Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Multiple Fire pump- Electrical Load calcuations

User: monitaverma

Asked on: Monday, September 8, 2025 at 3:01 pm EDT
Answered on: Monday, September 8, 2025 at 3:06 pm EDT

Question: Hello,Please see the attached SLD. We are upgrading the power for the entire campus. Each building on the campus has a 30 HP fire pump. FPB#2 is the board that will feed all the fire pumps.The breaker size for each fire pump is based on the fire pump LRC, which is 240A.My question: Since the fire pumps are being connected after the meter, should the service board be sized to include both the FPB load (720A) and the MSBH2 load (933A), for a total of 1,653A? In other words, does the MSBH2 board need to be rated for 2,000A? or are we ok with 1200Amps?

You're asking a crucial question about service sizing, and it's smart to be thorough. Here's a breakdown of the considerations, and why you likely do need to consider the combined load for the service board, and likely do need to upgrade to 2000A.

Key Considerations and Code Implications Simultaneous Operation

The big question is,

Can all fire pumps run simultaneously?
Generally, the answer is YES. Code assumes the worst-case scenario. While statistically, they might rarely all run at once, the code mandates planning for that possibility.
NEC 220.18 - Fire Pumps This section of the National Electrical Code requires a feeder circuit to be able to carry the locked-rotor current of the fire pump. NEC 695 - Fire Pumps This is the dedicated article in the NEC that addresses fire pumps. It has special requirements for reliability and power source independence. While it allows for some load shedding, it's usually not applicable in a standard campus setting like this. Service Entrance Equipment Rating

The service entrance equipment (the MSBH2 in your case) must be rated to carry the calculated load, including the fire pump load.

Why You Likely Need to Account for Combined Load (and Upgrade to 2000A)
1. Code Compliance

NEC 220.18 and NEC 695 generally require you to assume the fire pumps could all operate simultaneously. Therefore, you must include their loads in the service calculation.2.

Safety and Reliability

The primary purpose of the fire pumps is to protect life and property. Undersizing the service board creates a point of failure during an emergency. You want the system to function as designed, even under the most demanding circumstances.3.

Future Expansion

Even if the current loads seem manageable, future building expansions or equipment upgrades could push the system beyond its limits. A properly sized service board provides headroom for growth.4.

Insurance Requirements

Fire protection systems often have strict insurance requirements. An undersized service board could invalidate your coverage.

Analysis of Your Numbers
MSBH2 Load: 933A (Existing Building Loads) FPB Load: 720A (Fire Pump Load, Assuming 3 pumps x 240A each) Total Calculated Load: 1653A

Based on these numbers, a 1200A MSBH2 is NOT sufficient. You would be overloading the board as soon as the pumps started running.A 2000A MSBH2 is likely needed.

Recommendations1. Verify Fire Pump LRC

Double-check the Locked Rotor Current (LRC) for each fire pump motor. Use the motor nameplate data. Don't just rely on a rule of thumb.2.

Professional Engineering Review

Have a licensed electrical engineer perform a complete service load calculation, taking into account all applicable NEC sections and local amendments. This is not a DIY project. The engineer should document the calculation and assumptions.3.

Coordination Study

Perform a coordination study to ensure proper selective coordination between the service board breaker, the FPB breakers, and the individual fire pump breakers. This is critical for reliability.4.

Consider a Separate Service

In some cases, it might be more economical or reliable to install a separate service dedicated solely to the fire pumps. This isolates them from the rest of the building load and simplifies the calculations. NEC 695.3(A) indicates that the fire pump source of power shall be from a reliable source. A dedicated service from the utility is the most reliable.

Important Notes

This is general guidance based on the information provided. You MUST consult with qualified professionals (licensed electrical engineer) to ensure compliance with local codes and regulations.

Always prioritize safety and reliability when dealing with life-safety systems.
Document everything!Let me know if you have more details or questions. Flag for review

Previous Question Next Question