Question: We have been working a multi family complex for a couple weeks and noticed a few things I need help.There is an 4 unit complex meaning they all share walls/floors. 2 on top 2 on bottom. The meter can bank sits on one side of the units. The units didnt original have washer/dryer circuits so they ran all the dry circuits through ceiling in one unit to the other side so they can add circuits to patio area on back side. Can all the circuits be installed through same unit?
Okay, I understand. You're working on a 4-unit multi-family building where new washer/dryer circuits were added. Instead of running circuits directly to each unit, they ran all the circuits through the ceiling of one unit to reach the other side of the building for the back patios. Here's a breakdown of the issues and considerations
Issues and Concerns:
Code Violation (Likely)
This configuration highly likely violates several sections of the National Electrical Code (NEC). The NEC emphasizes that each dwelling unit must be served by its own electrical system, with limited exceptions for common areas or services.
Overloading/Voltage Drop
Running all those circuits through one unit's ceiling could lead to overloading that unit's wiring, junction boxes, or conduit (if used). It also creates potential voltage drop issues, especially if the distances are significant.
Access and Maintenance
If a problem arises with one of those "pass-through" circuits, accessing it for repair or troubleshooting could be difficult and require entry into the neighbor's unit. This creates inconvenience and potential liability issues.
Future Modifications
This setup makes future modifications to any of the units' electrical systems much more complicated. For example, if one unit upgrades its electrical service, it could impact the other units using the "pass-through" circuits.
Liability
If there were a fire or electrical problem caused by this unusual configuration, the building owner and/or the electrician who performed the work could face significant liability.
NEC Considerations (General Examples - Consult the Actual Code)
Article 225 (Outside Branch Circuits and Feeders)
This article covers the installation of outside branch circuits and feeders and will likely have rules that were violated if the circuits are not properly sized or installed.
Article 310 (Conductors for General Wiring)
This article covers ampacity, insulation, and other conductor requirements. Overcrowding of conductors in raceways or junction boxes can lead to overheating and is a common code violation.
Article 314 (Outlet Boxes, Conduit Bodies, and Handhole Enclosures)
This article specifies requirements for boxes and enclosures. Overfilling boxes with too many conductors is a common violation.
Article 400 (Flexible Cords and Cables)
If flexible cords were used for any part of this installation, they must be used properly and protected.
Article 408 (Switchboards, Switchgear, and Panelboards)
Panelboards must be properly sized and have enough capacity to handle the added load.
Why It's Probably Not Allowed
The core principle is that each dwelling unit should have its own independent electrical system. Running circuits through another unit blurs this boundary and creates dependencies that the NEC generally tries to avoid.
What Should Be Done
Contact a Qualified Electrical Contractor
The best course of action is to consult with a licensed and experienced electrical contractor familiar with multi-family dwelling electrical systems and local codes.2.
Inspection
Get a thorough inspection of the existing electrical system to identify all code violations and potential hazards.3.
Develop a Remediation Plan
The electrical contractor can develop a plan to correct the issues. This will likely involve: Running dedicated circuits for each unit directly from the meter bank to the appropriate unit. Ensuring proper sizing of conductors, conduit, and overcurrent protection devices. Verifying that all wiring and connections are done according to code.
Important Considerations
Local Codes
Always check and comply with local electrical codes and ordinances, as they may have more stringent requirements than the NEC.
Permits
Obtain the necessary electrical permits before starting any electrical work.
Property Owner
Keep the property owner informed of the situation and the proposed remediation plan.
In summary, running all the circuits through one unit is almost certainly a code violation and creates numerous potential problems. It's crucial to have a qualified electrician inspect the system and develop a plan to correct the issues to ensure safety and code compliance. Flag for review