Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Pull Box Sizing

User: Jacob Gerstner, Location: Michigan

Asked on: Thursday, September 4, 2025 at 10:01 am EDT
Answered on: Saturday, September 6, 2025 at 12:12 pm EDT

Question: Hello, I could use some help sizing this pullbox. I will attach a photo with what I need to accomplish. Thanks for any feedback.

Okay, I'm ready to help. Please provide the photo. I need to see the following information to help you size the pull box correctly: Number and size of conduits entering and exiting the pull box

I need the trade size (e.g., 1", 2", 3 1/2", etc.) of each conduit. I also need to know if it is metal or PVC.


Conduit configuration

A drawing or clear photo showing how the conduits enter and exit the box. This includes where the conduits are located in relation to each other and whether they are entering on the same wall, on opposite walls, or on adjacent walls.

Wire size and quantity

The gauge (e.g., 4/0 AWG, 2 AWG, 12 AWG, etc.) and number of conductors in
each conduit.

Whether it is a pull box or a junction box

Although they're often used interchangeably, junction boxes typically contain splices, taps, or terminations, while pull boxes are simply for facilitating wire pulling.

Voltage

While not directly affecting the sizing per se, knowing the voltage helps ensure appropriate spacing and construction of the box, especially if it's a junction box.


Code Requirements

While I can offer guidance based on general NEC (National Electrical Code) principles, it is ultimately your responsibility to comply with the applicable electrical codes in your jurisdiction. Local amendments may exist.

Once you provide the photo and the details above, I can help you determine the minimum dimensions for the pull box based on the NEC requirements. Specifically, I will focus on these sections



NEC 314.28(A) (Pull Boxes and Junction Boxes for Raceways and Cables)

This section provides the rules for sizing pull boxes and junction boxes, including specific requirements for straight pulls, angle pulls, and U pulls.

General Considerations



Straight Pulls

For straight pulls, the minimum length of the pull box must be at least eight times the trade diameter of the largest raceway.

Angle or U Pulls

For angle or U pulls, the distance from the raceway entry to the opposite wall must be at least six times the trade diameter of the largest raceway, plus the sum of the diameters of all other raceways on the same wall.

Important Notes



Derating

If the pull box is also a junction box and contains splices, you will also need to consider conductor derating based on the number of current-carrying conductors in the box. This doesn't affect the box size, but it does affect the ampacity of the conductors.

Accessibility

Ensure the pull box is accessible for future maintenance and modifications.


Manufacturer's Instructions:
Always follow the manufacturer's instructions for installation and use of the pull box.I look forward to seeing the photo and getting the necessary information! Flag for review