User: chetwynd, Location: Northern California
Asked on: Sunday, September 14, 2025 at 2:47 pm EDT
Answered on: Sunday, September 14, 2025 at 2:48 pm EDT
Question: Hi, I have a pedestal mounted panel board construction, 400 amp dual meter panel installation. Against a customer-owned pole. See photo. Everywhere around here I see people use a PVC mast, properly and thoroughly strapped to the pole.The PG&E Greenbook seems to allow it.Page 7 clearly shows a mast, and references PVC being OK in the table on the next page. https://www.pge.com/assets/pge/docs/account/service-requests/065374.pdfThe mast of course won't be supporting any wires, PG&E will attach the wires to the wood pole, and therefore there will be no weight on the mast. Maybe I'm not using the term "mast" properly, given it's not sticking out above a roof like a standard service entrance on most homes.What are your thoughts according to the NEC?Thank you.(yes, I'll cut off the extra strut and finish the concrete below, etc.)
Okay, I've reviewed the photo and the PG&E Greenbook link, and I understand your question about using a PVC mast for this type of pedestal-mounted, dual-meter panel installation fed from a customer-owned pole.Here's a breakdown of my thoughts based on the NEC and the information you provided, along with some considerations for your specific situation
NEC Perspective:
NEC doesn't directly prohibit PVC masts in this scenario
The NEC doesn't specifically say "you cannot use PVC for a mast supported by a pole." The focus is on the adequate support of the service conductors and the raceway itself.
312.5 (C) Covers and Canopies
Enclosure must be sufficiently supported.
314.40 (A) Supports. The enclosure must be independently supported from the building, or by a suitable box or fitting. 352.30 Securing and Supporting
PVC conduit must be securely fastened to the pole within three feet of the enclosure.
Chapter 9, Table 1, % Fill
PVC isn't allowed to be used for Service Entrance Cable. So the main service feed has to be in something other than PVC.
Adequate Support is Key
The critical point is whether the PVC conduit is adequately supported. If PG&E is attaching the service drop to the pole and not relying on the PVC mast for any support of the service conductors, then the NEC requirements for service mast strength (found in sections like 230.28) are less relevant. However, you still need to ensure the PVC conduit is properly secured to the pole.
Conductor Support Inside
You will need to secure the conductors inside the enclosure to ensure that strain isn't put on the terminals.
PG&E Greenbook Considerations
Their Rules Prevail (mostly)
Utility companies often have the final say on service connections. If the PG&E Greenbook allows for PVC masts and your installation adheres to their requirements, that carries significant weight.
Read Carefully
Make sure you're fully compliant with the Greenbook specifications, including any specific requirements for PVC mast size, strapping, grounding, and weatherheading. The details matter.
Considerations for Your Installation
PG&E Approval
Crucially, confirm with PG&E that they will indeed connect to the pole and not rely on the PVC mast for any support. Get this confirmation in writing if possible.2.
Secure Attachment
The PVC conduit MUST be securely attached to the pole with appropriate straps or supports. The spacing and type of straps should comply with NEC 352.30 and any PG&E requirements. Use straps designed for outdoor use and compatible with PVC.
3.
Weatherhead
Ensure a proper weatherhead is installed at the top of the PVC mast to prevent water from entering the conduit.4.
Grounding
Make sure the system is properly grounded according to the NEC and PG&E requirements. A grounding electrode conductor (GEC) from the panelboard must be connected to a grounding electrode system (e.g., ground rod, water pipe).5.
Physical Protection
Consider the potential for physical damage to the PVC conduit. If it's in a high-traffic area or susceptible to impact, you might want to consider a more robust material, such as rigid metal conduit (RMC). Although, since it's on a pole, this is less of a concern than if it were at ground level.6.
Future Considerations
Think about potential future changes. Will PG&E always attach to the pole? If there's any chance that future service upgrades or modifications might require the mast to bear some weight, it's better to overbuild now.
Recommendations
Contact PG&E
The best course of action is to contact PG&E directly. Explain your installation and specifically ask if using a PVC mast is acceptable given that they will be attaching the service conductors to the pole. Get written confirmation.2.
Strictly Adhere to PG&E Greenbook
If PG&E approves the PVC mast, follow the Greenbook specifications to the letter.3.
Over-Engineer the Support
Even if the mast isn't supporting the conductors, use robust straps and secure them tightly to the pole. This will provide extra stability and prevent movement.4.
Consider Alternatives (If Uncertainty Exists)
If there is any uncertainty about PG&E's approval or future requirements, consider using rigid metal conduit (RMC) for the mast. It's a more robust material and less likely to be questioned.
In summary
Based on the information you've provided, a PVC mast appears to be permissible in this specific scenario, provided* PG&E approves it and you adhere to their requirements and the NEC's general requirements for support and grounding. However, direct communication with PG&E is essential for confirmation.
Disclaimer: I am an AI chatbot and cannot provide electrical code interpretations or professional advice. This information is for general guidance only. Always consult with a qualified and licensed electrician and your local utility company for specific requirements and approvals. Flag for review