User: leboot, Location: Baltimore, MD United States
Asked on: Friday, September 12, 2025 at 1:55 pm EDT
Answered on: Friday, September 12, 2025 at 1:55 pm EDT
Question: I'm working on a metering plan (LEED) for a project that will have multiple switchboards as well as a tenant wireway for tenant spaces. The tenant spaces will be powered from enclosed circuit breakers or fused switches tapped from the wireway and metered separately for LEED and revenue (utility metering is upstream). I'm having trouble visualizing what the voltage reference connection for the meter will look like. The meter can accept #22-14, but the feeder for the tenant space will be 200+ Amps.I've typically had either circuit breakers with the electronic metering trip units or a panel that we could provide a 3P-15A breaker in for this purpose.I'm attaching one diagram I saw from Eaton.Any guidance would be appreciated!
Okay, this is a common issue and I can help you brainstorm some solutions for getting a proper voltage reference for your tenant space meters, especially when tapping off a large wireway. Let's break down the challenges and then discuss potential approaches.
Challenges
Large Conductors vs. Small Meter Terminals
You're dealing with very large feeder conductors (200+ Amps) for the tenant spaces, but your meters only accept small gauge wires (#22-14) for the voltage reference. Directly tapping a #14 wire off a 200+ Amp conductor is unsafe and impractical.
No Dedicated Panelboard
You don't have a traditional panelboard downstream of the wireway to easily provide a small voltage reference breaker (like a 15A).
Safety
Any solution needs to be safe, code-compliant, and minimize the risk of accidental short circuits or overloads in the voltage reference circuit.
LEED Compliance
The metering needs to be accurate and reliable to meet LEED requirements.
Revenue Grade
Since you need revenue-grade metering, the solution must be accurate and meet the utility requirements for voltage monitoring.
Potential Solutions and Considerations
Here's a breakdown of several approaches, with pros and cons:1.
Control Power Transformer (CPT)
This is generally the best and safest method, especially with revenue-grade metering involved.
How it Works
Install a small control power transformer (e.g., 480V:120V, or whatever your wireway voltage is to a safe voltage for your meter) for each tenant space. The transformer primaries are connected to the wireway conductors using appropriate fusing. The secondary side provides a dedicated, isolated, and properly sized voltage reference for the meter.
Pros
Isolation
Completely isolates the metering circuit from the high-current feeder. This improves safety and reduces the risk of transients affecting the meter.
Proper Voltage
Steps down the voltage to a safe and manageable level (e.g., 120V), making the metering system easier to work with.
Precise voltage: A CPT is far more accurate than a voltage divider. Code Compliance
Easiest to meet code requirements.
Revenue Grade Suitability
Preferred method for revenue-grade metering due to accuracy and isolation.
Cons
Cost
Adds the expense of the CPTs.
Space
Requires space to mount the transformers.
Implementation Details
Fusing
Crucially, you MUST provide properly sized overcurrent protection (fuses or a small circuit breaker) on the primary side of the CPT. Size the fusing according to the transformer's VA rating.
Secondary Wiring
Run appropriately sized wires (e.g., #14 AWG) from the CPT secondary to the meter's voltage inputs. Consider using terminal blocks for clean connections.
Grounding
Ensure proper grounding of the transformer's secondary neutral (if applicable) and the meter.2.
Voltage Taps with Fuses and Voltage Divider (Less Recommended)
How it Works
This involves directly tapping the wireway conductors, but with careful overcurrent protection and voltage reduction.
Pros
Potentially Lower Cost
If you can find suitable components.
Cons
Safety Concerns
Directly tapping high-current conductors is inherently risky. A fault in the metering circuit could lead to a major arc flash hazard.
Complexity
Designing a reliable and safe voltage divider circuit requires careful engineering.
Accuracy
Voltage dividers can be sensitive to component tolerances and temperature variations, potentially affecting metering accuracy. Likely not suitable for revenue-grade metering.
Code Compliance
More difficult to demonstrate code compliance, especially regarding short-circuit protection and conductor ampacity.
Implementation Details (if you MUST use this)
Fusing
Install high-quality, fast-acting fuses (e.g., CC or J class) immediately at the tap point on each phase conductor. Size the fuses very conservatively to protect the downstream metering circuit.
Voltage Divider
Use a voltage divider network to reduce the voltage to a level suitable for the meter (e.g., 120V or less). Use high-precision resistors with adequate wattage ratings. Consider using a pre-packaged voltage transducer designed for metering applications.
Enclosure
Enclose the entire voltage tap, fusing, and voltage divider network in a robust, grounded enclosure to prevent accidental contact and protect against environmental factors.
Professional Engineering Review
This approach absolutely requires review and approval by a qualified electrical engineer to ensure safety and code compliance.3.
Specialized Metering Tap Boxes (Consider if available for your system)
How it Works
Some manufacturers offer pre-engineered tap boxes specifically designed for metering applications off busways or wireways. These boxes typically include fusing, voltage reduction, and connection points for the meter.
Pros
Integrated Solution
Simplifies installation and reduces the risk of errors.
Safety
Designed with safety in mind, including overcurrent protection and isolation.
May be Pre-Certified
Might have certifications that ease the approval process.
Cons
Availability
Might not be readily available for your specific wireway type and voltage.
Cost
Can be more expensive than building a solution from individual components.
Implementation Details
Contact Wireway/Busway Manufacturer
Check with the wireway/busway manufacturer to see if they offer compatible metering tap boxes.
Review Specifications
Carefully review the specifications of the tap box to ensure it meets your voltage, current, and metering requirements.
Diagram from Eaton (and its limitations in your case)
The Eaton diagram you attached is helpful, but it assumes a panelboard or similar distribution point. You don't have that luxury with a wireway. The diagram essentially shows a breaker within a panel acting as the overcurrent protection and providing the voltage source. Since you don't have an easy way to install small breakers for this, the diagram becomes less relevant.
Recommendations
Prioritize CPTs
The Control Power Transformer approach is the safest, most reliable, and generally recommended method, especially for revenue-grade metering and LEED compliance. The cost is justified by the increased safety, accuracy, and reduced risk of problems down the road. Talk to your electrical contractor and engineer about sourcing appropriately sized and fused CPTs.2.
Explore Metering Tap Boxes
Contact the wireway manufacturer to see if they offer any pre-engineered metering tap boxes. If so, carefully review their specifications.3.
Avoid Direct Tapping (if possible)
Only consider the direct tapping with fuses and a voltage divider as a last resort. It's significantly more complex, riskier, and less likely to meet revenue-grade metering standards. If you pursue this, engage a qualified electrical engineer immediately to design and approve the solution.4.
Consult with Your Electrical Engineer
Crucially, discuss all these options with your electrical engineer. They can help you select the best solution based on your specific project requirements, budget, and local codes. They'll also be responsible for ensuring the design is safe and code-compliant.5.
Consider Future Expansion
Think about future tenant space additions and make sure your wireway and metering plan have enough capacity.
Key Questions to Discuss with Your Engineer/Contractor: What is the available fault current at the wireway? (This is critical for proper fuse sizing). What are the specific revenue-grade metering requirements in your jurisdiction? What space is available for CPTs or tap boxes?* What are the long-term maintenance and reliability considerations?By carefully considering these factors and consulting with qualified professionals, you can develop a safe, accurate, and code-compliant metering plan for your tenant spaces. Good luck! Flag for review