Topic: What’s the deal with bundling?

User: Pinnie, Location: Ohio

Asked on: Wednesday, September 10, 2025 at 6:18 pm EDT
Answered on: Wednesday, September 10, 2025 at 6:19 pm EDT

Question: I’ve been told you can’t have more than 3 mcs under the same zip tie. I also know there’s a bundled definition but that only applies to art 520. There’s also a code rule that says something like if more than two mcs pass through the same hole with insulation or fire caulk you have to start derating.

You're touching on a few key areas related to cable management and potential derating in electrical installations. Let's break down each point and clarify the relevant code references

1. The "3 MCs Under a Zip Tie" Rule:
There isn't a direct, explicitly stated rule that limits you to only 3 MC cables under a single zip tie in the NEC. This is likely a misunderstanding or a company-specific policy based on best practices. Why the misinterpretation? The concern stems from: Bundle Overheating

When cables are tightly bundled, especially with insulation, the heat generated by the current flowing through them can't dissipate effectively. This can lead to overheating, insulation degradation, and potential failure.


Cable Damage

Over-tightening zip ties can damage the outer jacket of MC cable, reducing its ability to protect the conductors inside.

Accessibility

Tightly packed cables can make it difficult to trace, maintain, or modify circuits later on.


Best Practice

The spirit of the "3 MC" rule is good practice. Keeping bundles reasonably sized and not overly tight helps with heat dissipation and prevents damage. Focus on neat and secure cable management. The number that works is the number that allows you to be neat and secure without putting undue pressure on the cables or making the group of cables so bulky that it can’t be supported properly.

2. "Bundled" Definition (Art. 520)

You're correct that the definition of "bundled" is used specifically in Article 520 (Theaters, Audience Areas, and Similar Locations) of the NEC.

3. Multiple Cables Through the Same Hole and Derating



NEC 310.15(B)(3)(a) Adjustment Factors (Bundled Cables)
This is the crucial section you're thinking of. While it doesn't specifically require fire caulk, it states that when conductors are installed in conduits, cable trays, or direct buried, they are considered bundled when installed without maintaining spacing for more than 24 inches (600 mm). Application

If you have more than three current-carrying conductors (CCCs) bundled together through a single hole (especially if it's also sealed with insulation or fire caulk), you
must apply derating factors to the ampacity of the conductors. The ampacity table in 310.16 shows the allowable ampacity of a cable at different ambient temperatures. Once you have more than 3 current carrying conductors you have to use Table 310.15(B)(3)(a) to de-rate the allowable ampacity. So if you have 4-6 current carrying conductors, you're allowed to use 80% of the ampacity.

"Current-Carrying Conductor"

Important! The derating only applies to current-carrying conductors (usually the hot and neutral wires). Ground wires (equipment grounding conductors) generally don't count towards the number of current-carrying conductors for derating purposes.

Summary and Key Considerations



No Hard "3 MC" Rule in the NEC

But good cable management practices are essential for safety and reliability.


Derating for Bundled Conductors

NEC 310.15(B)(3)(a) is the primary rule requiring derating when multiple conductors are bundled tightly, especially in enclosed spaces (like passing through a sealed hole).

Consider Heat Dissipation

Pay attention to how heat can dissipate from the cables. Avoid overly tight bundles and use cable management techniques that allow for airflow.


Use Appropriate Zip Ties

Use zip ties designed for cable management. They should be UV-resistant (for outdoor use) and have rounded edges to prevent damage to the cable jacket.*

Follow Manufacturer Instructions

Always follow the manufacturer's instructions for installing and supporting MC cable and any associated fittings or accessories.

Example

Let's say you have four MC cables, each with three current-carrying conductors (hot, neutral, and ground). You're running them through a single hole in a wall and sealing it with fire caulk.1.

Determine the number of CCCs

4 cables x 2 CCCs (hot and neutral, ignoring the ground) = 8 CCCs.2.

Refer to Table 310.15(B)(3)(a)

For 7-9 current-carrying conductors in a bundle, you need to derate to 70% of the ampacity listed in Table 310.16.
3.


Calculate the Adjusted Ampacity

Look up the ampacity of the conductor size you're using in Table 310.16 (based on its insulation type and temperature rating). Multiply that ampacity by 0.7 (70%). The result is the maximum current you can safely run through each conductor in that bundle.

Important Disclaimer:
Electrical codes are complex and subject to interpretation by local authorities. Always consult with a qualified electrician or electrical inspector for specific guidance on your project. This information is for educational purposes and should not be considered a substitute for professional advice. Flag for review