Question: I searched a couple topics but nothing really clarified. I have a few books but cant really narrow down the address in NEC. Is the GEC at Service disconnect need to be on same buss as neutral or equipment frame? I recently ran service call at a multi family dwelling I noticed a common GEC wire tied to each service disconnect with mechanical lug per disconnect

You're right to be looking for clarity on this, as proper grounding and bonding are critical for safety. Here's a breakdown of the relevant NEC requirements, specifically related to your question about the GEC connection at the service disconnect and multifamily dwellings

NEC Requirements and Explanation
NEC 250.24(C): Grounded Conductor Brought to Service Equipment

"Where an ac system operating at 50 volts to 1000 volts is grounded at any point, the grounded conductor shall be run to each service. This conductor shall be routed with the ungrounded conductors and shall not be smaller than specified in Table 250.102(C)(1).
This grounded conductor shall be connected to each service disconnecting means enclosure." This is stating that the neutral conductor is required to be run to each service disconnect enclosure

NEC 250.24(D): Main Bonding Jumper

"For a grounded system, an unspliced main bonding jumper shall be used to connect the equipment grounding conductor(s) and the service-disconnect enclosure to the grounded conductor within the enclosure for each service disconnect. Where more than one service disconnecting means is located in an assembly, the main bonding jumper shall be installed at each service disconnecting means."

NEC 250.24(A)(1): Grounding Electrode Conductor Connection Location

"The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded conductor is connected at the service equipment as provided in 250.24(A)(1) through (5)."


NEC 250.28 Main Bonding Jumper and System Bonding Jumper.
This article goes into the requirements of the main bonding jumper.

In Summary1. GEC Connection Point

The Grounding Electrode Conductor (GEC) connects to the

grounded conductor
(neutral) at the service equipment.2. Main Bonding Jumper

The main bonding jumper connects the

grounded conductor
(neutral) to the service enclosure and the equipment grounding conductors.3. Same Bus/Location

This effectively means the GEC, grounded conductor (neutral), and the equipment grounding (the enclosure) are all connected at the service equipment, typically at the neutral bus.

Therefore, the GEC must be connected to the grounded conductor bus (typically the neutral bus) at the service equipment.
Regarding your multi-family dwelling observation



Multiple Service Disconnects

In a multi-family dwelling with individual service disconnects for each unit, each service disconnect needs to comply with the rules above.


Common GEC

It is permissible to have a common GEC run to multiple service disconnects. The size of this common GEC must be sized according to NEC Table 250.66 based on the size of the largest service entrance conductor.

Mechanical Lugs

Connecting the GEC to each service disconnect with mechanical lugs is a common and acceptable practice,
provided the lugs are listed for the purpose. The lugs should be properly sized for the conductor and tightened according to the manufacturer's instructions.

Ensuring Continuity

The key thing to verify is that each service disconnect enclosure is effectively bonded to the grounded conductor (neutral). The common GEC provides the grounding path to the grounding electrode system, and the main bonding jumper at each service disconnect ensures that the enclosure and equipment grounding conductors are properly connected to the neutral.

Important Considerations for Multi-Family Dwellings
Qualified Person

Installation, maintenance, and troubleshooting should be performed by qualified electrical personnel.


Local Amendments

Always check with local amendments to the NEC, as requirements can vary.*

Documentation

Proper documentation is critical, especially for multi-family dwellings. Accurate records of the grounding and bonding system, including conductor sizes and connections, are essential for future maintenance and troubleshooting.

In Conclusion


The grounding system in a multi-family dwelling with multiple service disconnects requires careful attention to detail to ensure the safety and reliability of the electrical system. Flag for review