Topic: 480V 800 AMP MLO PARALLEL RUN

User: Step by step of electric, Location: Dfw

Asked on: Thursday, September 4, 2025 at 3:57 pm EDT
Answered on: Saturday, September 6, 2025 at 12:14 pm EDT

Question: I have a client of mine which invited me to bid for power distribution in his warehouse, his warehouse has a 1900amp siemens switch board which i will need to provide a 500 ft run from the switchboard to designated power distribution, Is it proper for me to install 3 sets of 2 1/2 emt conduit with 400 mcm alumminum wire with a 1/0 copper gu wire .From the 480v distribution panel i will need to feed a 225kva transformer i know that at 480v i get 271 amps which i will need to multiply 125% for continuous loadwhich gives me 338 A and my next standard size is 350 amps is this correct because i have a supposed electrical engineer that works in the facilily that says "breaker size of the step-down transformer to 250A. Breaker protection for transformer should not be more than it's capacity"what primary side size conductor at 75c is necessary to feed a 225kva transfomer in parallel.thank you!

Okay, let's break down these calculations and address the electrical engineer's concerns.

Part 1: 1900A Switchboard to Distribution Panel (500ft Run) Your Proposal

3 sets of 2 1/2" EMT conduit with 400 MCM Aluminum wire and 1/0 Copper ground wire.


Analysis and Considerations


Ampacity of 400 MCM Aluminum

You need to consult the National Electrical Code (NEC) Table 310.16 (or the applicable local code) to determine the ampacity of 400 MCM aluminum wire at its termination temperature rating. Typically, at 75°C (which is very common for termination ratings), 400 MCM aluminum is rated for about 300-335 amps. Make sure to confirm this value in your codebook.2.

Parallel Conductor Requirements (NEC 310.10(H))

When using parallel conductors, you must ensure they are: The same length The same conductor material (aluminum in your case) The same size (400 MCM) Have the same insulation type Terminated in the same manner.3.

Total Ampacity

With three sets of conductors, your total ampacity would be approximately 3 x 300-335 amps = 900-1005 amps. This is considerably less than what is needed in this installation.4.

Voltage Drop Calculation

At 500 feet, voltage drop is a critical concern. You
must perform a voltage drop calculation to ensure that the voltage at the distribution panel is within acceptable limits (typically 3% maximum for power circuits) under full load. There are many online voltage drop calculators and formulas available. Input the length (500 ft), current (approximately 1900A) , conductor size (400 MCM Aluminum), and voltage (480V). A significant voltage drop will likely require larger conductors.5.

Grounding

A 1/0 copper grounding wire
per set is likely adequate, but you need to verify this against NEC Table 250.122 based on the size of the overcurrent protection device (the 1900A switchboard main breaker). You need a grounding conductor for each conduit run.6.

Conduit Fill

2 1/2" EMT conduit may be cutting it close. Use Chapter 9, Table 4 of the NEC to verify that 4 x 400 MCM aluminum conductors plus the grounding conductor fit within the allowable fill percentage. It's often better to upsize the conduit slightly to make pulling easier.


Recommendation



Increase Conductor Size

You likely need significantly larger aluminum conductors than 400 MCM, or consider using copper conductors (which have higher ampacity for a given size). Copper would result in smaller conduit sizes but is more expensive.


Voltage Drop Calculation is Mandatory

Don't skip this step! This will determine the necessary conductor size.

Confirm Grounding Conductor Size

Check Table 250.122 in the NEC.


Consider Bus Duct

For runs of this length and current, consider using bus duct instead of conduit and wire. It can be more cost-effective and provide better heat dissipation. Evaluate the costs of each option.

Short Circuit Withstand

Check the short circuit withstand rating of the conductor and conduit combination. You need to make sure your run can withstand any potential shorts circuits in the field.

