Topic: MLO Meterstack and one main bonding jumper

User: hhsting, Location: Glen bunie, md, us

Asked on: Tuesday, September 16, 2025 at 12:08 pm EDT
Answered on: Tuesday, September 16, 2025 at 12:14 pm EDT

Question: I have 600A MLO meterstack with 4x 200A meter/breaker. The meterstack is fed from utility service conductor.Under NEC 2017 Article 250.24(B) exception no. 1 would this be considered an assembly listed for use as service equipment so that one main bonding jumper is provided or it needs to be provided at each 200A meter/breaker?

This is a common and important question. Here's a breakdown of how the NEC 2017 applies and the most likely answer

Understanding NEC 250.24(B) and Exception No. 1
250.24(B)

This section deals with Grounding Electrode Conductor connections on the supply side of the service disconnecting means. It generally requires the grounding electrode conductor to be connected to the grounded conductor (neutral) at the service disconnecting means.


Exception No. 1

This is the key. It allows the connection of the grounding electrode conductor to the grounded conductor at more than one point if the service equipment is part of a listed assembly that is specifically designed for such multiple connections. The intent is to accommodate listed meter stacks and similar assemblies.

Applying it to your Situation
Listed Assembly is Critical

The applicability of Exception No. 1 hinges on whether your 600A MLO meter stack with 4x 200A meter/breakers is a
listed assembly. This means it has been tested and certified by a nationally recognized testing laboratory (NRTL) like UL, ETL, or CSA as a complete assembly.

Evidence of Listing

The most common way to confirm listing is to look for the NRTL's mark (e.g., a UL label) on the entire meter stack assembly, not just the individual breakers. The label should also include a listing number. The manufacturer's catalog information or technical specifications should also explicitly state that the meter stack is a listed service equipment assembly.

If it's Listed

If the meter stack is a listed service equipment assembly designed for this purpose,
you only need one main bonding jumper connecting the neutral to the enclosure. The listing should dictate where that main bonding jumper is located. The installation instructions that accompany the meter stack will also specify how it is to be grounded and bonded. The NRTL has already evaluated the design and determined that a single bonding location is sufficient for proper grounding.

If it's Not a Listed Assembly

This is where things get more complicated. If the meter stack is not a listed assembly, then each of the 4 x 200A meter/breakers is considered a separate service disconnecting means. You would then need to provide a separate grounding electrode conductor and a main bonding jumper at each of the 200A meter/breaker locations. This is because each 200A breaker is essentially acting as an individual service disconnect.

Therefore, the answer depends on whether the meterstack is a listed assembly.
If the meterstack assembly is a listed service equipment, then ONE main bonding jumper is required. If the meterstack assembly is NOT a listed service equipment, then ONE main bonding jumper at EACH 200A meter/breaker is required.Important Considerations



Consult the Manufacturer

Always check the manufacturer's documentation and installation instructions for the meter stack. They will specify whether it's a listed assembly and detail the correct grounding and bonding procedures.


Local AHJ

Ultimately, the final authority on code interpretation is your local Authority Having Jurisdiction (AHJ). Consult with them if you have any doubts or if the listing status is unclear.*

Safety

Grounding and bonding are critical for safety. Improper installation can lead to dangerous voltage on metal parts and increase the risk of electric shock.

In summary, carefully determine if your meter stack is a listed assembly before deciding on the number and location of main bonding jumpers.