User: conrad503, Location: Portland, OR
Asked on: Monday, September 8, 2025 at 1:58 am EDT
Answered on: Monday, September 8, 2025 at 5:54 am EDT
Question: I'm helping a friend of mine so some renovation in the basement of his home. He has a temporary service panel on a hill with two 20 amp breakers that are designed to feed the receptacles in the panel. He's hardwired a 10/3 conductor from one two pole breaker to a service panel inside the structure approximately 40 feet away. The panel has two 20 amp breakers. One feeds a single 240v receptacle and one feeds a duplex 120v receptacle attached to the panel enclosure. Currently, the panel has a single neutral/ground bus which is bonded to the chassis. This bus is ultimately connected via the 10/3 to the neutral and ground of the temp service panel on the hill, which is itself grounded to earth via an 8' rod. The grounds and neutral terminals of both the receptacles on the panel are also connect to this single bus.I'd like run equipment from this interior panel without concerns about safety. Can someone verify that this is the proper configuration please? Or does something need to be hooked up differently. Specifically, is it proper to have a single bus for both ground and neutral, and should this bus be bonded to the panel chassis.Yes, I am aware that there are many reasons why this could be a bad idea/in violation of the NEC/local codes, etc., but due to the very inconvenient location of the temp pole, I think it's highly likely it will remain until the weather head and permanent service panel are installed in a few months. Thanks for any input.
Okay, let's break down your friend's temporary setup and address the safety concerns. It sounds like he's trying to create a subpanel inside the basement fed from the temporary service on the hill. While I cannot provide definitive code compliance advice since I don't know your local codes, here's a critical safety assessment
MAJOR CONCERNS & REQUIRED FIXES:
Neutral-Ground Bond
This is the biggest problem and creates a very dangerous situation. In a subpanel (the panel inside the basement), the neutral and ground must be kept SEPARATE. Bonding the neutral and ground together at the subpanel creates a parallel path for neutral current. That neutral current will flow through the equipment grounding conductors (the grounds in your cords, the metal enclosures of appliances, etc.). This means a potentially live metal chassis on everything connected to the panel. This is dangerous and a recipe for electrical shock. SOLUTION
Remove the bonding screw or strap that connects the neutral bus to the panel enclosure (chassis) in the basement panel. It sounds like this connection already exists; you need to remove it. The bonding only happens at the main service panel (in this case, the temp service panel on the hill).2. Install a separate ground bus bar in the basement panel. This is where all the equipment grounding conductors (bare or green wires from the receptacles, and any ground wires from the 10/3 cable) will connect. It is OK to BOND this ground bus bar to the metal chassis of the basement panel.3. The neutral bus bar should only have the neutral wire from the 10/3 cable and the neutral wires from the 120v receptacle connected to it. Grounding
With the Neutral-Ground Bond fixed, the ground wire in the 10/3 cable (assuming it's correctly connected back to the temporary service panel) should provide a sufficient grounding path. The ground rod at the main service panel on the hill is essential.
Conductor Size
The 10/3 conductor from the temporary service to the interior panel should be adequately sized for the load that will be placed on the circuit. Since the breakers in the temporary service panel are 20 amp breakers, and the breaker in the interior panel is also a 20 amp breaker, the 10/3 conductor would typically be code compliant.
Overcurrent Protection (Breakers)
The breakers in the basement panel are adequate and well suited for the receptacles they serve.
Verified Items The interior panel serves two receptacles. One 240V receptacle, and one 120V receptacle.
Diagram
Here's a conceptual diagram to help visualize the corrected wiring (this is a simplified representation and not a substitute for proper electrical knowledge and adherence to local codes)
Temporary Service Panel (Hill)
Two 20A Breakers (Double Pole) 10/3 Cable to Basement Panel (4 wires: Black, Red, White, Green/Bare) Neutral and Ground BONDED together Ground RodBasement Panel (Subpanel) Neutral Bus
White wire from 10/3 cable Neutral wire from 120V Receptacle
NO BOND TO PANEL CHASSIS Ground Bus
Green/Bare wire from 10/3 cable Ground wires from both receptacles
BONDED to Panel Chassis 240V Receptacle: Black and Red wires from 10/3 to 2-pole breaker 120V Receptacle: Black wire from 10/3 to breakerImportant Safety Reminders
Power Off
ALWAYS work with the power OFF. Double and triple-check.
Testing
After making these changes, use a multimeter to verify: No voltage between the neutral bus and the panel enclosure. Proper voltage at the receptacles.
GFCI Protection
Strongly consider adding GFCI protection to the 120V receptacle, especially in a basement environment.
Disclaimer: I am an AI Chatbot. This information is for general guidance only and should NOT be considered a substitute for the advice of a qualified, licensed electrician. Incorrect wiring can lead to fire, electrical shock, and other serious hazards. Your friend should consult with a licensed electrician to ensure the wiring is safe and code-compliant. Flag for review