Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Calculating 3-Phase Hi Leg Service Size.

User: Mirwin, Location: Defuniak Springs, Florida

Asked on: Monday, September 15, 2025 at 10:29 am EDT
Answered on: Monday, September 15, 2025 at 10:35 am EDT

Question: I am trying to perform a load calculation for a project that will feature a 3-phase, high-leg delta system with a 120/240V voltage. I have compiled all the load information for the project and applied the relevant demand factors to the appliance loads for this occupancy (a restaurant).My total VA after demand factors are applied is 112,752 VA.I am familiar with the formula for a 120/208V, 3-phase service.Total VA / (volts x 1.732) = AmpsDoes the same formula work for the hi-leg calculation?For example: 112,752 / (240 x 1.732) = 271Amps.I checked Annex D in the NEC and didn't see any hi-leg load calculation examples.

Yes, your calculation is correct! The formula `Total VA / (Volts x 1.732) = Amps` works for a high-leg delta system as long as you are using the line-to-line voltage (240V in your case).Here's why: 3-Phase Power Basics

The formula stems from the fundamental relationship of power in a balanced 3-phase system. Total VA (Volt-Amps) is related to the line-to-line voltage (V) and the line current (I) by:VA = √3
V I (where √3 is approximately 1.732)

High-Leg Delta and Balanced Loads

The formula assumes a relatively balanced load across the three phases. In other words, the total VA you've calculated is considered to be distributed fairly evenly among the three phases. While a high-leg delta can inherently handle some imbalance, significantly unbalanced loads can lead to inaccurate current calculations and potential issues. For highly unbalanced systems, a more detailed phase-by-phase analysis would be necessary.

Using Line-to-Line Voltage

The "V" in the formula
must be the line-to-line voltage. In a 120/240V high-leg delta system, the line-to-line voltage is 240V. You are not using the 120V in this formula because this voltage is line-to-neutral and this calculation is for the overall 3-phase service.

NEC Annex D

You're right that Annex D doesn't have specific high-leg examples. It primarily focuses on standard wye and delta systems. The principles are the same, but understanding the specific voltage configurations is key.

Therefore, your calculation: 112,752 VA / (240V x 1.732) = 271 Amps is the correct way to estimate the total service current for the 3-phase portion of your load.
Important Considerations and Best Practices

1.

Single-Phase Loads

Your 112,752 VA likely doesn't include all single-phase 120V loads connected line-to-neutral. You'll need to calculate the current for these separately. These single-phase loads will primarily use the A and C phases (the ones providing 120V to neutral) and should be balanced as much as possible between those two phases. The High-leg (B Phase) can not be used for single-phase loads.2.

Neutral Load

Calculate the neutral load separately. This is particularly important in a high-leg delta system, as imbalances in the 120V loads will contribute to neutral current. Note that in the US, the NEC allows for a reduced neutral conductor size under certain conditions (see NEC Article 220.61).
3.


Oversizing

It's generally a good practice to add a safety factor (oversize) to your calculated current. This accounts for future load growth or unforeseen circumstances. Consider increasing your calculated current by at least 15-25% when selecting service conductors and overcurrent protection.4.

NEC Compliance

Always consult the National Electrical Code (NEC) and local codes for specific requirements related to service sizing, conductor ampacity, overcurrent protection, and high-leg delta systems. Pay attention to articles like:

Article 220

Load Calculations


Article 215

Feeders*

Article 230

Services5.

Phase Balancing

Strive to balance the loads across all three phases as evenly as possible. This is crucial for efficient operation and minimizing voltage imbalances.6.

High-Leg Identification

Ensure the high-leg is permanently identified with orange marking per NEC requirements.7.

Professional Review

Given the complexity of electrical systems, it's always recommended to have your load calculations and electrical design reviewed by a qualified electrical engineer or licensed electrician.

In summary, your initial calculation is correct for the 3-phase portion of the load, but you need to account for single-phase 120V loads, neutral load, and safety factors, as well as comply with all applicable codes and regulations. Consult a qualified professional for final design and verification.
Flag for review

Previous Question Next Question