Question: When supplying power to multiple 208V fan coil units with an RLA of 1.5 amps, 2.5 amps, etc., does each FCU require individual short circuit & ground fault protection (i.e. fused at 15 amps in each local disconnect)? Or can a single 15A circuit breaker circuit multiple FCU's without needing individual SCGF protection at the unit (local disconnect only)?Applying 430.53(A) Not Over 1 Horsepower, I don't see any guidance on how many fan coil units you can connect in a single 15A circuit. 430.53(B) indicates that branch circuit will not open. But I don't see this mentioned as a bullet point in 430.53(A). Am I missing something?
Okay, let's break down the NEC requirements for supplying power to multiple 208V fan coil units with small motors and figure out whether you need individual fused disconnects or if a single circuit breaker can handle multiple units.
Understanding the Relevant NEC Sections 430.53(A) Not Over 1 Horsepower
This section is likely the most relevant to your situation. It allows you to protect motors not over 1 horsepower with an overcurrent device sized based on Table 430.52. This section also details that the installation complies with 430.53(C).
430.53(B) Over 1 Horsepower
This section is applicable to motors larger than 1 horsepower, which doesn't seem to be the case here.
430.53(C) Other Group Installations
This section outlines the conditions that must be met when you have multiple motors (including fan coil units) connected to a single branch circuit.
This is the key to your question. 430.55 Combined Overcurrent Protection
This section deals with situations where the motor and other loads are on the same circuit and discusses the sizing of the overcurrent device for the overall circuit. Likely applies to your situation.
Analysis and Code Requirements
Here's a breakdown of how the code applies to your scenario:1. Individual Overcurrent Protection is NOT Necessarily Required at Each FCU
NEC does
NOT require individual SCGF protection at each fan coil unit. It IS permissible to have multiple small motors (like those in your fan coil units) on a single branch circuit, as long as you meet the requirements of 430.53(C).
2. Meeting the Requirements of 430.53(C) (Other Group Installations)
This is where the specifics come in. To put multiple fan coil units on one circuit, you must meet all of the following conditions outlined in 430.53(C):
(1) Protection of the Motor
Each motor must be individually protected against overload per 430.32 (Overload Protection). This usually means the motor has an integral thermal protector or an external overload relay. Most fan coil units have this built in. Look for a marking on the motor or in the product documentation that states that it is "thermally protected" or has "inherent overload protection." If they don't, you must provide separate overload protection (which gets complex and often makes separate circuits more practical). If motors do not have built-in thermal protection (overload protection) you are NOT able to combine.
(2) Rating of Overcurrent Device
The branch-circuit overcurrent device (your 15A breaker) cannot be larger than the smallest rating or setting of the short-circuit and ground-fault protective device for any motor in the group plus the sum of the full-load currents of the other motors in the group. This is where the calculations get important.
Example
Let's say you have three fan coil units with RLAs of 1.5A, 2.5A, and 3.0A. Let's assume we are using inverse time circuit breakers. You would start by checking table 430.52 to size the branch circuit protection. For an inverse time circuit breaker, 250% of the motor RLA would be used. For the 3.0 amp motor, 250% times 3.0 is 7.5 amps. Since we can round up to the next standard breaker size, we would use a 10 amp breaker. 10 amps is the value used in the next step. The maximum size of the branch circuit breaker would be calculated as 10 amps (10 amp is the lowest sized breaker of all the motors, as stated above) + 1.5A + 2.5A = 14 Amps. This is under our max of 15 amps, which is compliant.
(3) Conductor Size
The branch-circuit conductors (the wires) must have an ampacity sufficient for the sum of the full-load currents of all the motors, plus 25% of the highest-rated motor in the group, per 430.24. In the example above, the conductor ampacity must be at least: 1.5A + 2.5A + 3.0A + (0.25 3.0A) = 7.75 A. This means you would need at least 14 AWG copper wire (which is rated for 15 Amps in most situations, consult 310.16). The disconnect must be rated for the minimum current that is calculated from 430.24. The branch circuit sizing must also be large enough to account for any nonmotor loads being fed off of the circuit (lights, receptacle outlets, etc).
(4) Overload Relays
The overload relay tripping current per 430.32 for each motor is required. Overload protection that will prevent dangerous overheating of the motor. (Usually found on the motor's data plate).
3.
Local Disconnect Switches
The local disconnect switch at each fan coil unit is required by NEC 440.14 and is used to de-energize equipment for maintenance. This local disconnect needs to be rated for the voltage and current it will be carrying.
Practical Implications and Recommendation
Careful Calculation is Crucial
Before deciding to put multiple fan coil units on a single circuit, you must perform the calculations outlined in 430.53(C) to ensure you are within the code limits. If your calculations are close to the 15A limit, you might want to consider separate circuits anyway.
Nameplate Information
You need to have the
actual RLA (Rated Load Amps) from the fan coil unit nameplates to do the calculations correctly.
Built-in Overload Protection
Confirm the fan coil units have built-in thermal overload protection.
Consider Voltage Drop
Long circuit runs can cause voltage drop, which can affect motor performance. Take this into account when sizing conductors, and especially when determining how many units to place on a circuit.
Future Expansion
Consider if there's a possibility of adding more fan coil units in the future. It might be wise to run separate circuits now to avoid overloads later.
AHJ Approval
Ultimately, the final decision rests with the Authority Having Jurisdiction (AHJ, typically the local electrical inspector). Be prepared to show your calculations and explain how your installation meets the code requirements.
In summary
You can put multiple fan coil units on a single 15A circuit if you meet all the requirements of 430.53(C). However, it requires careful calculations, consideration of motor overload protection, and proper conductor sizing. The individual fused disconnects at each unit are not specifically required for short circuit and ground fault protection if you meet the code in other ways (as described above), however it is still required that you put a local disconnect on each unit.