User: John165, Location: New Mexico
Asked on: Tuesday, September 16, 2025 at 5:42 pm EDT
Answered on: Tuesday, September 16, 2025 at 5:45 pm EDT
Question: Can anyone tell me what a sub feed as opposed to a tap. One of or guys hooked up a panel with a main, he says it's a subfeed, the inspector says it's a tap, and won't pass it. Thanks
Okay, this is a common point of confusion and can hinge on very specific wording in the National Electrical Code (NEC). The terms "subfeed" and "tap" aren't always precisely defined in the NEC, but the outcome they must achieve is. Here's a breakdown to understand the core issue
The Key Difference (Generally):
Subfeed
A subfeed typically implies a
calculated load is being served by the downstream panel. The upstream panel's capacity is sufficient to handle the new load in addition to its existing loads. The subfeed conductors are sized based on the calculated load they will carry. The upstream panel is not operating at capacity. Tap
A tap rule is a specific exception to the general rule that conductors must be sized based on the load they serve. Tap rules are found in the NEC, and they allow smaller conductors to be used for a short distance to connect to an overcurrent protection device. These rules have very specific requirements about conductor length, overcurrent protection, and the load being served. A tap is typically used to feed a single device or a small group of devices where you don't have a calculated load for an entire panel.
Why the Inspector Cares
The inspector is likely concerned that the conductors feeding the new panel are undersized for the actual load they will be carrying. If the conductors are undersized, they could overheat and create a fire hazard. The inspector wants to ensure the installation complies with the NEC rules for conductor ampacity (how much current a conductor can safely carry).
The NEC (National Electrical Code) and Relevant Considerations
The NEC is the ultimate authority here. Without knowing the specific installation details, I can only give general guidance. The inspector's decision will be based on the specific articles of the NEC. Here's what they're likely looking at:1.
Ampacity of Conductors (NEC Article 310)
The conductors feeding the new panel must have sufficient ampacity to carry the load. This is the fundamental rule. The ampacity of a conductor is determined by its size, insulation type, and installation conditions (e.g., temperature rating of terminals, ambient temperature, number of conductors in a raceway).2.
Overcurrent Protection (NEC Article 240)
The conductors must be protected against overcurrent (excessive current). This is typically done with a circuit breaker or fuses at the point where the conductors originate. The overcurrent protection device must be sized to protect the conductors, but cannot exceed the ampacity of the conductors.3.
Feeder Taps (NEC 240.21(B))
This is where the "tap" concept comes in. There are various tap rules, but they all have restrictions. Common tap rules include the 10-foot tap rule and the 25-foot tap rule. These rules allow you to use conductors with lower ampacity than the upstream overcurrent device under very specific conditions.
Key Restrictions for Tap Rules
Length
The tap conductors must be a specific length (e.g., no more than 10 feet or 25 feet).
Ampacity
The tap conductors must have an ampacity that is at least a certain percentage of the upstream overcurrent device. For example, the 10ft tap rule requires the tap conductors to have an ampacity of no less than 1/10 of the overcurrent device that is feeding the tap conductors.
Enclosure
The tap conductors must be protected from physical damage.
Termination
The tap conductors must terminate in an overcurrent protection device that protects the conductors at their ampacity.
Application
Tap rules cannot be used as a substitute for a correctly sized feeder. The main purpose is to connect a single load with short runs, not to create a new distribution point (like a panel) for multiple loads.4.
Feeder Calculations (NEC Article 220)
This article deals with calculating the load on a feeder. You need to calculate the total load that the new panel will be serving to ensure the conductors and overcurrent protection are adequately sized.5.
Panelboard Overcurrent Protection (NEC 408.36)
Often overlooked, this code section requires that a panelboard with a busbar ampacity of 200A or less be protected by an overcurrent protection device (OCPD) rated no higher than the panelboard's ampacity. This is often done using the main breaker in the panel.
How to Resolve the Issue
Determine the Total Calculated Load
Start by calculating the total load that the new panel will be serving, using NEC Article 220. This includes all lighting, receptacles, appliances, and any other loads that will be connected to the panel.
2.
Size Conductors Based on Load
The conductors feeding the new panel must have an ampacity sufficient to carry the calculated load (with adjustments for derating factors, if applicable).3.
Verify Overcurrent Protection
The overcurrent protection device (circuit breaker or fuses) feeding the conductors must protect the conductors at their ampacity.4.
Evaluate Tap Rules (if applicable)
Only if you are trying to use smaller conductors for a short distance to feed the panel, and if the upstream panel is fully rated, can you consider a tap rule. However, carefully review all the requirements of the specific tap rule you are trying to apply.
Taps are not generally intended for feeding entire subpanels; they are generally for individual loads.5. Discuss with the Inspector
The best approach is to talk to the inspector. Understand exactly why they are rejecting the installation. Ask them which specific NEC articles are being violated. If you can demonstrate that the conductors are properly sized for the load, and that the overcurrent protection is correct, you may be able to get the installation approved. However, if the inspector is correct that the conductors are undersized, you must correct the problem.
In Summary
Don't focus on the terms "subfeed" vs. "tap." Focus on the underlying requirements of the NEC for conductor ampacity, overcurrent protection, and load calculations. The inspector is ultimately responsible for ensuring the installation meets the minimum safety standards of the NEC. Proper load calculations and correct conductor sizing are essential for safety. If you're unsure, consult with a qualified electrical engineer or a more experienced electrician.Good luck resolving this! Flag for review