Topic: Portable Fuel Cell

User: BDamage707, Location: Marion NC

Asked on: Thursday, September 4, 2025 at 6:42 pm EDT
Answered on: Saturday, September 6, 2025 at 12:14 pm EDT

Question: The company I work for has bought some of these portable fuel cubes Fuel Cubes . They poured a concrete pad to set them on and had a contractor install an open-walled carport roof over them to protect them from the weather. They currently have DC pumps with the battery clips on the end of the wiring. They have previously bought some of these and wired them using solar panels and a charge controller to power them up.When I went to the company website to look for specifications, I noticed that if you wanted to purchase one of these, you first had to pick gasoline or diesel for your fuel. Besides coming with a vent kit, the one thing that stands out to me is that if you choose "diesel", you have the option of an AC or DC motor. However, if you choose "gasoline", you are only able to select one of 2 sizes of AC motor.I go to look at the tanks we have on site, and the nameplate on the pump motor says it is "Class 1, Div 2," which I think makes perfect sense for a DIESEL-rated setup.But I am thinking that to be compliant, to use this with gasoline, the AC motor must be "Class 1, Div 1" ... am I thinking correctly, or is there an exception that I might be overlooking?The supplier that they purchased these from hasn't been much help, he has been trying to contact the manufacturer, but so far I have not had any luck obtaining any information from them.

You're right to be concerned. Here's a breakdown of why your concern is valid and what to consider

Understanding Hazardous Locations (Class/Division):
Class I

Locations where flammable gases or vapors are or may be present in the air in quantities sufficient to produce explosive or ignitable mixtures.
This is your concern with gasoline.



Division 1

A location where ignitable concentrations of flammable gases, vapors, or liquids: Exist under normal operating conditions. Exist frequently because of repair or maintenance operations or because of leakage. Might exist because of equipment breakdown or faulty operation.

Division 2

A location where ignitable concentrations of flammable gases, vapors, or liquids: Are handled, processed, or used, but are normally confined within closed containers or closed systems from which they can escape only in case of accidental rupture or breakdown of such containers or systems, or in case of abnormal operation of equipment. Are prevented by positive mechanical ventilation from accumulating in hazardous concentrations, and where safeguards against failure of the ventilation system are provided. Are adjacent to a Class I, Division 1 location, and occasionally the ignitable concentration might be communicated.

Why the Difference Between Gasoline and Diesel



Vapor Pressure

Gasoline has a much higher vapor pressure than diesel. This means it evaporates much more readily, creating flammable vapor concentrations more easily and frequently. Diesel's lower vapor pressure means it's less likely to form an ignitable mixture in normal operation, leading to the allowance of Division 2 rated equipment in many diesel applications.

Ignition Temperature

Diesel has a lower flashpoint and autoignition temperature than gasoline.

Why a Class I, Division 2 Motor
Likely Isn't Sufficient for Gasoline

Because of gasoline's tendency to vaporize and create flammable concentrations even under normal operating conditions, a Class I, Division 2 rating is generally
not considered adequate for a gasoline dispensing application. The risk of a flammable atmosphere existing during normal filling operations is too high.

This is particularly true in an open-air carport-covered environment. A Division 2 rating is based on the assumption that flammable concentrations are
not normally present.

What You
Likely Need



Class I, Division 1 Equipment

You are likely correct. Equipment used directly for gasoline dispensing, especially the motor, should generally be rated for Class I, Division 1. This means it's designed to contain any ignition within the device itself, preventing it from igniting the surrounding atmosphere. This type of equipment is more robust and expensive.

National Electrical Code (NEC) and Other Regulations

The NEC (specifically Article 514 for gasoline dispensing facilities) is the primary standard in the US, but your local authorities having jurisdiction (AHJ) may have additional requirements. You
must consult the NEC and local codes.

Things to Consider and Investigate Further


Manufacturer's Documentation

Keep pressing the supplier and the manufacturer for documentation. You
need the manufacturer's certifications and listings for the equipment, explicitly stating its suitability for gasoline dispensing. Look for UL listings, FM approvals, or similar certifications from recognized testing laboratories.2.

Area Classification Study

Ideally, a qualified person should conduct an area classification study for your specific installation. This involves evaluating the potential for flammable vapors and determining the appropriate hazardous area classifications (Class, Division, and Zone if applicable). This is something a professional electrical engineer or industrial hygienist can do.3.

Venting and Ventilation

While you have a carport roof, it sounds like the sides are open, which is good. Proper ventilation is
crucial. However, natural ventilation alone might not be enough to justify a less stringent hazardous area classification. The study (above) would determine if the ventilation is adequate.4.

Grounding and Bonding

Proper grounding and bonding are critical to prevent static electricity buildup, which could be an ignition source.5.

Emergency Shut-Off

Ensure there's a readily accessible emergency shut-off switch to cut power to the pump in case of a spill or other problem.6.

Signage

Post clear "No Smoking" and "Shut Off Engine" signs.7.

Employee Training

Train employees on safe fueling practices, spill prevention, and emergency procedures.8.

Consult a Qualified Electrician/Engineer

This is not a DIY situation. You need a qualified electrician
experienced in hazardous locations to inspect the installation and ensure it meets all applicable codes and standards. They can also advise on the best way to upgrade the system to meet gasoline dispensing requirements.9.

Insurance Company

Notify your insurance company about the installation. They may have specific requirements for gasoline storage and dispensing.

In Summary:
*Your concern about the Class I, Division 2 motor is well-founded. It's highly likely you need Class I, Division 1 equipment for gasoline dispensing, especially given the open-air carport setup. Contact the manufacturer of the tanks, a qualified electrician, and your insurance company immediately. Do not use the system for gasoline until you've had it inspected and approved by a qualified professional and you have documentation to prove the equipment is safe for that use. It's better to be safe than sorry when dealing with flammable liquids. Flag for review