Topic: 1200 amp federal pacific mdp

User: pszwayka, Location: Pennsylvania

Asked on: Friday, September 5, 2025 at 9:59 am EDT
Answered on: Saturday, September 6, 2025 at 12:15 pm EDT

Question: Good afternoonI have a customer that had a 1200 amp 3 phase fpe main distribution panel in a building they are looking to buy. My question is do the larger breakers have the same problems as the smaller smaller fpe breakers

Good afternoon! That's a very important question when considering a building with an FPE panel, especially one of that size.

The short answer is: Yes, the larger FPE breakers (including those in a 1200A panel) are subject to the same types of issues and failures as the smaller ones.

Here's a breakdown of why and what to consider: Core Problem: Design Flaw

The fundamental issue with FPE breakers isn't just size-dependent. It stems from inherent design flaws that affect their ability to trip reliably under overload or short-circuit conditions. These flaws were present across their entire product line. The primary issue was their failure to trip under overload conditions, posing a significant fire hazard.


Testing and Certification Issues

The issues with FPE's UL listing apply to the entire product line. There is evidence that FPE manipulated testing procedures and fraudulently obtained UL listings for their breakers.

Age and Deterioration

The age of these panels (many are decades old) adds another layer of risk. Components degrade over time. Lubricants can dry out, contacts can corrode, and mechanisms can become stiff, further hindering proper breaker operation. This aging effect is amplified by the high current loads these larger breakers carry.


The Larger the Load, the Larger the Potential Consequences

While a failed smaller breaker might only affect a single circuit, a failure in a large breaker in a main distribution panel can have far more significant consequences. It could potentially overload downstream breakers and wiring, leading to a much larger fire or safety hazard.

What to do


Full Panel Replacement is the Recommended Best Practice

The safest and most recommended course of action is to completely replace the FPE main distribution panel with a modern, reliable system from a reputable manufacturer. This eliminates the known risks associated with FPE equipment.2.

Thorough Professional Inspection (Considered a Minimal Step, Not a Solution)

If replacement isn't immediately feasible, have the entire panel, including every breaker, thoroughly inspected by a qualified electrical engineer experienced with FPE equipment. They should: Visually inspect for signs of overheating, corrosion, arcing, or physical damage. Perform dynamic testing on each breaker to verify its tripping characteristics. Static testing (like just measuring resistance) is not sufficient. Document all findings and provide a detailed report outlining the risks and recommended actions. Understand that even a clean bill of health from an inspection doesn't eliminate the inherent design flaws and potential for future failure.3.

Documentation

Get the manufacturer date for the panel and breakers. Research any documented issues specific to that manufacturing period.

Important Considerations for Your Customer



Safety First

Emphasize that the presence of an FPE panel represents a significant safety hazard. The risk of fire and electrical shock should be the primary concern.


Insurance Implications

Many insurance companies are hesitant to insure buildings with FPE panels due to the known risks. Replacing the panel can often improve insurability and potentially reduce premiums.

Due Diligence

Your customer should factor the cost of replacing the panel into their purchase negotiations.


Don't Delay

If the customer proceeds with the purchase, schedule the panel replacement as soon as possible. Don't postpone it.

In summary, while a thorough inspection is essential if replacement isn't immediately possible, the long-term solution and best practice is to replace the FPE main distribution panel. The risks associated with these panels are well-documented, and the potential consequences of a failure are too great to ignore.


Let me know if you have any other questions! I'm here to help you advise your customer. Flag for review