User: QA/QC guy, Location: Mesa, AZ and Cheyenne, WY
Asked on: Wednesday, September 10, 2025 at 3:21 pm EDT
Answered on: Wednesday, September 10, 2025 at 3:23 pm EDT
Question: I have 2 local disconnects from different busways (277/480VAC @100A).They feed S1 and S2 of an MTS.The raceway between them is NON-metallic liquid tight.One of the boxes has reducing washers due to an oversized hole (not concentric or eccentric knock-outs) to fit the raceway.I do not believe a bond bushing is necessary because these are feeder circuits not service conductors.Another electrician thinks it is due to NEC 250.97 and 250.92B (2020 NEC).We've searched the code and have found: "if you torture the code book enough - it will confess to anything".I would like to hear opinions from electricians or inspectors.
Okay, let's break down this scenario and address the bonding bushing requirement. Your reasoning is sound, but let's make sure we've covered all the angles.
Here's a summary of the situation
Two 277/480V, 100A Disconnects
Feeding an MTS (Manual Transfer Switch).
Non-Metallic Liquidtight Raceway
Connects the two disconnect enclosures.
Reducing Washers
Used on one box due to an oversized hole.
Disagreement
Whether a bonding bushing is needed.
Your Assessment (and Why It's Largely Correct)
You're primarily correct. Bonding bushings are typically associated with service equipment and connections to metallic raceways containing service conductors to ensure a low-impedance fault current path back to the source. Since these are feeder circuits, the direct application of NEC 250.92(B) is questionable.
The Other Electrician's Reasoning (NEC 250.97 & 250.92(B) - 2020 NEC)
The other electrician is likely focusing on the potential for voltage on the enclosure due to a ground fault and the need to maintain a low-impedance path. Let's examine those articles:
NEC 250.97 (Bonding for Over 250 Volts)
This section states that for systems over 250V to ground, where a raceway (or cable armor) is used as the equipment grounding conductor, the electrical continuity of the raceway must be ensured by one or more of the methods specified in 250.92(B).
NEC 250.92(B) (Methods of Bonding at the Service)
This section lists methods to ensure the required electrical conductivity of metal parts that are required to be bonded. These are commonly bonding jumpers, and bonding bushings
Why a Bonding Bushing Is Probably NOT Required, But Consider These Points
Non-Metallic Raceway
The critical factor here is the non-metallic liquidtight. Since the raceway is non-metallic, it cannot be used as the equipment grounding conductor (EGC). Therefore, 250.97 doesn't directly apply because you're not relying on a metallic raceway for grounding.
2.
Equipment Grounding Conductor (EGC) within the Raceway
The equipment grounding conductor (EGC) is the key. Is there a properly sized EGC (typically a green wire) installed within the non-metallic liquidtight conduit and properly connected to the grounding terminals in both disconnect enclosures?
If yes, then you have the required low-impedance ground fault path, and a bonding bushing is most likely NOT required. The EGC is doing the job of providing a path back to the source for fault current.3. Reducing Washers and Grounding
The reducing washers themselves do not inherently create a grounding issue. The problem they could present is if the raceway were metallic and relied on mechanical connections for grounding. Since you have a non-metallic raceway, the washers are only a mechanical issue (and they address the hole size, which is good).4.
AHJ Discretion
Ultimately, the Authority Having Jurisdiction (AHJ - the inspector) has the final say. They may have a local interpretation or a specific concern.
When a Bonding Bushing MIGHT Be Considered (Unlikely, But Possible)
If the Inspector Believes the Enclosure Needs Additional Bonding
Even with the EGC, an inspector might argue for additional bonding to the enclosure itself if they are concerned about induced voltage or other factors. This is less common with feeder circuits, but it's possible. In that case, you could supplement the EGC with a bonding jumper connected to the enclosure if requested by the inspector, but that is rare.
Recommended Action
Verify the EGC
Double-check that a properly sized equipment grounding conductor (EGC) is installed inside the non-metallic liquidtight conduit and is securely connected to the grounding terminals in both disconnect enclosures. This is the most important factor.2.
Consult with the AHJ
Before proceeding, discuss the situation with the inspector. Explain your reasoning and the presence of the EGC. This is the best way to avoid rework and ensure compliance.3.
Document
Keep thorough documentation of the installation, including wire sizes, conduit type, and grounding connections.
In Summary:
You are likely correct in your assessment that a bonding bushing is not required in this situation, provided a properly sized EGC is installed within the non-metallic raceway.* The non-metallic conduit negates the need to bond the raceway itself. However, always consult with the AHJ to ensure compliance with local interpretations and requirements. Be prepared to explain your reasoning and demonstrate the presence of the EGC. Flag for review