User: Will Wire, Location: California: NEC 2020
Asked on: Tuesday, September 9, 2025 at 3:57 pm EDT
Answered on: Tuesday, September 9, 2025 at 3:58 pm EDT
Question: Referencing NEC 110.14(C)(1)(3). Is it code compliant to use 6-3 SER w/Ground Aluminum for a 50 amp sub-panel, with the breaker rated at 75 C and the sub-panel rated at 75 C due to the wire being rated at 50 amps in the 75 C column of Table 310.16? Thank you
Okay, let's break down NEC 110.14(C)(1) and (C)(1)(3) in relation to your specific scenario of 6-3 SER aluminum feeding a 50A sub-panel.
Understanding NEC 110.14(C)(1) and (C)(1)(3) (2023 NEC) 110.14(C)(1): Termination Provisions. States that the temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both. 110.14(C)(1)(3): Equipment Provisions. Equipment terminals for circuits rated 100 amperes or less, or marked for sizes AWG 14 through 1 AWG, shall be permitted to be used with conductors rated for 75°C (167°F).
Your Scenario: 6-3 SER Aluminum to 50A Sub-Panel
You want to use 6-3 SER aluminum cable (with ground) to feed a 50A sub-panel. Your breaker is rated for 75°C, and the sub-panel is rated for 75°C. You're relying on the 75°C ampacity column of Table 310.16, where #6 AWG Aluminum is listed at 50A.
Analysis and Code Compliance
Here's the breakdown of whether this is code-compliant:1. Ampacity of #6 AWG Aluminum
Yes, in Table 310.16, #6 AWG aluminum wire has an ampacity of 50 amps when rated at 75°C.
2.
Termination Temperature Ratings (Crucial Point)
Breaker
You state the breaker is rated for 75°C. This is good.
Sub-Panel Terminals
You state the sub-panel is rated for 75°C. This is also good.3.
SER Cable Considerations
SER cable is subject to derating, but that comes later in the calculation.4.
NEC 334.80 Ampacity for NM, NMC, and SE Cables
SE cable ampacity is governed by this section. NM, NMC, and SE cables are to use the 60C conductor ratings found in 310.16.
5.
NEC 334.80 Exception
SE cables are allowed to use the 75C conductor ratings found in 310.16 if the following two conditions are met: The SE cable terminates in equipment listed and marked for use with 75°C conductors. The ampacity of the SE cable does not exceed that of a 75°C-rated conductor.
Conclusion Initial Impression
Based on the information provided, and assuming that the SER is installed in free air, and the conditions of NEC 334.80 Exception are met, using #6 AWG Aluminum SER with a 50A breaker and 75°C rated terminations
appears to be code-compliant without any derating.
Important Considerations and Caveats Actual Installation Conditions
Table 310.16 ampacities are based on specific conditions (e.g., not more than three current-carrying conductors in a raceway or cable or earth, ambient temperature of 30°C). You must apply derating factors from NEC 310.15 if your installation deviates from these conditions (e.g., higher ambient temperature, more than three current-carrying conductors bundled together). This is where things can get tricky. If you have to derate the wire due to ambient temperature or bundling, it may no longer be sufficient for the 50A load.
Voltage Drop
Always consider voltage drop! While the cable may be ampacity-rated for 50A, a long run can cause excessive voltage drop, which affects the performance of equipment connected to the sub-panel. Use voltage drop calculators to verify adequate voltage at the sub-panel.
Local Amendments
Be aware of any local amendments to the NEC in your jurisdiction. Some areas may have stricter requirements.
Recommendation1. Double-Check Termination Ratings
Confirm the actual temperature ratings marked on the breaker and sub-panel terminals. Look for markings like "75°C" or "60/75°C."2.
Assess Installation Conditions
Carefully evaluate the actual installation conditions (ambient temperature, bundling, etc.) to determine if any derating is required.3.
Calculate Voltage Drop
Calculate the voltage drop for the planned cable run.4.
Consult a Qualified Electrician: If you are not completely confident in your understanding of the NEC and electrical calculations, consult a licensed electrician to ensure the installation is safe and code-compliant. They can perform a thorough assessment and make the best recommendations for your specific situation. Flag for review