Topic: Same load has different power factor when fed from different sources

User: acolella

Asked on: Tuesday, September 16, 2025 at 5:10 pm EDT
Answered on: Tuesday, September 16, 2025 at 5:11 pm EDT

Question: I have some ECM fan motors that are running different power factors when fed from different sources. The motors are 230V single phase motors. The first source that they were fed from is a 600V/240V single phase step down transformer. When fed from this transformer I got the following measurements:233.7 VAC4.0 amps653 watts0.702 power factor934 VA-660 VARD 45.2° phase angle6.06% THD voltage94.3% THD currentThe second source that they were fed from is a 480V delta primary 230V wye secondary three phase transformer. That isn't a typo either. This transformer has a 230V wye secondary. The exact same motors were tested and the exact same power analyzer was used to obtain the measurements. When fed from this transformer I got the following measurements:236 VAC5.5 amps663 watts0.51 power factor1.296 kVA-1.117 kVARD 59.2° phase angle1.63% THD voltage165% THD currentHas anybody ever seen this before? Why would the motors run a lower power factor/draw higher current at essentially the same voltage and power when connected to the three phase transformer?

This is a very interesting and unusual situation. It points strongly to issues with the power quality being supplied by the three-phase transformer, even though the voltage THD appears low. Here's a breakdown of potential causes and troubleshooting steps

Key Observations:
Similar Voltage and Power

The voltage is almost identical, and the actual power (watts) consumed by the motor is close. This suggests the motor is doing roughly the same amount of work.


Lower Power Factor

The power factor drops dramatically when fed by the three-phase transformer. This means a much larger proportion of the current is reactive (VARs).

Higher Current

To deliver the same power (watts) at a lower power factor, the current
must increase (Power = Volts Amps Power Factor). That's what you're seeing.

Significantly Higher Current THD

This is the smoking gun. A THD of 165% on the current means the current waveform is severely distorted. This is not a clean sine wave.

Transformer Configuration (Delta-Wye)

Delta-Wye transformers
can suppress certain harmonic currents (specifically triplens - 3rd, 9th, 15th, etc.) that might be present on the delta primary. However, that doesn't fully explain the high THD on the secondary.

Possible Causes and Troubleshooting Steps


Harmonic Distortion - The Most Likely Culprit



Source of Harmonics

ECM motors themselves can generate harmonics, though typically not this extreme. The more likely scenario is that other non-linear loads connected to the three-phase transformer's secondary are generating significant harmonic currents that are distorting the voltage and current waveforms. Examples of such loads could be VFD's, switch-mode power supplies, or other electronic equipment.

Transformer Impedance

The impedance of the three-phase transformer can play a role. A transformer with lower impedance will be "stiffer" and less susceptible to voltage distortion caused by harmonic currents. The 600/240V transformer may have a higher impedance, which reduces the amount of harmonic current it can supply.


Resonance

It's possible that a resonant condition exists between the inductance of the transformer and the capacitance of other loads connected to the three-phase system. This can amplify harmonic currents at specific frequencies, leading to very high THD.

Troubleshooting



Disconnect Loads

Systematically disconnect other loads on the three-phase transformer's secondary. Monitor the current THD and power factor with each disconnection. If the THD drops significantly when a particular load is removed, that's a strong indication that the removed load is the source of the problem.

Harmonic Analyzer

Use a dedicated harmonic analyzer to identify the specific harmonic frequencies that are most prevalent in the current waveform. This can help pinpoint the source of the distortion.


Transformer Loading

Is the three-phase transformer heavily loaded? Overloading can exacerbate harmonic distortion.2.

Transformer Issues (Less Likely, But Possible)



Transformer Saturation

If the three-phase transformer is undersized or overloaded, it could be experiencing core saturation. Saturation can lead to highly distorted voltage and current waveforms.


Loose Connections/Winding Faults

Loose connections or a developing winding fault within the transformer could introduce non-linearities that affect the power factor and generate harmonics.

Troubleshooting



Transformer Nameplate Check

Verify that the transformer is appropriately sized for the total load connected to it.

Transformer Temperature

Monitor the transformer's temperature. Excessive heat can indicate overloading or internal problems.


Insulation Resistance Test

Perform an insulation resistance test (Megger test) on the transformer windings to check for insulation breakdown.

Turn Off and Test

Shut down the transformer (safely!) and perform resistance measurements across the windings. Look for imbalances.3.

Neutral Issues (More Relevant for Wye Systems)



Excessive Neutral Current

In a wye-connected system, harmonic currents (especially triplens) add arithmetically in the neutral conductor. A high neutral current can distort the voltage and current waveforms, especially if the neutral conductor is undersized or has high impedance.

Troubleshooting



Neutral Current Measurement

Measure the current in the neutral conductor of the three-phase transformer. A high neutral current is a red flag.

Neutral-Ground Voltage

Measure the voltage between neutral and ground. Excessive voltage can indicate neutral problems.


Neutral Conductor Sizing

Verify that the neutral conductor is adequately sized to handle the expected harmonic currents.4.

Motor-Specific Problems (Less Likely, Given the Similar Watts)



Internal Motor Fault

While unlikely, a developing internal fault in the ECM motor itself (e.g., shorted turns in the winding)
could contribute to the high current THD. However, if the motor performs similarly (same watts) on a different source, this is less likely.

Troubleshooting



Motor Insulation Resistance Test

Perform an insulation resistance test on the motor windings.


Compare Motors

Test several of the same model ECM motors on both power sources. If only one motor exhibits the problem, it points to a motor issue.

Action Plan


Focus on Harmonic Distortion

This is the most probable cause. Begin by disconnecting loads from the three-phase transformer's secondary to isolate the source of the harmonics.2.

Measure Neutral Current

Check for excessive neutral current in the three-phase transformer's neutral conductor.3.

Inspect the Transformer

Visually inspect the transformer for signs of overheating or damage. Verify that it's properly sized.4.

Consider Power Quality Mitigation

If harmonics are confirmed, explore mitigation options such as:

Harmonic Filters

Tuned filters or active harmonic filters can reduce harmonic currents.


Line Reactors/Inductors

These can reduce the impact of harmonic currents on the power system.

K-Rated Transformers

These transformers are designed to withstand the heating effects of harmonic currents.

Important Safety Considerations:
Work with qualified electricians and follow all applicable safety procedures when working with electrical equipment. De-energize circuits before disconnecting or testing components. Use appropriate personal protective equipment (PPE).By systematically investigating these possibilities, you should be able to identify the root cause of the power factor and current THD issues. It's likely a combination of factors, but the high current THD points strongly to harmonic distortion as the primary driver. Good luck! Flag for review