Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Aluminum conductor sized same as copper table 310.16?

User: designer82, Location: Boston

Asked on: Thursday, September 4, 2025 at 9:33 am EDT
Answered on: Saturday, September 6, 2025 at 12:12 pm EDT

Question: So in table 310.16 I go to the 75°C column to select my appropriate copper cable for the required ampacity.Do you do same thing for the aluminum side? (from 75°C column same way?)

Yes, you are correct.You would use the 75°C column in Table 310.16 for Aluminum conductors if the terminations are rated for 75°C and the conductor is also rated for 75°C.Here's a breakdown of how to choose the correct column for aluminum (and copper) conductors: Determine the Termination Temperature Rating

This is
crucial. Most terminations (breakers, panels, equipment terminals) are rated for either 60°C or 75°C.

The lowest rated termination determines the column you must use.
Look for the temperature rating stamped on the equipment. If you can't find it, assume 60°C for equipment rated less than 100A and 75°C for equipment rated 100A or more. Exception: Specific terminals may be marked for higher ratings.

Determine the Conductor Temperature Rating

The insulation of the wire itself also has a maximum temperature rating (e.g., THHN is rated for 90°C in dry locations, but the termination temperature limit still applies).

Apply the Ampacity Selection Rules



If the terminations are rated for 60°C

Use the 60°C column, regardless of the conductor's insulation temperature rating.

If the terminations are rated for 75°C

Use the 75°C column if the conductor is also rated for 75°C or higher.


If the terminations are rated for 90°C

This is rare in typical residential/commercial installations. If they are, and the conductor is rated for 90°C, you can potentially use the 90°C column for ampacity. However, you must still use the 75°C ampacity when landing on equipment rated less than 100 amps. If you land on equipment rated 100amps or more, you must use the 75 degree column for that equipment.

In Summary

You follow the same logic and temperature rating rules whether you are using copper or aluminum conductors. The termination temperature is the driving factor in the selection of the correct ampacity column.

Important Considerations



Ampacity Correction Factors

Remember to apply ampacity correction factors for ambient temperature and the number of conductors in a raceway or cable
after you've determined the initial ampacity from Table 310.16.

Voltage Drop

Always calculate voltage drop, especially for longer runs. Aluminum has higher resistance than copper, so voltage drop is more of a concern.

Local Codes and Regulations

Always follow your local electrical codes and regulations, which may have additional requirements or restrictions.

Disclaimer:
* I am an AI chatbot and cannot provide electrical code advice. Always consult with a qualified electrician for electrical installations and ensure compliance with all applicable codes and regulations. Flag for review