Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: TIA 1474

User: TwistLock, Location: California

Asked on: Monday, September 8, 2025 at 10:57 am EDT
Answered on: Monday, September 8, 2025 at 11:04 am EDT

Question: NEC 2020 TIA 20-8 Reference: 551.71(F) TIA Log #14741. Revise 551.71(F) to read as follows:551.71(F) GFCI Protection.All 125-volt, single-phase, 15- and 20-ampere receptacles shall have listed ground-fault circuit-interrupter protection forpersonnel. The GFCI devices used in RV site electrical equipment shall not be required to be weather or tamper resistantin accordance with 406.9 and 406.12.Informational Note: The percentage of 50 ampere sites required by 551.71 could be inadequate for seasonalrecreational vehicle sites serving a higher percentage of recreational vehicles with 50 ampere electrical systems. In thattype of recreational vehicle park, the percentage of 50 ampere sites could approach 100 percent.Ground-fault circuit-interrupter protection shall be provided as required in 210.8(B). GFCI protection shall not berequired for other than 125-volt, 15- and 20-ampere receptacles used in the recreational vehicle site equipment.Informational Note No. 1: Appliances used within the recreational vehicle can create leakage current levels at thesupply receptacle(s) that could exceed the limits of a Class A GFCI device.Informational Note No. 2: The definition of Power-Supply Assembly in 551.2 and the definition of Feeder in Article100 clarifies that the power supply cord to a recreational vehicle is considered a feeder.(Apologies if this has been discussed before):I read this TIA as RV 'Parks'. Not residential. Residential being covered in 210.8. So an exterior residential 30a/50a receptacle (for an RV) would require GFCI as well as WR. Again with the WR rating for 50a receptacles not becoming effective until 2026 only applying to RV 'Parks'.Am I misinterpreting ?

You're reading the TIA and its implications fairly accurately, with a couple of minor clarifications needed. Let's break it down: TIA 20-8 and 551.71(F): Focus on RV Parks

The TIA
specifically addresses GFCI requirements within

recreational vehicle sites
which are defined as dedicated section of land provided for the accommodation of recreational vehicles used for temporary human habitation.. The change clarifies that while GFCI protection is required for 125V, 15A and 20A receptacles at these sites, weather-resistance (WR) and tamper-resistance (TR) are not mandatory (406.9 and 406.12) for the GFCI devices used within the RV site equipment itself. Residential Applications and 210.8(B)

You are correct that

residential
installations of 30A and 50A receptacles for RVs fall under 210.8(B). This section mandates GFCI protection for all 240V outlets up to 50 amps (among others) installed in specific locations. This applies to an outlet intended for RV use at a residence. The 2023 code also mandates weather resistance for receptacles installed in damp or wet locations, which is most outside receptacles. Weather-Resistance and the 2026 Effective Date

It's important to note that you are referencing the 2020 code. While there may be some localities that are still on the 2020 code, the 2023 code is now active, which makes weather resistance mandatory. The TIA is only referring to weather resistance in RV parks.
The 2020 version of the code did not have a sunset on the requirement for WR receptacles The 2023 version of the code mandates WR on all receptacles installed in damp or wet locations.

Summary of Your Understanding



RV Parks (551.71(F) with TIA 20-8)

GFCI
required for 125V/15A/20A receptacles. WR is not required for the GFCI device itself.

Residential RV Outlets (210.8(B))

GFCI required for 240V receptacles up to 50 amps. WR receptacles required as outlets are in wet locations.

Clarifications


"RV Site Electrical Equipment":
The TIA is referring to things like the pedestal or power outlet assembly that provides the RV hookup in the RV park. The GFCI protection is required, but the GFCI device used in that equipment doesn't have to meet WR and TR standards.In conclusion, your interpretation is largely correct. The TIA clarifies the requirements for GFCI protection within RV parks, leaving the residential installations to be governed by 210.8(B) and WR. Flag for review

Previous Question Next Question