User: Genepires, Location: Washington state
Asked on: Tuesday, September 16, 2025 at 11:39 am EDT
Answered on: Tuesday, September 16, 2025 at 11:41 am EDT
Question: I think i know answer but just checking with the smartest folks. If I size branch circuit conductors for a system with 4 continuous motors according to NEC430.24 i use the table based FLA with but there is no comment on the 125% for continuous duty. there is comment for sizing conductors for single motor.Take 125% of the FLC of the highest-rated motor.Add the FLC of all other motors on the same phase.Add 100% of any non-continuous non-motor loads and 125% of any continuous non-motor loads on the same feeder.The sum of these values is the minimum ampacity your conductors must handleI am thinking that I still need to use the 125% for all 4 motors and add the appropriate non motor loads.thanks y'all!
You are correct to question the application of the 125% factor. Let's break it down according to the NEC.
NEC 430.24 (Conductor Size) does NOT inherently require 125% for EACH individual motor. 430.24 is for sizing branch-circuit conductors that supply multiple motors. It focuses on the overall load. It specifies that you take 125% of the largest motor's Full-Load Current (FLC) and add the FLC of all the other motors on the same phase. This implicitly handles the fact that the largest motor will need to be able to start while the others are already running. This caters for the fact that motors are intermittent loads ( starting current is much higher than the running current.)Where does the 125% factor definitely come into play? NEC 430.22, for single motor applications.. If you have a single motor branch circuit, and the motor is continuous duty, then conductors must have an ampacity of not less than 125% of the motor's full-load current (FLC).
Addressing Your Specific Scenario (4 Continuous Motors)
In your situation with 4 motors on a single branch circuit, and assuming they're all considered continuous-duty, here's how you'd apply the NEC:1. Identify the Largest Motor
Determine the motor with the highest FLC from NEC tables (430.248, 430.249, and 430.250).
2.
Calculate 125% of the Largest Motor's FLC
Multiply the largest motor's FLC by 1.25.
3.
Add the FLC of Other Motors
Add the full-load currents (FLC) of the remaining three motors.4.
Non-Motor Loads
Add 100% of non-continuous non-motor loads and 125% of all continuous non-motor loads.5.
Total Ampacity
The sum of steps 2, 3, and 4 is the minimum ampacity your branch-circuit conductors must have. Select a conductor size from NEC Table 310.16 that meets or exceeds this ampacity, considering the conductor's insulation type and the ambient temperature.
Therefore, you do NOT need to apply 125% to all four motors individually and add them. You only apply the 125% to the largest motor's FLC and add the full FLC of the remaining motors.In Summary
Your initial understanding was partially correct but could have led to oversizing the conductors. NEC 430.24 already accounts for the starting requirements of the largest motor, while the other motors contribute their running currents. You only need to apply the 125% factor to the largest motor's FLC. Always remember to factor in any non-motor loads as well, applying the 125% factor to any continuous* non-motor loads. Flag for review