Question: Hello forum,I have main panelboard with a 100A bus and 100A MCB. It will be feeding a subpanel 225A bus with 200A MCB. Feeder wires will sized per 240.4(B). Planning to use #1 AWG. Connected loads on the panel will be less than 100A. Will this be compliant installation?Thanks.
Let's break down your proposed installation and see if it meets code requirements. Here's a summary and a detailed explanation
Summary: Most likely NOT compliant and a very poor design.
Why it's likely not compliant and a poor design
Overcurrent Protection Mismatch
You can't feed a 225A busbar with a 200A breaker when the upstream protection is only 100A. The subpanel needs to be rated to handle the fault current available at the source.
Subpanel Protection
The 200A MCB in the subpanel doesn't protect the #1 AWG feeder conductors that are only rated for 130A (NEC Table 310.16 - 75°C column, assuming typical installation).
Poor Design
The primary purpose of a subpanel is to distribute power to circuits and provide local overcurrent protection. In your scenario, you're essentially bottlenecking the subpanel at 100A. While the loads might be less than 100A currently, it limits future expansion significantly.
Detailed Explanation and NEC Considerations
NEC 240.4(B) - Overcurrent Protection of Conductors
You're intending to use the "next size up" rule. However, this rule only applies if the standard ampere rating of a fuse or breaker doesn't align with the conductor's ampacity. #1 AWG copper, assuming you're using the 75°C column in Table 310.16 (most common for termination temperature ratings), is rated for 130A. You can't automatically jump to a 200A breaker because your load is under 100A. The conductor must be protected at its ampacity or the next lower standard size. You also can't size the conductors based on calculated load, and increase the OCPD size to match the subpanel rating. That is not permitted.2.
NEC 240.21(C) - Feeder Taps
This section allows you to tap feeders under specific conditions. However, tapping rules don't apply here because you're not tapping a main feeder. You're feeding a subpanel directly from the main panel.3.
NEC 408.36 - Overcurrent Protection of Panelboards
"Panelboards shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard." Your 225A panelboard needs to be protected at or below its rating. The upstream 100A breaker provides that protection, but at the cost of severely limiting the panelboard's utility.4.
NEC 408.16 - Clearance for conductors "Panelboards shall be so arranged that the conductors entering the cabinet pass directly to the terminals to which they are connected without deflection between the cabinet walls and the terminals.5. Feeder Size and Subpanel Rating
The entire point of having a 225A busbar is to allow for future expansion and higher load capacity. By feeding it with a 100A breaker, you're negating the benefit of the larger panel.
Corrected Design Recommendations
To make this a compliant and useful installation, here's what you need to consider:1.
Determine Actual Load
Calculate the actual anticipated load, including future expansion. A load calculation is essential (NEC Article 220).2.
Properly Size Feeder Conductors
Size the feeder conductors (from the main panel to the subpanel) to handle the calculated load and future expansion, ensuring you are using correct temperature ratings. Use NEC Table 310.16 to determine the ampacity.
3.
Select Subpanel Breaker
Choose a breaker for the subpanel that: Is rated to protect the feeder conductors at or below their ampacity, following NEC 240.4(B). Is rated at or below the panel's ampacity (225A in your case).4.
Consider Increasing Main Panel Capacity
If you need to feed a significantly higher load to the subpanel and the main panel's 100A breaker is insufficient, you may need to upgrade the main panel itself to a higher amperage. This could involve service entrance upgrades as well.
Example Scenario
Let's say your load calculation comes out to 150A, considering future growth. You could use #1/0 AWG copper conductors, rated for 150A at 75°C. You would then use a 150A breaker at the subpanel to protect those conductors. This 150A breaker would also protect the 225A busbar of the subpanel, per NEC 408.36. The 100A breaker at the main panel would need to be replaced with a breaker capable of handling 150A, or even higher if considering future expansion of the main panel.
Important Notes
Local Codes
Always check with your local electrical inspector. Local codes can have stricter requirements than the NEC.
Qualified Electrician
Electrical work can be dangerous. Always hire a qualified and licensed electrician to perform any electrical work.
Documentation: Keep accurate records of your load calculations and wire sizes for future reference and inspection.In conclusion, your proposed installation is unlikely to be compliant. Re-evaluate your load requirements, properly size the conductors, and ensure that the overcurrent protection is appropriate for both the conductors and the panelboard. Flag for review