Question: We use a lot of MC Quik Lite with my current job. We make sure to use MCI-A rated connectors. This is the style of MC that has the internal aluminum wire running down the length of the cable; it does not have a separate ground wire.One of my journeymen is unhappy because the rough-in crew used this stuff for a wall heater and there was nothing for the wall heater can to ground to. The only bond was via the cable connector.I also just learned today that some of the electricians are using MC Quik Lite into our sub-panels and landing the aluminum bonding wire into the ground bar. <--- this part makes me cringe.However, I think all of the above is technically to code.Can you help see any blind spots I'm overlooking? Is there a technical reason I need to be using regular MC for devices other than receptacles - and also sub-panels? I mean the latter is something I would open up and think amateurs did it.
Okay, let's break down your MC Quik Lite situation and see if we can uncover any potential code violations or best practices that you might be missing. You're right that on the surface, much of this can appear to technically comply with code, but that doesn't mean it's always the best or safest approach.
Here's a breakdown of the situation and my thoughts
1. MC Quik Lite (MCI-A) Characteristics
MCI-A Construction
This is crucial. MCI-A (Metal-Clad Cable, internal aluminum bonding/grounding conductor) relies on the aluminum bonding wire and the metal jacket for grounding/bonding. It is specifically designed and listed to provide an effective ground-fault current path when installed with listed MCI-A connectors.
No Separate Ground Wire
As you correctly pointed out, the absence of a separate insulated grounding conductor is the defining characteristic.
2. Wall Heater with MCI-A
The Journeyman's Concern
Your journeyman's concern is legitimate. While the connector can technically provide the ground, it's often a less-than-ideal solution for a fixed appliance like a wall heater. Here's why:
Mechanical Connection Reliance
The grounding depends entirely on the integrity and tightness of the connector. Over time, vibration, corrosion, or loosening can degrade this connection, impacting grounding.
"Professionalism" and Perception
It just looks and feels like a less robust installation to many experienced electricians, even if it meets minimum code. This can raise concerns during inspections or future maintenance.
Code Compliance (Potentially)
NEC 250.4(A)(5)
Grounding of electrical equipment must create a low impedance ground fault current path to facilitate the operation of the overcurrent device.
NEC 250.118(10)
Type MC cable is recognized as an equipment grounding conductor.
NEC 250.134(B)
If the outlet box is nonmetallic, use a method described in 250.146 to ground the device. IF the MCI-A cable is properly terminated in a listed connector, and IF the heater is properly bonded to the box, then it could be argued it meets the minimum requirements of the code.
Blind Spots
Connector Rating
This is critical. The connector must be specifically listed for use with MCI-A cable, and the listing must cover the amperage requirements. Standard MC connectors are often not sufficient. (You said you're using MCI-A rated connectors, but double-check this every time!)
Box Bonding
The metal box must be bonded. The way most people achieve this is through direct contact with the connector.
Maintenance
Future maintenance could cause issues if someone doesn't understand the setup.
3. MCI-A into Sub-Panels and Landing the Aluminum Bonding Wire on the Ground Bar
This is the MOST Concerning part and requires a closer look. Why it's Questionable
Intended Use
While MCI-A is allowed to be used as an equipment grounding conductor, using the aluminum bonding wire alone as the sole ground to the ground bar is questionable. The intent of MCI-A is that both the armor and the aluminum bonding wire contribute to the fault current path.
Aluminum to Copper
Direct connection of aluminum to copper, especially under vibration or in a potentially corrosive environment (sub-panel), can lead to corrosion and connection failure over time. While the ground bar should be rated for aluminum terminations, relying solely on this can be risky.
Poor Practice
This just isn't the way experienced electricians typically do this. It looks shortcutted.
Code Compliance (Very Doubtful)
NEC 250.8
Connections must be made using methods identified for the particular material of the conductors involved. Direct aluminum to copper connections without proper terminations can violate this.
NEC 314.40(D)
Proper support of conductors and terminations within the panel. Over-reliance on the aluminum bonding wire as the sole grounding conductor could be argued as improper support.
Blind Spots
Panel Instructions
The panel manufacturer's instructions are a requirement and often dictate how to properly ground/bond within the panel. Many panel manufacturers will specify a separate grounding conductor (Green wire)
AHJ Interpretation
This is almost certainly something that would raise red flags with an inspector.
Recommendations
Re-evaluate the Sub-Panel Grounding
Stop Landing the Aluminum Wire Only! This is the most critical. Use Regular MC Cable with a Green Ground Wire
This is the best practice for sub-panels. Terminate the green insulated grounding wire to the ground bar.
Consider an Additional Grounding Conductor
If you must use MCI-A for some reason (cost, availability, etc.) and you are in an area where corrosion is common, consider pulling an additional green insulated grounding wire in with the MCI-A and connecting it to the ground bar. This provides a redundant and more reliable grounding path.2.
Wall Heaters
Consider Using Regular MC Cable
For fixed appliances like wall heaters, the peace of mind and professional appearance of using regular MC cable with a dedicated ground wire is often worth the small extra cost.
Ensure Robust Connector Installation
If you must use MCI-A, ensure the MCI-A connector is rated for the application, is properly tightened, and provides a solid mechanical connection to the box.
Verify Box Grounding
Make sure the wall heater can be directly bonded to the metal box.3.
Education
Train Your Electricians
Ensure your electricians fully understand the nuances of MCI-A cable, its limitations, and proper termination techniques.
Review Code Sections
Regularly review relevant NEC sections related to grounding and bonding, especially those pertaining to MC cable.
AHJ Consultation
If you're unsure about any specific application, consult with your local Authority Having Jurisdiction (AHJ) for clarification and guidance.4.
Material Standardization
Consider Restricting MCI-A to Specific Applications
Instead of allowing MCI-A for everything, limit its use to specific situations where it's truly the best solution (e.g., long runs where weight is a factor).
In Summary:
While technically some of what you're doing might meet minimum code requirements, it's often skirting the edge and relying on potentially weak links in the grounding path. Using regular MC cable with a dedicated ground wire, especially for sub-panels and fixed appliances, is generally a much safer, more reliable, and more professional approach. The cost difference is usually minimal compared to the potential risks of a compromised grounding system. The way you're landing the aluminum conductor in the sub-panel is highly* suspect. Flag for review