Question: Installed a 250kW natural gas generator. The 4" rigid conduits are risers from PVC conduit in the ground. Are the ridged conduits need to bonded to ground.
Yes, the rigid conduits serving a natural gas generator, especially where they transition from PVC underground, need to be bonded to ground. Here's why and what you need to consider
Reasons for Bonding:
Safety
Bonding provides a low-impedance path for fault current to return to the source (the generator's neutral). This is crucial for:
Prompt Overcurrent Device Operation
A fault current will quickly trip the circuit breaker or blow the fuse, minimizing the duration of the fault and the risk of electric shock or fire.
Reducing Touch Potential
Bonding helps keep all exposed metal parts at or near the same potential, minimizing the voltage difference between them and earth. This is particularly important near equipment where people may be present.
Lightning Protection
While bonding isn't a substitute for a dedicated lightning protection system, it can help mitigate the effects of lightning strikes by providing a path for the current to ground.
NEC Requirements
The National Electrical Code (NEC) has specific requirements for grounding and bonding, and these requirements typically apply to generators and their associated raceways.
NEC 250.104(A)
Requires grounding of metal water piping system(s) and exposed structural metal members that are interconnected to form a building frame or are of substantial size and are likely to become energized.
NEC 250.102 (C)
Sizing of equipment grounding conductors.
NEC 250.92: Methods of Equipment Bonding Gas Piping Bonding
While not directly related to the conduits, natural gas piping systems also require bonding to ground according to the NEC. This is to prevent differences in potential that could cause arcing across gas fittings, potentially leading to ignition. Because the generator uses natural gas, this requirement is particularly relevant.
Transition from Non-Metallic to Metallic
The transition from PVC (non-metallic) to rigid metal conduit creates a break in the continuous grounding path. The rigid conduit must be bonded to re-establish this path.
How to Bond the Rigid Conduits
Equipment Grounding Conductor (EGC)
A properly sized equipment grounding conductor (EGC) must be run inside the conduit, along with the circuit conductors. This EGC should originate at the generator's grounding terminal and terminate at the first overcurrent protection device (breaker or fuse) serving the generator. The EGC provides the primary fault current path.
Sizing the EGC
Use NEC Table 250.122 to determine the correct size of the EGC based on the rating of the overcurrent device.
2.
Bonding Bushings or Locknuts
Use bonding bushings or bonding locknuts where the rigid conduit enters enclosures (such as junction boxes or the generator enclosure). These fittings ensure a secure and reliable connection between the conduit and the enclosure, creating a continuous bonding path. Use a bonding jumper to connect the bonding bushing to the enclosure grounding terminal.3.
Bonding Jumper to Grounding Electrode System
A bonding jumper should connect the generator's grounding electrode conductor (GEC) connection point to the building's grounding electrode system. This ensures that the generator is properly referenced to earth ground.
Important Considerations
Local Codes
Always check and comply with local electrical codes, as they may have additional or more stringent requirements.
Qualified Electrician
Have a qualified electrician perform the bonding to ensure it is done correctly and safely. Incorrect bonding can be more dangerous than no bonding at all.
Inspection
After the installation is complete, have it inspected by a qualified electrical inspector to verify that it meets all applicable code requirements.
Generator Manufacturer's Instructions
Always follow the generator manufacturer's specific instructions for grounding and bonding.
In summary, bonding the rigid conduits is essential for the safe and compliant operation of your 250kW natural gas generator. It ensures a low-impedance fault current path, protects against electric shock and fire hazards, and complies with NEC requirements. Flag for review