Question: Hello! I am preparing for my journeysman exam which I am taking soon and I purchased Mike holts examination preparation course and I came across something that gave me a hard time and I’ll post the question below:c) 10 AWG440.33Conductor Ampacity = (25A × 125%) + 2AConductor Ampacity = 31.25A + 2AConductor Ampacity = 33.25AConductor Size = 10 AWG, rated 30A at 60°C, 110.14(C)(1)(a)(2) and Table 310.16What I don’t get is why is the conductor a parity above the ampacity of 10 awg? I thought the ampacity always had to be bigger than the calculated amps. Thanks for your time and knowledge!
Okay, let's break down why the 10 AWG conductor is acceptable in this Mike Holt example, even though the calculated ampacity (33.25A) is slightly above the 30A rating of 10 AWG at 60°C. This comes down to specific code interpretations and overload protection rules, which can be a tricky area on the journeyman exam.Here's the rationale, based on the NEC and the context provided by Mike Holt
Understanding the Context (This is Key!)
440.33 (Part of Article 440: Air-Conditioning and Refrigerating Equipment)
This code section is critical. Article 440 has specific rules for sizing conductors serving motor-compressors, which often allow for the next size up in certain circumstances. This is because motor-compressors have unique starting characteristics.
Continuous Load + Small Load
The calculation indicates a continuous load (25A 125%) plus a small, non-continuous load (2A). This suggests the 25A load is likely the motor-compressor itself.
Why 10 AWG is Acceptable According to Mike Holt (and often the NEC)
440.22(A) Single Motor-Compressor
This section typically states conductors supplying a single motor-compressor must have an ampacity not less than 125% of the motor-compressor's rated-load current. This is what drives the 25A 125% calculation.2.
440.33 : Branch-Circuit Overload Protection
This is where the leeway comes in. It allows to use the next standard size fuse/breaker when the calculated overload protection does not match a standard size.3.
The "Next Size Up" Rule and Overcurrent Protection
The most important consideration here, and often overlooked, is the OVERCURRENT PROTECTION. Even though the calculated conductor ampacity is 33.25A, the overcurrent protection device (fuse or breaker) must be sized appropriately to protect the conductor from overload.
If the overcurrent protection is 30A or less
The 10 AWG conductor is likely compliant, as it's protected against overcurrent. The NEC expects the overcurrent device to limit the current through the conductor to its rated ampacity (or below).
If the overcurrent protection is larger than 30A
The 10 AWG conductor would likely not be compliant. You can't use an oversized breaker and still claim the conductor is protected. You'd need to upsize the conductor.
Important Considerations for the Exam
Overcurrent Protection is Paramount
Always think about the overcurrent protection device when sizing conductors. Is it protecting the conductor?
Read the Question Carefully
Pay close attention to the specific loads (motor-compressors, continuous loads, etc.) and the references to specific code sections (Article 440 in this case).
Mike Holt's Interpretation
Mike Holt is generally very conservative in his interpretations, but he also emphasizes understanding the intent of the code. In this case, the intent is to allow for the inrush current of the motor-compressor while still protecting the conductor from overload.
Table 310.16
Understand Table 310.16, which gives the ampacity of conductors based on their size and insulation type (and temperature rating).
110.14(C)
This section deals with the termination temperature ratings of equipment. The 60°C rating is often a limiting factor, as many older devices are only rated for 60°C.
In Summary
The 10 AWG conductor in the Mike Holt example is likely acceptable if and only if the overcurrent protection is properly sized to protect the conductor at or below its 30A rating (taking into account any adjustments or corrections needed). This example highlights the interaction between conductor ampacity, load calculations, and overcurrent protection. This principle is especially important for motor-compressor circuits governed by Article 440.
Final Advice for the Exam: If you're unsure, err on the side of oversizing the conductor. Always consider the overcurrent protection. Read the question carefully and identify any specific code references.* Understand the context of the application (motor-compressor, continuous load, etc.).Good luck on your journeyman exam! Flag for review