Question: Haven't done much underground conduit work and am wanting to know just how much pulling force will need to be exerted. The pulling app I usually use just lists wire, not cable. Is there a pulling app you fine folks know of that gives calculations for tray cable in conduit?The three conduit runs are 200 feet of 2" PVC with 2" rigid 6ft stub ups. There's two 90's in the PVC and another two 90's in the rigid. The pull is expected to be one 3 conductor #8 tray cable and one 16 conductor #16 tray cable. Yeah, going for large radius 90's, even if I gotta make them myself, and ordering a 5,000 gallon tanker of lube.
Okay, let's break down this pulling force calculation for your tray cable installation. You're right, many pulling apps are geared towards individual wires and not multi-conductor cables, especially tray cable. This makes it a bit more challenging, but we can estimate.
Challenges & Key Considerations
Tray Cable Complexity
Tray cable (TC) has a larger surface area than individual conductors and often has a thicker, less flexible jacket. This contributes significantly to friction. The construction of the cable (shielding, fillers, etc.) also affects friction.
Fill Percentage
While technically not exceeding the fill percentage, pulling two cables of different sizes will cause them to twist and turn around each other which will also contribute to friction.
Bend Multipliers
90-degree bends are the major friction contributors.
Lube
You're wise to plan for ample lubricant. The right type is critical (more on that later).
Temperature
Colder temperatures make cable less flexible and increase pulling force.
Here's a step-by-step approach to estimating pulling force
1. Data Gathering
Exact Cable Specs
Get the exact outer diameter (OD) of both the 3-conductor #8 TC and the 16-conductor #16 TC. This is crucial. Look at the manufacturer's data sheets or physically measure the cables. Also note the cable jacket material (e.g., PVC, XLPE, etc.).
Conduit Type & Condition
You know it's 2" PVC and Rigid. Note its internal Diameter. Make sure the conduit is clean inside, free of debris.
Bend Radius
While you're planning for large radius bends, what's the actual radius you're aiming for? This affects the bend multiplier. NEC guidelines provide minimum bend radii.
Lube Type
What lubricant will you use? Different lubricants have different coefficients of friction.
2. Calculating Raceway Lengths and Bend Degrees
Straight Sections
200 feet of PVC.
Stub Ups
6 feet of Rigid each = 12 feet total Rigid.
Bends
Two 90-degree bends in PVC (180 degrees total PVC).
Bends
Two 90-degree bends in Rigid (180 degrees total Rigid).
3. Estimating Pulling Force (This requires some assumptions)
Since most apps don't directly calculate TC in conduit, we'll use a combination of methods and be conservative in our estimates.
a. Fill Percentage Check
Verify the combined cross-sectional area of the two cables does not exceed 40% of the conduit's internal area per NEC. It probably will, but it's essential to confirm.
b. Simplified Approach (Highest Friction)
Assume a coefficient of friction (COF) for cable on PVC of 0.5. This is a relatively high value. A good lubricant can lower this, but let's be safe. Assume a COF for cable on Rigid of 0.6. (Slightly higher due to potentially rougher surface). Calculate the total weight of the cable in the conduit: Determine the weight per foot of each cable from the manufacturer's data. Multiply by the total length of the conduit run (200 ft + 12 ft = 212 ft). Add the two weights together. Calculate the straight pull force: `Force (straight) = COF Total Weight`. Calculate the bend force for each 90-degree bend: `Force (bend) = Force (straight) (1 + COF Bend Angle in Radians)`. Where the bend angle in radians is 90 degrees (pi/180) = 1.57 radians. Add all the forces together: `Total Pulling Force = Force (straight) + (4 Force (bend))` (4 bends total).
c. Using Wire Pulling Apps (Indirectly)
Treat each cable as a single, equivalent wire. This is a very rough estimate. Calculate the total circular mil area of all conductors in both cables. (e.g., #8 has a certain circular mil area, multiply by 3, then #16 has a circular mil area, multiply by 16. Add the results). Use a wire pulling app like Southwire's (or similar) and input this total circular mil area as if it were a single large conductor. Use the outer diameter of the larger cable as the "wire diameter." Important: Use a high coefficient of friction (COF) for cable in PVC/Rigid. 0.5-0.6 is a good starting point. Overestimate the number of bends slightly.
This method will likely OVERESTIMATE the force, but better safe than sorry.4. Lube Selection & Application
Choose the Right Lube
Use a polymer-based cable pulling lubricant specifically designed for tray cable and compatible with the cable jacket and conduit materials (check the lubricant's data sheet). Do not use grease or petroleum-based lubricants, as they can damage cable jackets.
Apply Liberally
Coat the cables thoroughly as they enter the conduit. Use a pump or bucket with a pouring spout to ensure even coverage. Re-apply during the pull if needed. The 5,000-gallon tanker might be slight overkill.
5. Pulling Techniques
Pulling Eye/Grip
Use a proper pulling eye or basket grip designed for tray cable. Make sure it's securely attached.
Tension Monitoring
Use a dynamometer or load cell to monitor the pulling force during the pull.
Never exceed the manufacturer's recommended maximum pulling tension for the cables. This is critical. If you don't know the allowable tension, contact the cable manufacturer. Slow & Steady
Pull slowly and steadily. Avoid jerking or sudden changes in force.
Communication
Have clear communication between the person pulling and the person feeding the cable.
Consider Intermediate Pull Points
If the calculated pulling force is very high, or if you encounter resistance during the pull, consider installing pull boxes or using intermediate pull points.
6. Important Considerations & Warnings
Cable Damage
Excessive pulling force can damage the cable insulation and conductors, leading to premature failure or even immediate shorts.
NEC Compliance
Ensure your installation meets all applicable NEC requirements, including conduit fill, bending radii, and support requirements.
Manufacturer's Instructions
Always follow the cable and conduit manufacturer's instructions.
Example Using Simplified Approach
Let's pretend you've looked up your data. #8 3 Conductor TC weighs .75 lbs/ft and the #16 16 Conductor TC weighs 1 lb/ft. Total weight in conduit: (212ft .75 lbs/ft) + (212ft 1 lb/ft) = 159 lbs + 212 lbs = 371 lbs Force (straight) = .5 COF 371 lbs = 185.5 lbs Force (bend) = 185.5lbs (1 + (.5 1.57 radians)) = 331.6 lbs Total Pulling Force = 185.5lbs + (4 331.6 lbs) = 1511.9 lbsDisclaimer
These calculations are estimates. The actual pulling force can vary significantly depending on the factors mentioned above.
Always consult with a qualified engineer or experienced electrician for critical installations or when pulling large, expensive cables. It's better to be overly cautious and safe than to risk damaging the cable or equipment. And of course, all work should conform to local and national electrical codes.Consider getting quotes from electrical contractors specializing in underground cable pulling. They have the tools and experience to do the job safely and efficiently. They might have pulling force measurement devices, and have a better idea of what realistic friction coefficients are.Good luck with your project! Flag for review