposed design with them before starting any work. Get their approval in writing if possible.
Proper Bonding
Ensure all metallic enclosures, raceways, and equipment are properly bonded to the grounding system.
NEC Compliance
Carefully review all applicable sections of the NEC, especially Articles 230, 250, and 690 (if it's a PV system).
Professional Expertise
This type of installation requires a high degree of electrical knowledge. If you're not a qualified electrician, hire one to ensure the work is done safely and correctly.
Load Calculations
Ensure the service conductors and overcurrent protection are adequately sized for the combined load of both services.
Labeling
Clearly label all equipment to indicate the presence of multiple services.
In Summary
You might be able to use the "common location" provision to avoid running a separate GEC to the second disconnect, but only if:1. The two disconnects are demonstrably in a "common location" (as defined by the AHJ).
2. The GEC is sized correctly for the entire service load.3. A properly sized bonding jumper connects the neutral of the first panel to the equipment grounding bus of the second panel.
4. All other grounding and bonding requirements of the NEC are met.For PV systems, additional requirements apply from Article 690, so careful planning and consultation with the AHJ are essential. Always prioritize safety and compliance with the NEC. Flag for review