Topic: Sub panel conductor size

User: MR.DEI, Location: Hollister,CA

Asked on: Thursday, September 4, 2025 at 5:12 pm EDT
Answered on: Saturday, September 6, 2025 at 12:14 pm EDT

Question: I have a 200amp sub panel fed from a 200amp breaker with 2/0 THHN. Article 240.2(B) (2) indicates if it does not correspond to the standard amperage rating the conductor can be one size smaller. Article 240.6(A) table shows 200amp as standard rating, so if 200amp is a standard should the conductor be 3/0? In the past I have always use this rule without knowing the standard rating. Can anyone clarify this interpretation?Thanks,

You've hit on a common point of confusion with the "next higher standard overcurrent device" rule. Let's break it down and clarify

Understanding the Relevant NEC Sections:
Article 240.4(B)

This is the
general rule allowing you to use the next higher standard overcurrent device. It applies only if all of the following conditions are met:1. The ampacity of the conductors has been calculated after all applicable adjustment and correction factors have been applied (like ambient temperature or conduit fill).2. The conductor ampacity does not correspond with the standard ampere rating of a fuse or circuit breaker as listed in 240.6(A).
3. The next higher standard overcurrent device rating selected
does not exceed 800 amperes.4. You are not dealing with any of the specific exceptions listed in 240.4(C) through (G), which includes (but is not limited to) fixture wires, flexible cords, motor circuits, air conditioning circuits, and certain tap conductor rules.


Article 240.6(A)

This lists the standard ampere ratings for fuses and circuit breakers. 200 amps is a standard rating.

Your Specific Situation

You have a 200 amp subpanel fed from a 200 amp breaker. You are using 2/0 THHN copper conductors. Per NEC table 310.16, 2/0 THHN in a raceway has an ampacity of 175 amps in the 75 degree column. (check your temperature rating to be sure).

Therefore, 2/0 THHN (175A) does NOT correspond to the standard ampere rating of 200A (240.6(A)).
Applying the Rule

Since 2/0 THHN (175A) does NOT correspond to the standard ampere rating of 200A. You CAN use the next size up as long as you meet the other conditions outlined in article 240.4 (B).In your case the next size up available is a 200 amp breaker, and the other conditions of 240.4 (B) are met, so you are able to use this rule.If you were to use 3/0 THHN, it has an ampacity of 200A. This DOES correspond to the 200A breaker and you would not be able to use the next size up rule.

Important Considerations



Voltage Drop

Always consider voltage drop. Even if the conductors are code-compliant for ampacity, excessive voltage drop can cause equipment malfunction and is a violation of NEC 210.19(A)(1) FPN No. 4 and 215.2(A)(1) FPN No. 2. Longer runs require larger conductors to minimize voltage drop.


Local Amendments

Some jurisdictions amend the NEC. Always check with your local electrical inspector for any local requirements that might supersede or modify the NEC.

Professional Advice

If you are unsure,
always* consult with a licensed electrician. Electrical work can be dangerous, and improper installations can lead to fire, injury, or death.

In Summary:


Using 2/0 THHN feeding a 200 amp subpanel from a 200 amp breaker is compliant according to the 2020 NEC. Flag for review