Topic: WEG cfw320 frequency inverter——

User: AC\DC, Location: Florence,Oregon,Lane

Asked on: Wednesday, September 3, 2025 at 8:37 pm EDT
Answered on: Saturday, September 6, 2025 at 12:11 pm EDT

Question: I called the motor shop and they gave me this drive to take my 240 V single and make 208- 3 phase for some motors I gotHas any one worked with one of these I set all my peramiters but it stuck in ready mode- can’t get to run-Jumped terminal 1-5 from my understanding that indicates run forward mode——https://www.weg.net/catalog/weg/US/en/Drives/Variable-Speed-Drives/Micro-and-Mini-Drives/Variable-Speed-Drive-CFW320/Variable-Speed-Drive-CFW320/p/MKT_WDC_GLOBAL_PRODUCT_INVERTER_CFW320

Okay, let's troubleshoot your CFW320 and get those motors spinning. It sounds like you've got the right idea jumping terminals 1 and 5 for forward run. Here's a breakdown of things to check and consider, based on my understanding of the CFW320 and similar VFDs

1. Double-Check the Basics:
Voltage

Confirm your input voltage is
actually 240V single-phase. A significant voltage drop can cause issues.

Wiring

Verify your wiring is correct.

Input

Line voltage to L1 and L2 (or L1 and N if applicable,
but check your manual). No connection to L3.

Output

U, V, and W to your motor. Ensure the motor leads are properly insulated.

Grounding

Make sure the grounding connection to the PE terminal is solid. This is crucial for safety and proper operation.


Motor Compatibility

Confirm your motors are truly compatible with 208V 3-phase. Are they wired correctly for that voltage? (e.g., star/wye vs. delta). Check the nameplate of the motor.

2. Parameter Checklist (Most Likely Culprit)



P200: Motor Voltage

Absolutely critical. Set this to

208V
. An incorrect voltage setting can prevent the drive from running or damage the motor. P201: Motor Current

Set to the full load amps (FLA) listed on the motor nameplate.

P202: Motor Frequency

Set to the motor's rated frequency (typically 60 Hz in the US).


P203: Motor Speed

Set to the motor's rated RPM.

P204: Number of Poles

Set the number of poles of the motor (usually 2 or 4). This determines the synchronous speed.


P000: Operating Mode

This is important. Make sure it's set to a mode that allows external control via the digital inputs.

Key choices for P000



0

Local (keypad) control. To use the keypad, you'll need to press the Run button (usually the arrow key). This is good for testing.

1

External control. This is
likely what you want. It means the drive will respond to the digital inputs (like your 1-5 jumper).

2

Both local and external control.

P205: Ramp-Up Time

How long it takes to reach target speed.


P206: Ramp-Down Time

How long it takes to stop.

3. Digital Input Configuration (Very Important)



P211 - P215

These parameters configure the function of each digital input. Check P211 (or whatever parameter corresponds to Digital Input 1 where you're connecting the jumper). It needs to be configured for "Start/Run Forward." It might be called "Forward Enable," "Run Command," or similar. The manual will list the possible values.
This is a common mistake.



Logic

Make sure the logic of the digital input is correct (Normally Open vs. Normally Closed). Sometimes you need to set a parameter to invert the signal. If the instruction manual does not have all of the codes listed call Weg tech support.

4. Ready Mode Troubleshooting



Fault Codes

The CFW320
should display a fault code if there's an issue preventing it from running. Check the display carefully. Consult the manual for the meaning of the fault code.

Lockout

Is there a lockout parameter set that prevents the drive from running?

Minimum Frequency

Is there a minimum frequency set (e.g., P207)? The drive might not start if the commanded frequency is below this minimum.


Keypad Control Test

As mentioned above, set P000 to 0 (local control). Can you then start the motor by pressing the "Run" button on the keypad? If not, there's a more fundamental problem.

5. Advanced Troubleshooting



Current Limiting

The drive might be in current limiting mode. If the motor is heavily loaded, the drive might prevent it from starting.


DC Bus Voltage

Use a multimeter to check the DC bus voltage inside the drive. It should be a reasonable value based on your input voltage. Warning: High voltage. Be extremely careful!

Oscilloscope

Ideally, use an oscilloscope to check the output voltage and current waveforms going to the motor. This can reveal issues like unbalanced phases or harmonics.


Communication

If you're using Modbus or another communication protocol, double-check the communication settings.

6. Steps to Take
Start with a factory reset

Reset the drive to factory settings. This will eliminate any incorrect parameter settings. Consult the manual for how to do this.
Write down your current settings before doing this!



Program the essential parameters

Program P200, P201, P202, P203, P204, and P211. Set P000 to 1.

Test

Try to run the motor by jumping terminals 1 and 5.

7. Important Considerations


Read the Manual

I know it's tempting to skip it, but the CFW320 manual is essential. Download it from the link you provided.

WEG Tech Support

WEG has good tech support. Don't hesitate to call them. Have your drive model number and serial number ready.


Safety

Work on electrical equipment only if you are qualified and comfortable doing so. Always disconnect power before working on the drive.

Let me know



What fault codes (if any) are displayed?


What are the settings of P000 and P211 (or the equivalent for DI1)?

Can you run the motor from the keypad (P000=0)?
*The more information you provide, the better I can assist. Good luck! Flag for review