Question: IF splices are made in a wire way it must not fill more than 75% of that space.Does this include calculating wire nuts area? How would this be done? We are speaking of a square length x height measurement but not a cubic volume measure l x h x w correct?

You are correct on both counts. Let's break it down: 75% Fill Rule

NEC 376.22 (or similar sections in other "Wireway" articles) limits the total cross-sectional area of conductors and splices to 75% of the wireway's interior cross-sectional area at the splice point.


Wire Nuts and Splices



Yes, the cross-sectional area occupied by wire connectors (like wire nuts, split bolts, etc.) must be included in the fill calculation.
This is because they physically occupy space within the wireway and contribute to the overall congestion. Area Calculation (Length x Height - 2D)

You are also correct in that the calculation is based on
area, not volume. You're determining the cross-sectional area that all the conductors and splices take up within the wireway's cross-section.

How to Determine Wire Nut Area

This is where it can get a little tricky because wire nuts don't have a uniform shape. Here's a practical approach:1.

Manufacturer Specifications (Best Option)

If possible, the best approach is to get the maximum outside diameter or dimensions of the wire nuts you intend to use from the manufacturer's datasheet or website. Treat the wire nut as either a circle (using the diameter to calculate the area of a circle: πr²) or a rectangle (if it's more elongated, use length x width).2.

Physical Measurement (If Specs Unavailable)

If you can't find the manufacturer's data, you'll need to physically measure the wire nuts you're using.
Use calipers to measure the maximum diameter or dimensions of the wire nut after it has been properly installed on the wires. This is important because the wires add to the overall size. As above, treat the wire nut as a circle or rectangle for area calculation.3.

Estimate Carefully

If you are estimating wire nut sizes for a job before you start, error on the side of caution. Wireways are cheaper to install and run new wire into than it is to install a new wireway!

Example

Let's say you have a wireway that is 4 inches wide and 4 inches high (16 square inches total cross-sectional area). The allowable fill is 75%, so you can use 16 x 0.75 = 12 square inches of that space for conductors and splices.You have 10 conductors that each take up 0.5 square inches of area (including insulation). That's 5 square inches.Now, let's say you have 5 wire nuts. You measure each wire nut and find it occupies approximately 0.75 square inches of cross-sectional area after the wires are installed. That's 5 x 0.75 = 3.75 square inches.Total fill: 5 sq. in (conductors) + 3.75 sq. in (wire nuts) = 8.75 sq. in.Since 8.75 square inches is less than the allowable 12 square inches, you're within the fill limit.

Important Considerations



Neatness

While the code specifies fill limits, remember that a neat and well-organized wiring job is always best. Avoid stuffing conductors and splices into a wireway haphazardly, even if you're technically within the fill limit. This helps with heat dissipation and makes troubleshooting easier.

Derating

High conductor fill can impact the ampacity of the conductors. Consider derating factors if you have many current-carrying conductors in a wireway (see NEC 310.15).


Access

Code requirements also mandate adequate access to conductors and splices within wireways. Be sure to allow space to work.

In summary:
Yes, include the area of wire nuts in your wireway fill calculations, and yes, you're calculating cross-sectional area (2D), not volume. Flag for review