User: binwork91, Location: new york
Asked on: Wednesday, September 10, 2025 at 5:13 pm EDT
Answered on: Wednesday, September 10, 2025 at 5:21 pm EDT
Question: I saw an existing building has a tap on conductor of secondary side of transformer. see picture.I know it is code violation per NEC (2008)240.21(C) Transformer Secondary Conductors. A set of conductorsfeeding a single load, or each set of conductorsfeeding separate loads, shall be permitted to be connectedto a transformer secondary, without overcurrent protectionat the secondary, as specified in 240.21(C)(1) through(C)(6). The provisions of 240.4(B) shall not be permittedfor transformer secondary conductors.My question is: since it is old building, I wonder if there any older code allow to do as picture show?
You are correct that the configuration in the picture, with a tap on the secondary side of the transformer without overcurrent protection at the tap, is a violation of the NEC, including NEC 2008 and newer editions.Let's investigate if older codes could have permitted this. It's highly unlikely, but worth considering the context. Older codes generally placed a strong emphasis on overcurrent protection.Here's a breakdown of why it's unlikely to be grandfathered in under older codes: Fundamental Principle of Overcurrent Protection
The basic principle of protecting conductors from overcurrent due to faults or overloads has been a cornerstone of electrical codes for a very long time. This is designed to prevent fires and equipment damage.
Tap Rules
Even older codes that had tap rules (allowing conductors to be tapped from a source without overcurrent protection at the tap point) had very specific limitations:
Length Restrictions
Taps were typically limited to a very short distance. Common distances were 10 feet or 25 feet, depending on the application and the specific code edition. Your picture appears to exceed these distances.
Ampacity Requirements
The tap conductor had to have an ampacity that was at least a certain percentage of the overcurrent protection device ahead of the tap. Usually this was a substantial percentage, like 1/3 or 1/2.
Overcurrent Protection at the End of the Tap
Critically, the tap rule always required overcurrent protection at the end of the tap. This is absent in your picture.
Single Load
Tap rules were almost exclusively for feeding a single load. Your situation looks like multiple loads are being fed.
Why it's very likely a code violation, regardless of the age of the building
Safety Hazard
This configuration is inherently dangerous. A fault on any of the tapped conductors would not be cleared by the transformer's primary overcurrent protection until it reaches a level that could seriously damage the transformer or the conductors themselves. It creates a significant fire hazard.2.
Lack of Discrimination
Even if the transformer's primary protection were sized small enough to protect the smallest conductor, it would create nuisance tripping problems. You would be taking out the entire transformer for a fault on a very small load.3.
Likely a Field Modification
It is more likely that someone added this wiring later, ignoring the code.
What to do
Consult a Qualified Electrician
The best course of action is to have a qualified electrician inspect the installation. They can determine the exact code violations and recommend appropriate corrective measures.2.
Correction Required
This configuration needs to be corrected. The electrician will likely recommend installing appropriately sized overcurrent protection devices (circuit breakers or fuses) at each tap point to protect the conductors.
In summary:
While it's possible older codes might have had more lenient rules in certain situations, the configuration in your picture is highly unlikely to have ever been compliant, even in older codes. It violates fundamental principles of overcurrent protection. Corrective action is necessary for safety. Flag for review