Question: I took my Washington Administrator test on Friday - and it looks like I have re-take the load calculations section. I want your opinions on a hypothetical duplex with a standard calculation: if each unit had only 3 appliances (per 220.53), would you apply the 75% demand factor? The duplex as a whole would have 6 total appliances, which qualifies it for the 75% demand factor; yet the way I was taught was to look at each side of the duplex individually. Therefore, only 3 appliances per unit would mean it doesn't qualify for the 75%. What is the correct way to calculate this?
This is a tricky question and highlights a common point of confusion in load calculations. Here's the breakdown of why the correct answer is likely NO, you should NOT apply the 75% demand factor separately to each unit in this case.Understanding the Code NEC 220.53
This section allows a demand factor of 75% to be applied to the nameplate rating of four or more appliances fastened in place on the same premises, other than ranges, clothes dryers, space-heating, and air-conditioning equipment.
The Key Phrase: "Same Premises" The crux of the matter is the interpretation of "same premises." In a duplex, both units are considered to be on the same premises for the purpose of electrical calculations, especially when you're sizing the service to the entire building.
Why You Don't Apply it to Individual Units1. Service Calculation Focus
When calculating the service load for the entire duplex, you're concerned with the total load the service must be able to handle. The code is designed to acknowledge that not all appliances in all units will be running simultaneously at their maximum load.2.
Intent of the Demand Factor
The 75% demand factor is based on statistical probability. With more appliances, the likelihood of all of them running at full load simultaneously decreases. If you treat each unit separately, you are essentially ignoring the diversity across the entire duplex.3.
Practicality
Imagine a large apartment building. You wouldn't calculate each apartment's appliance load separately and then apply a demand factor to each. You'd look at the total number of appliances across the entire building to determine if the demand factor applies to the entire building's appliance load. A duplex is just a smaller version of the same principle.
How You Should Calculate It1. Determine the appliances
Identify the appliances in each unit that qualify under 220.53 (fastened in place, not ranges, dryers, heating, or AC).
2.
Total Appliances
Add up the total number of qualifying appliances across both units (in this case, 6).3.
Apply Demand Factor (if applicable)
Since you have 6 appliances (more than 4), you are eligible to apply the 75% demand factor to the total load of those appliances for the entire duplex when you calculate the service size.
Example
Let's say the appliances are dishwashers (10 amps each) for a total of 6 dishwashers. Total appliance load: 6 appliances 10 amps = 60 amps. Demand factor applies (because you have 6, >4). Load with demand factor: 60 amps 0.75 = 45 amps.You would use 45 amps for the appliance load in your overall service calculation, not calculate the load separately for each unit and try to apply a demand factor there.
Important Considerations for the Exam Read the Question Carefully
Pay extremely close attention to what the question is asking. Is it asking about the service calculation for the entire duplex or just a load calculation for an individual unit? This will determine how you apply the demand factors.
Context Matters
The question might provide information that changes the interpretation. For example, if each unit has its own separately metered service, the calculation might be different (but even then, most jurisdictions would still want the overall service to the building calculated considering the total load).
Think About the Big Picture: Always step back and consider the overall purpose of the load calculation: to ensure the electrical service is adequate for the entire building, considering realistic usage patterns.Good luck on your retake! Understanding these nuances will definitely help you succeed. And always, when in doubt, consult the actual code book. The precise wording is crucial. Flag for review