Part 2: 480V Distribution Panel to 225 kVA Transformer
Your Calculations

225 kVA / (480V √3) = 271 amps (Correct) 271 amps 1.25 (125% for continuous load) = 338.75 amps (Correct) Next standard breaker size = 350 amps (Correct)

The Electrical Engineer's Concern: "Breaker size of the step-down transformer to 250A. Breaker protection for transformer should not be more than it's capacity"
This Statement is Inaccurate and Potentially Dangerous. The NEC specifically allows for overcurrent protection greater than the transformer's primary current, under certain conditions. The engineer's statement is overly simplistic and doesn't account for the NEC's transformer protection rules. NEC Transformer Primary Protection Rules (NEC 450.3(B))

This section is crucial. You need to refer to it directly in the NEC. The specific rules depend on whether you have primary-only protection or primary and secondary protection.

Primary-Only Protection

NEC 450.3(B)(1) allows you to use a primary-side overcurrent protection device (breaker) rated at up to 125% of the transformer's primary current rating (271 amps).
This is what you calculated and proposed, and it is generally acceptable as a starting point. 1. 25 x 271 = 339 amps which goes to your next standard size which is 350 amps.

Primary and Secondary Protection

If you have overcurrent protection on both the primary and secondary sides of the transformer, the primary protection can be smaller. However, this requires careful coordination.

Why the 125% Rule?
The 125% rule is there to allow for normal transformer inrush current when it's energized. Transformers can draw significantly higher current for a short period when they are first switched on. A breaker sized too tightly to the transformer's steady-state current would nuisance trip. Your proposed 350A breaker on the primary side is likely acceptable if it's primary-only protection and you are following NEC 450.3(B)(1). However, to be absolutely sure:1. Consult NEC 450.3(B) directly. Understand the requirements.2. Review the Transformer Nameplate

The transformer nameplate may have specific overcurrent protection recommendations.3.

Consider the Downstream Load

What is the load on the secondary side of the transformer? A larger load might require a larger primary breaker (within the NEC limits).4.

Coordination Study

For larger transformers, a coordination study is often recommended to ensure that the overcurrent devices (breakers and fuses) trip in a coordinated manner to minimize downtime.

Part 3: Parallel Conductor Size for 225 kVA Transformer Feed
You Need to Provide More Information: To determine the correct conductor size, I need to know: Material

Aluminum or Copper?

Termination Temperature Rating

Usually 75°C or 90°C (Check equipment ratings)


Number of Conductors per Phase

Are you planning on 2, 3, or more parallel conductors per phase?

Conduit Type

EMT, PVC, etc. (Affects ampacity due to derating)


Distance
: Length of the run from the distribution panel to the transformer. Example Calculation (Assuming Copper, 75°C, 2 Conductors per Phase, Short Distance)


Total Current

338.75 amps (as calculated above).
2.


Current per Conductor

338.75 amps / 2 conductors = 169.375 amps.
3.


NEC Table 310.16

Look up the ampacity of copper conductors at 75°C. You'll likely find that a 2/0 AWG copper conductor is rated for around 175 amps.4.

Adjustment/Derating Factors

Are there any adjustment or derating factors that apply (e.g., more than 3 current-carrying conductors in a raceway)? If so, you'll need to increase the conductor size to compensate.5.

Voltage Drop

Even for short distances, check voltage drop!6.

Grounding

Determine the appropriate grounding conductor size based on the overcurrent device (350A breaker). (NEC Table 250.122).


Important

Provide the missing information above, and I can give you a more accurate conductor size recommendation.

In Summary


The 500ft run needs a serious review and recalculation.
Consider bus duct.2. The engineer's statement about transformer protection is incorrect in its simplicity. Follow NEC 450.3(B). Your proposed 350A breaker may be acceptable.3. Provide the missing information for the transformer feed conductor size calculation.Disclaimer: I am an AI chatbot. This information is for general guidance only. Electrical work is dangerous and must be performed by qualified professionals. Always consult the National Electrical Code (NEC) and all applicable local codes, and hire a licensed electrical engineer for design and approval. Flag for review