Topic: Panelboard fully rate

User: binwork91, Location: new york

Asked on: Friday, September 12, 2025 at 3:57 pm EDT
Answered on: Friday, September 12, 2025 at 3:57 pm EDT

Question: I understand that when we talk about a fully rated system, the lowest-rated component determines the overall rating.My question is: If I have a cutsheet showing 10 kAIC fully rated with a 35 kAIC breaker, but the equipment catalog states that this panelboard has interrupting ratings up to 200 kA symmetrical—can I say this panelboard is 35 kAIC fully rated instead of 10 kAIC?Please see the picture below. It shows 10 kAIC fully rated with a PDD23F breaker (rated 35 kAIC). This is a PRL1X panelboard, and the Eaton catalog states, "Interrupting ratings up to 200 kA symmetrical." Can I consider this panelboard 35 kAIC fully rated?I know the best practice is to request an updated cutsheet from the supplier showing 35 kAIC fully rated, but that takes time.If this PRL1X panelboard is limited to 10 kAIC due to any component (other than the breaker), then I will need to have the cutsheet updated to reflect a 35 kAIC fully rated panel.However, if all PRL1X panelboards are identical regardless of whether they are labeled 10 kAIC or 200 kAIC fully rated—or if the panelboard itself is rated for 200 kA symmetrical—then I can assume the rating is determined by the breaker. In that case, I would not need to request an updated cutsheet from the supplier, and I can confirm it is 35 kAIC fully rated, not 10 kAIC fully rated.

Okay, let's break this down. You're right to be cautious. The "fully rated" concept is crucial for safety and code compliance. You cannot simply assume the panelboard is 35kAIC based solely on the breaker rating and the catalog's potential interrupting rating. Here's why and what to consider

Why you can't assume 35 kAIC:
Weakest Link Principle

A "fully rated" system is only as strong as its weakest link. If any component within the panelboard assembly has a lower AIC rating than the breaker,
that is the overall AIC rating of the entire assembly. This could be the busbars, the individual breaker stabs, the wiring connections within the panelboard, or even the physical structure of the enclosure.

Cut Sheet is King (for this specific configuration)

The cut sheet represents the specific configuration as tested and certified. It says this specific configuration of the panelboard is rated for 10 kAIC with that specific breaker. The catalog rating is a maximum potential rating for the product line under specific conditions.

Panelboard Construction Differences

Just because a panelboard
can be built to handle 200 kAIC doesn't mean every panelboard in the PRL1X line is built that way. Different components, busbar sizes, and bracing might be used to achieve different interrupting ratings.

What you need to verify


Specifically Designed and Tested Combinations
The interrupting ratings (AIC) of a panelboard and its branch circuit breaker combinations are tested and labeled at a nationally recognized testing laboratory (NRTL), for example, UL or ETL.2. Check the Panelboard Label

Look very closely at the panelboard label
itself. It may have more detailed information about the specific components and interrupting rating of that particular assembly.3.

Consult the Manufacturer (Eaton)

This is the
most reliable approach. Explain the situation to Eaton's technical support. Give them the exact model number and serial number of the panelboard, the exact breaker model number, and the existing cut sheet information. Ask them: "Can this specific panelboard (with its current internal components) be field-modified or verified to be fully rated at 35 kAIC when used with a PDD23F breaker?" "Is there any documentation (other than the catalog) that confirms this configuration is rated for 35 kAIC?" "What, if any, components within the panelboard would limit the AIC rating to 10kAIC when the breaker is rated higher?"

What could be happening?
Standard Build vs. High Interrupting Build

The panelboard
could be a "standard" PRL1X model that simply isn't designed for higher fault currents, even though the potential exists within the PRL1X line.

Component Limitation

A specific component inside the panelboard (busbar size, stabs, etc.) may be the limiting factor and rated for only 10 kAIC.

Testing and Listing Constraints

The
specific combination of that panelboard and breaker may simply never have been tested and listed at 35 kAIC, even if the components could theoretically handle it. NRTL listings are based on tested combinations, not theoretical calculations.

In summary



Do NOT assume 35 kAIC based on the breaker and catalog alone.
This is a potential safety hazard. The existing cut sheet stating 10 kAIC is your current limiting factor. Contact Eaton directly for clarification and supporting documentation. They are the only ones who can definitively tell you if the panelboard, as built, can be considered fully rated at 35 kAIC with that breaker.* Get the updated cut sheet from the supplier if Eaton confirms it. You'll need that documentation for your records and for inspection. Flag for review