Topic: How different are actual and calculated loads? Case study.

User: brycenesbitt, Location: United States

Asked on: Sunday, September 7, 2025 at 2:54 am EDT
Answered on: Sunday, September 7, 2025 at 2:54 am EDT

Question: I did a quick load study for a multifamily apartment. Here's the 2 bedroom unit load calculation, alternative method, based on the 2023 NEC:NEC Section §220.82 Determining Existing Loads : Two Bedroom Units#xtotalGeneral light, power @3 volt-amperes75032250vaKitchen appliance circuits (min 2 @ 1,500 va)150023000vaLaundry circuits (minimum 1,500 va)150000vaDryer (NP rating)720000vaElectric range (12.1 kW table 220.55)800018000vaWall mounted oven (NP rating)00vaDishwasher (nameplate)144011440vaDisposal (nameplate)114011140vaOther720000vafirst 10k of load10000va40% after first 10k2332vaheating load4800419200vasingle unit load31532vaconvert to amps240131A

Okay, let's break down your load calculation and see if we can identify any potential issues or areas for improvement. I'll focus on areas where the NEC might provide more specific guidance or where assumptions need clarification.

Analysis of Your Load Calculation General Lighting & Power (75032250 VA)

Your calculation implies a unit size of 750 square feet (3VA/sq ft
750 sq ft = 2250 VA). This is a reasonable approach based on the NEC's general lighting and receptacle load requirement. Be sure the actual apartment square footage closely matches.

Kitchen Appliance Circuits (3000 VA)

Correct. NEC requires a minimum of two 20-amp small appliance branch circuits for the kitchen, each rated at 1500 VA (2 x 1500 VA = 3000 VA).


Laundry Circuit (0 VA)

This seems unusual for a multifamily apartment. Most apartments, even if they don't have in-unit laundry, have a provision for a laundry area or require that they provide a space to hook up a washing machine. Verify if the unit has any laundry connection, if so include a laundry circuit minimum of 1500VA.

Dryer (0 VA)

You show that there is no laundry circuit. If no laundry hookup, dryer is correct.


Electric Range (8000 VA)

You use 8 kVA from Table 220.55. That table has the demand factor for ranges. You have to look at the nameplate rating for the range. If the range is < 3.5kW or over 12 kW then the table demands are different. You said that the range is rated at 12.1 kW which would mean that your calculation is correct.

Wall Mounted Oven (0 VA)

If the apartment does not have a wall mounted oven, this is correct.


Dishwasher (1440 VA) & Disposal (1140 VA)

Assuming these are the nameplate ratings, these are acceptable. However, always double-check the actual appliance ratings during installation to ensure accuracy.

Other (0 VA)

Be very cautious about this. Consider:


Garbage Disposal

Are you sure there isn't one? If so, include its nameplate rating.

Microwave

Though often plugged into a general-purpose circuit, a built-in microwave could be significant enough to warrant consideration.


Window AC Units/Portable Heaters

If the apartments might use these, it's wise to add a small allowance for potential load, even if not guaranteed.

Specialty Outlets

Balcony outlets for electric grills, etc.


Applying the Demand Factor (NEC 220.82)

You are correct in using the NEC 220.82 alternative calculation. You take the first 10 kVA at 100% and the remainder at 40%.

Final Amps (131 A)

Your conversion to amps (31532 VA / 240 V = 131 A) seems correct based on your calculated VA.

Potential Concerns & Suggestions
1. The "Other" Category

The biggest concern is the "Other" category being zero. Revisit the unit and its potential appliance usage. Even a small allowance (e.g., 1000 VA) might be prudent.2.

Washer and Dryer

Confirm if units have the hookups for a washer and dryer. If so you must include the minimum loads.

Important Notes & Disclaimer
Local Codes

Always consult your local electrical codes. They may have stricter requirements or amendments to the NEC.

Future Expansion

Consider the possibility of future upgrades or additions by tenants. Overestimating the load slightly can save headaches later.


Qualified Electrician

This analysis is for informational purposes only. A licensed and experienced electrician should perform the final load calculations and determine the appropriate service size.

Accuracy of Nameplate Data

The load calculation relies on accurate nameplate ratings for appliances.


Diversity Factors

The NEC's alternative method incorporates some diversity. Be careful not to double-count diversity by applying it again later in your calculations for the overall building service.*

HVAC:
You listed heating load, but did not list if there were any AC units. If there are, be sure to include the nameplate load.In summary, your calculation appears generally sound based on the information provided, but it's crucial to thoroughly investigate the "Other" category, verify appliance ratings, and double-check local code requirements. It is always better to overestimate than underestimate when performing load calculations. Flag for review