Question: Hello!I'm having an issue with my inspector and I'm trying to find out if he may be wrong..I have an NM feeder between main panel and sub panel with short piece of EMT conduit to and from a crawl space.In order to have each of these pieces grounded he is telling me that:1. Chase nipple that goes in LB does not ground the conduit.2. Ground busing without lock nut is not rated for grounding.3. Lock nut alone (even without leftover concentric rings) is not rated to ground EMT. He said that lock nut is for mechanical connection but not grounding..?I will include 3 refference photos plus photo of the piece that transitions in NM (NM connector is present)Any advice/refferece would be greatly appreciated!Also wanted to check: in your area when doing main panel grounding by the main water - is jumper over main water regulator required? Is it even a code?Thank you!
Okay, let's break down your inspector's claims and address the water pipe grounding question. Based on the NEC and common interpretations, here's my analysis
EMT Grounding Concerns
Your inspector is being extremely conservative (some might say unnecessarily strict). Let's address each point:1. Chase Nipple in LB Does Not Ground Conduit
This is partially true, but misleading. A simple chase nipple, by itself, does not guarantee a reliable ground path. However, when installed properly and tightly, and combined with other listed grounding components, it can contribute to the overall ground path. The key is whether the entire system provides a reliable, low-impedance ground fault path back to the source.2.
Ground Bushing Without Lock Nut is Not Rated for Grounding
This is incorrect and suggests a misunderstanding of the purpose of a ground bushing. A listed ground bushing is absolutely rated for grounding. The set screw (if equipped) bites into the enclosure to ensure a reliable connection. The grounding conductor then attaches to the lug of the bushing. However, a ground bushing needs to be secured to the enclosure. If there is no locknut on the opposite side, the bushing might not be tightly secured against the enclosure, which could lead to a poor connection and compromise its grounding capabilities.3.
Lock Nut Alone (Even Without Leftover Concentric Rings) is Not Rated to Ground EMT: Mechanical Connection Only
This is the most questionable claim. While a standard locknut's primary function is mechanical securing, the NEC does allow it to be used for grounding if installed properly and tightly on clean surfaces. However, the inspector's concern is valid, as it's not the most reliable method. The NEC prefers listed grounding locknuts or ground bushings for grounding EMT, especially in potentially corrosive environments. The keyword here is "reliable". A standard locknut is not considered reliable for long-term grounding compared to alternatives.
NEC Perspective NEC 250.96(A)
This section addresses bonding raceways and enclosures. It requires them to be bonded to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them.
NEC 250.97
This section addresses bonding metal raceways and enclosures containing service conductors. It mandates bonding jumpers if concentric or eccentric knockouts are present that are not listed for grounding.
NEC 250.92
This section details methods for bonding service equipment, which includes grounding bushings and listed grounding locknuts.
Why the Inspector is Being Strict
The inspector is likely concerned about the long-term reliability of the ground path, especially in a crawl space environment that may be damp or corrosive. A standard locknut can loosen over time due to vibration or corrosion, potentially compromising the ground connection. He may also be extra cautious because it's a feeder circuit, carrying a higher potential fault current.
What You Should Do (Recommendations)
Use Listed Grounding Locknuts or Ground Bushings
This is the easiest and best solution. Replace standard locknuts with listed grounding locknuts that are specifically designed for grounding EMT. For the ground bushing, verify that it is properly seated against the enclosure and held securely on the other side.2.
Consider Bonding Jumpers
If you are using standard locknuts (which I advise against), adding a bonding jumper around the EMT connection points would provide a redundant ground path and address the inspector's concern. This would involve connecting a grounding conductor between the enclosure and the EMT using appropriate connectors.3.
Document Everything
Keep receipts and documentation for all grounding components used. This will help demonstrate to the inspector that you have taken the grounding requirements seriously.4.
Talk to the Inspector (and Possibly a Second Opinion)
Respectfully ask the inspector for specific NEC code references that support his interpretation. If you still disagree, consider getting a second opinion from another qualified electrician or inspector in your area.
Water Pipe Grounding and Jumper Over Regulator Water Pipe Grounding (General)
Grounding to a metallic water pipe is a common and acceptable method if the water pipe is electrically continuous and makes good contact with the earth for at least 10 feet. This is because the water pipe acts as a grounding electrode.
Jumper Over Water Meter/Regulator
This is absolutely a code requirement in many jurisdictions. The purpose is to ensure electrical continuity of the grounding electrode even if the water meter or regulator is removed or replaced with a non-metallic component.
NEC 250.53(D)(1)
This section specifically requires the bonding of interior metal water piping systems to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor (if of sufficient size), or to one or more of the grounding electrodes used. If the water pipe is not continuous, you must install a jumper.
In your area, check with your local electrical codes and/or utility company for specific requirements regarding water pipe grounding and jumpering over water meters/regulators. These requirements can vary.
In Summary:
While your inspector is being very strict on the EMT grounding, his concerns are rooted in ensuring a reliable and safe ground fault path. Using listed grounding locknuts or ground bushings is the best practice.Regarding the water pipe grounding, always* jumper over the water meter/regulator (unless explicitly told otherwise by your local authority). It's a safety requirement to maintain a continuous grounding path. Flag for review