Topic: EM disconnect & 250.64

User: WD40, Location: Philly

Asked on: Thursday, September 11, 2025 at 11:42 am EDT
Answered on: Thursday, September 11, 2025 at 11:50 am EDT

Question: Looking at my new 2023 codebook;Is a one family dwelling with a EM disconnect and a Service disconnect a "building with multiple disconnecting means in separate enclosures"?Seems like if a dwelling has just a single service disconnect that also satisfies a EM disconnect 250.64 would not apply.If a dwelling has a EM disconnect and a service disconnect its now a building with multiple disconnecting means?Thanks

Yes, your understanding is correct. Let's break it down: Single Service Disconnect that also serves as the EM Disconnect

If you have a single service disconnect that
also meets the requirements of an emergency disconnect (and is properly labeled as such), then 250.64 would not necessarily apply because there is effectively only one disconnecting means, even though it serves a dual purpose.

Separate EM Disconnect AND Service Disconnect

If you have a separate emergency disconnect in addition to the service disconnect, then yes, you now have a "building with multiple disconnecting means in separate enclosures" as far as the NEC is concerned.

Therefore, if you have both a service disconnect and an EM disconnect, the requirements of 250.64 would then apply, particularly 250.64(D) regarding grounding electrode conductor connections.
In summary

One Disconnect (Service & EM combined): likely not "multiple disconnecting means." Two Disconnects (Separate Service and EM): is "multiple disconnecting means."

Important Considerations Regarding 250.64(D)



250.64(D)(1)
would require all grounding electrode conductors to be connected at the service disconnect location. 250.64(D)(2) If the 250.64(D)(1) requirements are not met, the individual grounding electrode conductor shall be extended to the other disconnecting means location and there shall be no interruption of the grounding electrode conductor.

Recommendation:

Always consult with the local AHJ (Authority Having Jurisdiction) to confirm interpretations and ensure compliance with local amendments to the NEC. They have the final say in how the code is applied in your specific area. Flag for review