Question: I'm in Florida. I'm reading 69.15 in 2020 NEC. Normally our disconnect goes beside the meter and directly into the combiner box. 10 foot rule compliance. On a multiplex with a meter bank, the house is approximately 65 feet away from the meter bank. I don't think that the disconnect should go there. it should be attached to the residence where the solar is, right? If that's the case, how do I stay in compliance? It looks like in 690.15 (C) that I can put the disconnect on the house as long as it is lockable? IS that correct?I've looked in other threads for a similar situation, but couldn't find one. Anybody want to chime in?
Okay, let's break down this scenario and how the 2020 NEC addresses it, particularly focusing on 690.15 and the "10-foot rule" considerations.
Understanding the Core Issues Distance
You have a significant distance (65 feet) between the meter bank and the point where the solar array and load are located (the house). This exceeds the typical "10-foot rule" for rapid shutdown and disconnect placement.
Safety and Access
The primary goal of disconnect requirements in Article 690 is to provide a readily accessible means for firefighters and other emergency responders to de-energize the PV system. Putting the disconnect at the meter bank when the house is 65 feet away compromises this principle.
690.15 - Disconnecting All Conductors
This section of the NEC outlines the requirements for disconnecting means for PV systems. The general principle is that you must be able to disconnect the PV system from all sources of power, including the utility grid and the PV array itself.
Analysis of 690.15 and the "10-Foot Rule"
The "10-foot rule" is not explicitly stated in the 2020 NEC. It is the AHJ interpretation for rapid shutdown.
Applying 690.15 (C) - Disconnecting Means for Inverters 690.15(C)(1) - Readily Accessible
This section requires the disconnecting means to be readily accessible. Given the 65-foot distance from the meter bank to the house, placing the disconnect at the meter bank likely does not meet the "readily accessible" requirement from the perspective of someone at the house needing to de-energize the PV system (for maintenance, emergencies, etc.).
690.15(C)(2) - Lockable Disconnecting Means
This is the key part that addresses your situation. The section states that the disconnecting means is to be lockable. The intent is to allow the disconnect to be locked in the open position.
How to Achieve Compliance
Based on the information you've provided, here's a recommended approach:1. Locate the Disconnect at the House
Install the PV disconnect (and any other required disconnecting means for the inverter) at the house, close to the inverter, and where it is readily accessible to homeowners and emergency personnel at the house.2.
Use a Lockable Disconnect
The disconnect(s) you use must be lockable in the open (OFF) position. Use a disconnect switch or breaker that has provisions for a padlock or other locking device.3.
Clear Labeling
Ensure the disconnect(s) are clearly labeled "PV System Disconnect" (or similar) so that they are easily identified.4.
Coordinate with the Utility
Talk to your utility company. They might have specific requirements for disconnect placement or signage.5.
Inspection Authority (AHJ) Approval
This is the most important step. Discuss your proposed plan with the local electrical inspector before you start the installation. Explain the situation with the distance and how you are meeting the intent of 690.15(C) by using a lockable disconnect at the house. Get their approval in advance. This will prevent issues during inspection.
In Summary
Yes, it is likely that you can place the disconnect at the house and stay in compliance with the NEC, provided you use a lockable disconnect, properly label it, and get approval from your local AHJ. The key is to address the safety and accessibility concerns that the code is designed to mitigate.
Important Considerations
Rapid Shutdown
Remember to address the rapid shutdown requirements of 690.12. The 65-foot distance from the meter bank will likely necessitate the use of a rapid shutdown system that de-energizes the PV conductors outside of the array boundary. This is usually accomplished with optimizers or microinverters that have built-in rapid shutdown functionality.
Conductor Sizing and Overcurrent Protection
Ensure that the conductors running from the meter bank to the house are properly sized for the PV system output and are protected by appropriate overcurrent devices at both ends (meter bank and the house).
Grounding
Make sure the entire PV system is properly grounded according to Article 690.
Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. Consult with a licensed electrical contractor and your local AHJ to ensure your PV system installation complies with all applicable codes and regulations. Flag for review