Question: Sorry for being new and doing electrical work in a plant...We need to run electrical to outlets for a deck that's basically sitting on the ground. This isn't the normal strap it to kindorf stuff that I'm used to and I'm not sure where I'd find this in the code.If we need to run rigid 20' and can't get a clean shot at the screws for straps, does this need to be trenched and buried in lieu of support?Also order THWN and received THHN. Any thoughts there?Really trying my best to get away from just pulling SO mentality.
Okay, no problem at all! It's great that you're prioritizing code compliance and safety. Let's break down these questions related to running electrical conduit and wiring for a ground-level deck in a plant environment.1. Supporting Rigid Conduit on a Ground-Level Deck The Challenge
You're right – attaching rigid conduit to a ground-level deck structure with standard straps can be tricky if you don't have good access to the mounting surfaces.
Code References
The primary code section you're looking for is in the NEC (National Electrical Code), Article 344 (Rigid Metal Conduit: RMC). Specific sections within Article 344 will address support requirements. You'll also want to look at Article 300 (Wiring Methods) for general wiring requirements.
Options and Considerations
Direct Burial
Yes, burying the conduit is a viable option, but it has specific requirements:
Depth
Table 300.5 specifies minimum burial depths based on voltage and use. In a plant environment, you'll likely need deeper burial than a residential setting due to potential heavy equipment traffic or other industrial hazards.
Conduit Type
While RMC is suitable for direct burial, you might also consider PVC-coated RMC (which provides added corrosion protection).
Backfill
Use approved backfill material (usually sand or fine gravel) to avoid damaging the conduit during compaction.
Warning Tape
Place warning tape above the conduit before backfilling to alert anyone digging in the future.
Surface Mounting with Innovative Supports
Concrete Anchors
If the deck is on a concrete pad, you can use concrete anchors to secure conduit straps.
Custom Supports
You could fabricate or purchase custom supports designed to rest on the ground and elevate the conduit. These supports should be corrosion-resistant and securely attached to the conduit. Consider using unistrut or similar channel systems that can be anchored to the ground or deck structure.
Saddle Supports
Saddle supports are designed to hold conduit off the ground and can be attached to a surface or used with stakes for direct ground support.
Spacing of Supports
NEC 344.30 specifies the maximum spacing between supports for RMC. This spacing depends on the conduit size. You need to support the conduit at intervals that prevent sagging or damage. Exceeding these spacings is a code violation.
Important Considerations for Industrial Environments
Corrosion
Plant environments can be harsh. Choose conduit and fittings that are resistant to the specific chemicals and conditions present.
Physical Protection
Consider whether the conduit needs additional protection from impact or abrasion.
Grounding
Ensure proper grounding of the conduit system. This is crucial for safety in an industrial setting.
2. THHN vs. THWN Wire Similarities
Both THHN and THWN are common building wires insulated with thermoplastic high heat-resistant nylon.
Key Difference
The "W" in THWN indicates that the wire is also suitable for wet locations. THHN is suitable for dry or damp locations.
Using THHN When THWN is Specified
If you ordered THWN and received THHN, it's not automatically a problem, but you need to evaluate the environment.
If the Conduit is in a Dry Location
If the conduit run is entirely indoors and you are confident that it will remain dry, THHN is acceptable.
If the Conduit is in a Damp or Wet Location
You cannot use THHN alone. The inside of a conduit buried underground, or even exposed to the elements, is generally considered a wet location.
3. Avoiding "SO Cord Mentality" Understanding the Issue
Using SO cord (flexible cord) for permanent wiring is a common shortcut but is generally a code violation unless specifically allowed for a particular application (e.g., connecting portable equipment).
Why it's Bad
SO cord is not designed for permanent installation. It's more susceptible to damage, abrasion, and degradation over time compared to properly installed conduit and wiring. It also lacks the mechanical protection of a conduit system.
Best Practices
Use Approved Wiring Methods
Stick to approved wiring methods for permanent installations, such as conduit systems (RMC, IMC, PVC), cable trays, or appropriate cable types like MC (Metal Clad) cable.
Consult the NEC
Refer to the NEC for allowed wiring methods and specific requirements for different applications.
Document Your Work
Keep detailed records of your electrical installations, including materials used, wiring diagrams, and inspection reports.
Action Plan
Consult the NEC
Review NEC Articles 300 and 344 carefully.2.
Assess the Environment
Determine whether the conduit run will be in a dry, damp, or wet location.3.
Choose the Appropriate Wiring Method
Select a wiring method that meets the code requirements and is suitable for the environment (e.g., direct burial, surface mounting with proper supports).4.
Ensure Proper Grounding
Implement a grounding system that complies with the NEC.5.
Get it Inspected
Have your work inspected by a qualified electrical inspector to ensure compliance with the code.
Important Note: This information is for general guidance only. Electrical codes and regulations can vary depending on your location. It is essential to consult the latest edition of the NEC, local electrical codes, and a qualified electrician to ensure compliance and safety. Flag for review