Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Splice

User: Lordczr, Location: Southern Shores, NC

Asked on: Thursday, September 4, 2025 at 3:25 pm EDT
Answered on: Saturday, September 6, 2025 at 12:13 pm EDT

Question: I took my North Carolina Exam. A question I have,is one the you have explained, but everyone (3) different master Electricians I have asked this to have given a different answer.Appreciate the ExplanationHere it goes:You have a 21 cu. LB with 3 - 8awg wires, how many splices are allowed?

Okay, this is a classic box fill calculation question that often trips people up, even experienced electricians! Let's break it down and see if we can resolve the differing opinions you've encountered.

Understanding the Code (NEC)

The relevant section of the National Electrical Code (NEC) that governs this is Article 314 - Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Handhole Enclosures. Specifically, we're interested in 314.16 Box Fill Calculations.Here's the core principle

Every conductor that enters the box counts towards the box fill. The code assigns a certain volume to each conductor based on its size. You can only have as many conductors as the box's volume rating can accommodate.

Breaking Down the Problem
1. Box Volume

You have a 21 cubic inch box (21 cu. in.).2.

Conductor Size

You have 3 - 8 AWG wires.3.

Number of Splices

This is what we're trying to determine. Each splice means two wires are connected together in the box.

Each conductor entering the box AND connected to the splice counts toward the box fill calculation.
NEC 314.16(B) - Conductor Fill

This section specifies the volume allowance for each conductor size. For 8 AWG conductors, the code requires 3.0 cubic inches per conductor.

The Calculation Original Conductors

You have 3 conductors
entering the box. Each requires 3.0 cu. in. fill, so 3 x 3.0 = 9 cu. in.

Remaining Volume

The box has 21 cu. in. total. After the original conductors, you have 21 - 9 = 12 cu. in. left.

Number of Splices Allowed

Each splice consists of 2 conductors
entering the box, each of which counts towards the fill calculation. So you're using 3 cu. in. x 2 conductors = 6 cu. in. of fill per splice. Therefore, you can have 12 cu. in. / 6 cu. in. per splice =

2 splices
Therefore, with a 21 cu. in. box and 3 - 8 AWG wires, you can have 2 splices.Why the Confusion with other Electricians?

Here are the most common reasons why experienced electricians might give different answers:
Forgetting the Fill per Conductor

A common mistake is to underestimate or forget to include each conductor required for each splice.

Misunderstanding "Derating"

Derating ampacity of conductors (adjusting for heat build-up when many wires are in a confined space) is entirely separate from
box fill calculations. Box fill is about volume, not ampacity.

Incorrect Assumptions About the Splice

If they assumed something like pigtailing the neutral (which is common), that would require additional conductors and affect the total.

Experience/Rule of Thumb vs. Code

Some electricians rely on "rules of thumb" gained over years of experience. While these rules can be helpful, they should always be checked against the current NEC code.


Local Amendments

Rarely, local jurisdictions might have amendments to the NEC that impact box fill. This is less likely, but still a possibility.

Grounding Conductor

In the calculation, we didn't account for grounding conductors. According to NEC 314.16(B)(5), you count all equipment grounding conductors in a box as one conductor, based on the largest equipment grounding conductor in the box. Since we do not know the size, we cannot account for it at this time.

Important Considerations
Device Fill

If the box also contains devices (switches, receptacles), you also need to factor in "device fill" according to NEC 314.16(B)(4). Each device counts as two conductors, based on the largest conductor connected to the device.

Clamps and Supports

If the box has internal clamps, cable connectors, or supports (as described in 314.16(B)(2)), they also add to the fill requirements.


Enforcement

Ultimately, the interpretation and enforcement of the NEC are up to the local inspector.

In Summary

Based strictly on the information given (21 cu. in. box, 3 - 8 AWG wires), and assuming no devices or internal clamps, you are allowed

2 splices
in the box. The key is understanding how to calculate the fill for conductors entering the box. Flag for review

Previous Question Next Question