Question: Per 2017 NEC 760; are there any circumstances where fire alarm circuits can be combined with other wiring systems?

According to the 2017 NEC Section 760.136(A) through (I), there are very limited circumstances where fire alarm circuits can be combined with other wiring systems. Here's a breakdown

General Prohibition:

In general, fire alarm circuit wiring must be kept separate from other wiring systems. The NEC emphasizes maintaining the integrity and reliability of the fire alarm system.

Permitted Combinations (with very specific restrictions)



760.136(A) Wiring Systems Allowed



Fire Alarm Circuits Only

Fire alarm circuits are allowed to be installed in the same raceway, cable, enclosure, junction box, or similar fittings as other fire alarm circuits, provided that all conductors are insulated for the maximum voltage of any conductor within the enclosure or raceway.

760.136(B) Non-Power-Limited Fire Alarm (NPLFA) Circuits



Raceway, Cable, and Enclosure

NPLFA circuits shall be permitted to be installed with conductors of other NPLFA circuits, general electrical circuits, and Class 1 circuits, provided they are separated by a barrier or installed in separate raceways, cables, or enclosures.

Junction Box

NPLFA circuits are permitted to be installed in the same junction box as other NPLFA circuits, general electrical circuits, and Class 1 circuits, provided the conductors are separated by a barrier or maintained at least 0.25 inches apart.


760.136(C) Power-Limited Fire Alarm (PLFA) Circuits and Class 3 Cables



Raceway, Cable, and Enclosure

PLFA circuits and Class 3 cables shall be permitted to be installed with conductors of other PLFA circuits, Class 2 circuits, and communications circuits, provided they are separated by a barrier or installed in separate raceways, cables, or enclosures.


Junction Box

PLFA circuits and Class 3 cables are permitted to be installed in the same junction box as other PLFA circuits, Class 2 circuits, and communications circuits, provided the conductors are separated by a barrier or maintained at least 0.25 inches apart.

760.136(D) Fire Alarm Cables



Cables in Raceways, Cable Trays, and Enclosures

Fire alarm cables are permitted to be installed in the same raceways, cable trays, and enclosures as other wiring systems.

760.136(E) Other Applications



Specific Manufacturer Instructions

Follow the manufacturer's instructions for combining fire alarm circuits with other systems when explicitly allowed by the manufacturer's listed equipment.

Key Considerations and Restrictions



Voltage Ratings

All conductors within a raceway or enclosure must be insulated for the highest voltage present.


Physical Separation

Where permitted, circuits must often be separated by a barrier or maintained a specified distance (e.g., 0.25 inches) apart.

Dedicated Raceways/Enclosures

The best practice and often required method is to use separate raceways or enclosures for fire alarm wiring whenever possible to ensure maximum reliability.


Cable Types

The specific cable types permitted for fire alarm circuits and their installation methods are crucial.

Listing and Labeling

Equipment must be listed and labeled for its intended use, which might influence permissible combinations.


Approved Methods

Wiring methods must be approved for fire alarm use.

In Summary:


While there are some limited circumstances where fire alarm circuits can be combined with other wiring, they are heavily restricted and often discouraged. The overriding principle is to maintain the reliability and integrity of the fire alarm system. Always prioritize separate wiring systems for fire alarm circuits, and carefully consult the NEC and manufacturer's instructions for any permitted combinations. When in doubt, err on the side of caution and use separate wiring systems. It's best to consult with a qualified electrical inspector or fire alarm specialist for specific installations. Flag for review