Question: Hi. Rewiring a two bulb 8’ fluorescent fixture fixture to use two 8’ led bulbs.Is the ballast wire rated that one wire can feed one side of both bulbs (hot) and one wire feed the other side of both bulbs (neutral)? Thank you.
Yes, generally, the existing wiring should be sufficient to handle the amperage load of two 8' LED bulbs, assuming you're using ballast-bypass (direct wire) LED tubes.
Here's a breakdown and important considerations: Ballast-Bypass (Direct Wire) is Key
You must remove and bypass the ballast completely. This is the most common and generally recommended way to convert to LED in these fixtures. This means the LED tubes will connect directly to the 120V (or 277V, if applicable) power source.
Amperage Calculation
LED bulbs draw significantly less power than fluorescent tubes. Even though it's a long fixture, the actual current draw will be low. For example, if each 8' LED bulb draws 30W, at 120V, that's only 0.25 amps per bulb (30W/120V = 0.25A). Two bulbs would be 0.5 amps.
Wire Gauge
The wiring in your fixture is almost certainly 18 AWG or 16 AWG. These gauges are rated for far more than 0.5 amps. 18 AWG is typically rated for 10 amps, and 16 AWG is rated for more than that.
Wire Insulation
The existing wire insulation is likely rated for 600V and 90°C or higher, which is more than adequate.
How to Wire (Ballast Bypass)
Disconnect Power
Turn off the breaker to the fixture.
Safety first!2. Remove the Ballast
Disconnect all wires connected to the ballast. Remove the ballast from the fixture.3.
Rewire the Sockets
Determine which sockets (tombstones) are wired together.
Consult the wiring diagram that came with your LED bulbs! The typical configuration is: Connect one wire (the Hot/Line wire) to one end (one pin) of both tombstones. Connect the other wire (the Neutral wire) to the other end (the other pin) of both tombstones. Important
This ensures each bulb receives power directly from the line and neutral.
Important Considerations and Warnings
Wiring Diagram is Critical
Always follow the wiring diagram provided with your specific LED bulbs. Different LED tube designs require different wiring configurations.
Double-Check Wiring
Before turning the power back on, double-check all connections to ensure they are secure and correct. Loose connections can cause arcing and fire hazards.
Non-Shunted vs. Shunted Sockets (Tombstones)
Some LED tubes require non-shunted tombstones (the two contacts inside the tombstone are isolated). If you have shunted tombstones (the two contacts are connected together), you'll need to replace them with non-shunted ones. Shunted tombstones are common in fluorescent fixtures. The wiring diagram with the LED bulbs should specify this. You can test this with a multimeter - if there is continuity between the two contacts on the tombstone, it is shunted.
Single-Ended vs. Double-Ended Wiring
Pay very close attention to whether your LED tubes are single-ended (power connected to only one end of the tube) or double-ended (power connected to both ends of the tube). This will drastically affect how you wire the tombstones.
Local Codes
Check your local electrical codes. Some jurisdictions may require a licensed electrician to perform this type of work.
Voltage Compatibility
Make sure the LED tubes are compatible with your supply voltage (usually 120V in residential settings in North America).
If you are unsure or uncomfortable with any of this, hire a qualified electrician. Working with electricity can be dangerous.
In summary: The existing wire gauge and insulation should be fine for the lower current draw of LED bulbs when doing a ballast bypass. However, the correct wiring method depends entirely on the type of LED bulbs you're using (single-ended vs. double-ended) and whether you need to replace the tombstones. Always follow the bulb manufacturer's instructions. Flag for review