Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Are we expected to use Table 220.55 for sizing range circuits?

User: Joe E, Location: Michigan

Asked on: Wednesday, September 3, 2025 at 7:53 pm EDT
Answered on: Saturday, September 6, 2025 at 12:11 pm EDT

Question: I’m struggling to reconcile 210.19(C):“Branch-circuit conductors supplying household ranges…shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served”with Note 4 of Table 220.55:“Calculating the branch-circuit load for one range in accordance with Table 220.55 shall be permitted.”Does this later note overrule the earlier requirement?

You've highlighted a common point of confusion. Here's the breakdown to reconcile 210.19(C) and Table 220.55 Note 4

Understanding the Core Concepts
210.19(C) - Branch Circuit Conductor Sizing (General Rule)

This section sets the
general rule for sizing branch-circuit conductors. The conductors must be able to handle both the branch circuit's rating (overcurrent protection) AND the maximum load connected to that circuit. This is a fundamental safety principle: the wire needs to carry the current.

Table 220.55 - Demand Factors for Ranges (Special Rule)

This table, and especially Note 4, provide a special allowance for calculating the load for household ranges. Ranges rarely operate at their maximum rated wattage continuously. Table 220.55 acknowledges this and allows you to use a demand factor (a percentage less than 100%) to determine the load used for service and feeder calculations. Note 4 simply allows the use of the range demand factors for branch circuit calculations, as well.

How They Work Together
1. Calculate the Load

You can use Table 220.55 to determine the calculated load for a range. This is the load you'll use in most cases.2.

Verify the Conductor Size

After calculating the load using Table 220.55 (or Note 4), you must ensure that the branch-circuit conductors are sized according to 210.19(C):

Ampacity Not Less Than Branch Circuit Rating

The conductors must be rated to handle the amperage of the overcurrent protection device (the breaker or fuse protecting the circuit).


Ampacity Not Less Than Maximum Load

The conductors must have an ampacity equal to or greater than the calculated load from Table 220.55.

In Essence


Note 4 of Table 220.55 modifies how you determine the load for a range. It doesn't overrule 210.19(C). 210.19(C) is the final step - ensuring the conductors are sized to handle the calculated load and the circuit's overcurrent protection.

Example

Let's say you have a 12 kW range connected to a 40 amp branch circuit:1.

Without Table 220.55

The load would seem to be 12,000W / 240V = 50 Amps. That would seemingly require larger conductors than the 40amp circuit would dictate.2.

Using Table 220.55

You would find the demand factor in Table 220.55. For a single range not over 12 kW, the demand factor is 8 kW (8,000 Watts). Calculated Load: 8,000W / 240V = 33.33 Amps.
3.


Applying 210.19(C)

Conductor Ampacity ≥ 40 Amps (because it's a 40-amp branch circuit). Conductor Ampacity ≥ 33.33 Amps (the calculated load from Table 220.55). Therefore, the conductors must be rated for at least 40 amps. Using the 75°C column of Table 310.16, you would likely need #8 AWG copper conductors (rated for 50 amps).

Key Takeaway


Table 220.55 and Note 4
reduce the calculated load. 210.19(C) makes sure the actual conductors are sized to safely carry that reduced load and are protected by the branch circuit overcurrent device. You can't use Table 220.55 to justify using undersized conductors for the branch circuit's overcurrent protection. You always have to adhere to the lower* of the two figures in the 210.19(C) requirement.I hope this clarifies the relationship between these code sections! Always consult the latest edition of the NEC and a qualified electrician for specific installations. Flag for review

Previous Question Next Question